The generator does not produce voltage. The engine starts fine and runs good! I disconnected the wire horness from the generator and checked for power straight out of the generator while running the engine and still had nothing! The brushes were clearly burnt. The resistors on top had burn spots on it, so I changed them. Part # 91825GS I checked the receptical and I still have no power.
    Scholar:
  • 133 Answers
I have only repaired 3 in my life but it was the rectifier on the second 2 and the first one needed to have its field coils "Excited". That's done by touching the NEGATIVE battery lead to their lead wire. Rectifies are cheap and only about the size of a quarter. The old ones weighed around 20 pounds and were made up of steel plates and wire. The new ones are ICs. Good Luck!
Posted on Apr 01, 2011
The gt5250 power back generator has stop producing
If it has sat, it may have lost it's rotor residual magnetism. Disconnect the rotor field wires at the AVR or on the exciter/brushes. Note they are polaroty sensitive. Connect a 12V battery to F+ and F- (note polarity) and momentarilly power from the battery for a few seconds. DO NOT forget to disconnect the rotor/exciter field wires first or the voltage regulator will be damaged. If it hasn't sat check voltage regulator, rotor resistance, and stator resistance, and for shorts to ground.
Oct 18, 2014 | Electrical Supplies
Brushless generator has stopped producing power ,
My 7500 watt generator doesn't produce any power
Jul 31, 2014 | Honeywell 7500 Watt Generator 15 HP Engine...
Black max 7kw generator high voltage output
Those voltage readings MAY be normal.
The AC waveform may cause your meter to read inaccurately. You would need to use a TRUE RMS meter to accurately read the voltage.
The siple meters actually read the AVERAGE voltage and then are calibrated to mulltiply it by the "form factor" for a sine wave. OFTEN these generators don't produce a clean sine wave. A square-ish wave will read higher on the garden variety meters.
Compare the brightness of a lamp comparing to when run on your utility.
The frequency depends on engine speed ... yours is running a bit fast...check it under at least half load and if off, adjust the govenor slightly.
May 01, 2010 | Briggs & Stratton Power Products 5,550...
Onan generator emerald III genset. I push the start button and the generator comes on as if it has started, as soon as I let the button go, it shuts down.
Here are the most common reasons for your condition.
CHECK IF ENGINE KEEPS RUNNING The most common complaint is that the engine starts but will not keep running when the START switch is released. This happens because the control board will not allow the engine to continue running if the generator is not producing voltage or if the oil pressure signal is not present. See CONDITIONS REQUIRED TO KEEP RUNNING on the Troubleshooting Chart for your model. If the engine will not keep running, do the following:
A1. Generator AC Output Check the generator AC output voltage as soon as the engine starts. Models showing "B1-B2 Volts" or "L1 AC Volts" under CONDITIONS REQUIRED TO KEEP RUNNING need this AC voltage to keep running. Read between the points shown on the Troubleshooting Chart. If the AC voltage readings are good, proceed to "B" below.
A2. Field Flash If there is no AC, check for 10-12 VDC at the FIELD FLASH pin of the control board during cranking. If the field flash voltage is not present, the control board is defective. If the field flash voltage is present, the wiring or regulator may be defective. To eliminate the wiring, check continuity between the FIELD FLASH pin of the control board and pin 7 of the regulator. If the continuity is good, either the regulator or the field circuit (rotor and brushes) may be the problem.
A3 Field Circuit Check the field circuit by unplugging the regulator and measuring the resistance between pins 9 and 10 of the regulator’s mating plug. This reading should be 22 to 28 ohms. If this reading is too high, check the brushes and/or clean the slip rings (use the Slick Stick, or a similar tool). If this reading is too low, there may be a short in the rotor. Also, check the resistance from pins 9 and 10 to ground. This reading should be very high or infinity. If not, there is likely a ground in the rotor. If these readings are all good, the regulator is likely defective.
A4 External Excitation To confirm that the regulator is defective, turn off the generator’s AC circuit breaker(s), reconnect the regulator and apply 12 volts through a diode to pin 9 of the regulator plug (see illustration) while attempting to start the engine. CAUTION: DO NOT attempt this without the diode. If you do, there will be fireworks! Remove the 12 volts within 1-2 seconds after the engine starts. If the genset now continues to run and produces normal AC voltage, the generator is OK and the regulator is defective. If the genset does not continue to run but produces about 40% of normal AC voltage, again the generator is OK and the regulator is defective. If no AC voltage is produced, the generator may have a problem that is beyond the scope of this guide. Re-check all wiring for security and signs of damage. It may be necessary to take the unit to a qualified repair shop.
B. Check the oil pressure switch as soon as the engine starts. Models showing "LOP to GND" under CONDITIONS REQUIRED TO KEEP RUNNING need the oil pressure switch to be closed to ground when running. If the voltage on the LOL/LOP SW pin of the control does not go to near zero, the switch is not closing. These switches sometimes stick open if the generator has not been used or exercised often enough. Multiple start/stop cycles and/or tapping on the oil pressure switch will sometimes fix it. It may be necessary to temporarily jumper the switch to ground to keep the engine running. This can be done at the switch or at the OIL LOL/LOP SW pin on the control board. Models showing "LOP Open" under CONDITIONS REQUIRED TO KEEP RUNNING have electronic governors and require the low oil pressure switch to be closed at starting but open during running. When the switch opens, the governor module places a ground on the oil pressure input of the control board (P1-5). It is OK to temporarily ground P1-5 on this model to keep the engine running. NOTE: See chart for oil pressure and oil level switch locations.
C. If there is AC voltage present on B1-B2 or L1 AC, as applicable, and the correct oil pressure/level signal is present at the OIL LOL/LOP SW input of the control board, and the engine will not keep running, the control board is defective.
This should help you get it going.
Kelly
Mar 08, 2010 | Watts Onan Portable Generator - 5000 ,...
Charging failure on a 1987 fz600
The generator will produce ac voltage not dc so the meter needs to read ac voltage. the readings need to be taken between the three wires using two at a time until all combinations have been tried. readings should all be the same. Engine will have to be run at about 5000rpm while readings are obtained. Other possible problem could be the regulator / rectifier unit breaking down when hot.
Aug 08, 2009 | 1986 Yamaha FZ 600
My generator starts but not give 220 volts power
Check the voltage regulator and any fuses or breakers.
Jul 02, 2009 | Coleman Powermate Premium Plus 6250W...
No power output from my generac 5000 power plus.
sounds like you need to "flash the field". This means you've lost you excitation voltage for the generator to produce electricity. In most cases you need to get a 9volt battery and connect it to 2 & 6 inside the generator. They are Blue & Red wires, but they are not the only blue & red ones there. The generator should be running and the battery should only be connected for about 5 seconds. This is very dangerous because of all the high voltage and democrats.
Apr 09, 2009 | Generac 100 Amp 120/240-Volt Transfer...
Powermate PM0496500.02 No voltage output
Here is a simple test to check field and other wiring. With engine off apply 12v ac 1 amp to 110v outlet plug on generator. This will energize the field windings and should cause the armature to produce dc voltage at the brushes and produce a nice magnet. If there is a short in the field or broken wire or shorted capacitor there will be no dc reading at the brushes. . This test is the opposite of what actually occurs when the engine is running. That is the armature produces a magnet fed thru the windings, regulator and brushes. If dc voltage is present at the burshes, remove 12v ac and start engine to check for output. enjoy