I have a toshiba a/c unit showing fault code p03, i have found this to be a compressor high discharge temperature, what are the most likely causes of this fault please??
3 Suggested Answers
tborn6
  • 700 Answers
SOURCE: heat pump discharge over temperature
have you changed out the filter on the inside unit lately? remember that is the condenser in the heating mode.
Posted on Feb 01, 2009
  • 744 Answers
SOURCE: COMPRESSOR NOT RUNNING, HOT
The high side/low side pressure equalization you describe is normal for a compressor sitting idle.
If you have an ohm meter you can check the compressor windings for opens and shorts. If your compressor is 3 phase as you state (this would be very unusual for a residential unit) you should have continuity across all 3 phases and no continuity to ground. Take the compressor out of the circuit before you check.
If the compressor does have crankcase heat, it should have been left on for at least 24 hours before starting the unit. Another cause for failure could be overcharging which could have resulted in refrigerant slugging back to the compressor.
Does the unit have any low or high pressure control safeties? If so, check them too - some have resets. You said the condenser fan ran so it's not likely the breaker blew, but check anyway and also check to make sure you have available power on all 3 phases.
Posted on May 03, 2009
Noma a/c cq120 makes noise in compressor area and casing is hot to touch. Is compressor going? Is it worth to repair or buy new. I'm guessing this unit is 4 years old or more
Possible Causes There are several reasons for a compressor to run too hot, including high compression ratio, high return gas temperatures, and lack of external cooling.High compression ratios are the result of either lower than normal suction pressures or higher than normal discharge pressures. Changes in suction pressure will affect the compression ratio more rapidly than changes in the discharge pressure. For this reason, it is important to keep the suction pressure at its highest possible value.
Causes of low suction pressure can include incorrect sizing of components, misadjusted or defective metering devices (TXVs), loss of refrigerant charge, plugged driers or strainers, and excessive suction line pressure drop.
Although not as sensitive to change as the suction pressure, the discharge pressure can still greatly affect the compression ratio. Keeping the discharge pressure within normal operating conditions is still important.
Causes of high discharge pressure can include dirty condensing coils, undersized discharge line, a blockage or recirculation of condenser air, erratic condenser fan operation, refrigerant overcharge, noncondensibles in the system, and an undersized condenser.
Many larger refrigeration systems with electronic controllers will automatically monitor the temperature of the discharge line and will send out an alarm to alert the owner or service contractor of a potential problem. Regardless of how the discharge line temperature is monitored, it should always be checked as part of any service to a refrigeration system.
A technician should also check the discharge line temperature within 6 inches from the outlet of the compressor. Any temperature above 225 degrees should be investigated and the cause found and repaired.
Jul 26, 2017 | Refrigerators
A copper thin tube from the unit is very hot. Is it normal?
Yes, well somewhat normal. The refrigerant leaves the compressor at high temperature and flows through the condenser coil where it cools about 20 degrees warmer than the outside air flowing through the condenser. Many small air conditioner units use a small copper tube (capillary tube) of a specific diameter and length for that system to cause a decrease in refrigerant pressure between the condenser and the evaporator. The refrigerant leaves the compressor as a gas at high pressure, cools in the condenser and changes into a liquid. The liquid flows through the cap tube and cools more as the pressure decreases and gets closer to the evaporator. The refrigerant boils and evaporates under the low pressure of the evaporator and turns back into a gas. That gas is pulled back to the compressor.
If the condenser is not cooling the refrigerant enough, the tube can become extra hot. Efficiency is reduced. Actual temperatures throughout the system depend on the type refrigerant used, suction and discharge pressure at the compressor, outside and inside temperature. Tables, charts and graphs for various pressure-temperature relationships can be found in refrigeration books and chemical web sites.
Mar 17, 2015 | Carrier FB4ANF060 HVAC Electric Unit & AC...
My Air compressor Dich. temp shows high temp....what are the reasons for the same.....
High temperature discharge air is caused by leaking reed valves or leaking head gaskets. Another indication of leaking head parts is that it takes longer to fill than usual or the compressor will not reach cut-out pressure. Good luck
Dec 06, 2014 | Air Tools & Compressors
What problems can occur when you overcharge the hvac
The level of overcharge will dictate the severity of the possible problems. The most common problem with overcharging is creating high compressor head pressure which over-amps the compressor motor which waste energy and shortens compressor life. Installed high pressure safeties will usually shut off the unit off and must be manually reset. High system pressure also results in higher evaporator temperatures and higher air discharge temperatures. Grossly overcharged systems could return liquid to the compressor, destroying it.
Sep 04, 2014 | Heating & Cooling
How to tell if the compressor on your ac unit is running
If you have a split unit, it is fairly simple, just feel the small refrigerant line coming out of the unit. The temperature should be warmer than the surrounding air. If is not running the temperature will be the same as the surrounding air. If you have a package unit, take off the access cover to where the compressor is located. Find the compressor discharge piping to the the condensing coil. It is the smaller of the two major pipes on the side of the compressor. Be careful the temperature of line coming out of a properly operating compressor will be hot enough to cause second degree burns. If the line is very warm to very hot the compressor is running. If you have a set of gauges, attach the RED hose to the high pressure service connection and the other low pressure hose BLUE to the bigger pipe low pressure connection. Make sure the gauges are isolated by shutting the valves. The pressure difference between high and low pressure is normally at least 150 psig diference.
Jun 25, 2014 | Goodman CKL24AR24 Air Conditioner
What cuases high a/e discharge fault on ingersol rand air compressor
Dirty coolers are always associated with high discharge temps,always make sure your coolers are clean
compressor oil filters being clogged can also raise your temp n cause the unit to over heat,and on the much bigger machines if the compressor oil pump fails then you will have severe over heating as the oil flow to the cooler is assisted by the pump!!things like regulating pressure should always be adjusted to the machines specs so it doesn't over pressurize n put load on your airend while the engine is at idle.
Jun 24, 2014 | Ingersoll Rand Stationary Air Cooled...
Compressor problems
probably a bad discharge temp sensor or a bad thermo valve which is really a thermostat you need to take the temperature of the running unit when it is running best way is to use a inferred temp gun at the discharge of the pump or watch you temp guage if it jumps around or is erratic the sensor is bad .compressor usually will shut off on high temp at 230f
Mar 11, 2014 | Air Tools & Compressors
Ingersoll rand air compressor model SSR-UP5-30-14 frequent trip on high airend temperature ....what is the solution ? and another unit ( same model ) always trip on " starter fault ". Untill...
check if approach and discharge pipes to oil cooler are similar temperature as there is a thermo bypass valve that controls the flow through the cooler if cooler is quite cool but still very hot inside this could be stuck in closed position causing restricted flow through the cooler
Sep 20, 2011 | Ingersoll Air Tools & Compressors
P8 eroor code
P8 error is abnormal pipe temperature indoor. If you are running it on heating P8 error will appear because the disc pressure is too high. It could be overcharged.
May 31, 2009 | Mitsubishi Mr. Slim MXZ30TN Air...
Heat pump discharge over temperature
Jan 31, 2009 | Heating & Cooling
Heating & Cooling Logo
193 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Tim Whalen