The condenser fan will not come on the wiring is correct and the relay ohms out good with my meter when the wires are disconnected. the compressor comes on but the fan will not unless i hook it up to run constantly
    Genius:
  • 1,033 Answers
Hello, have you checked the capacitor, usually when a motor will not start it's because the capacitor is bad or the motor is bad. Most likely you have a bad capacitor.
Posted on Mar 30, 2011
Freezer working, fridge not, same on gas& 240
Check ur cold control thermostat, ur thermistors in both fridge and freezer ( they should be checked for both ohms and for amount of current being put out as per ur model ), ur air flow vent from freezer to fridge.( to make sure it opens and closes without any restrictions) On thermistors check for A close circuit and amount of ohms not just an Ohm reading. As per ur model. Most should atleast show 1200 ohms. Also Check door seals for leakage.
Evaporator coils
Poor cooling is often the result of a heavy frost build-up on the evaporator coils. You can't see these coils without removing a panel on the inside of your freezer. A sure sign that there is a build-up is the presence of any frost or ice build-up on the inside walls, floor, or ceiling of the freezer. Such a frost build-up usually indicates a problem in the self-defrosting system or damaged door gaskets.
If one of the components in the self-defrosting system fails, the refrigerator continues to try to cool. Eventually, though, so much frost builds up on the evaporator coils that the circulating fan can't draw air over the coils. There may still be a small amount of cooling because the coils are icy, but with no air flow over the coils, cooling in the refrigerator compartment is quite limited.
FAN check to see if it is operating or restricted A fan that is not blowing or restricted will not circulate the cold air properly.
Often, the first thing that folks do when their refrigerator starts to feel warm is turn both controls on the coldest settings.This is exactly the WRONG thing to do.Turning the cold control to the coldest settingwillkeep the compressor running longer and make lots of cold air.
But turning the air door to the coldest settingclosesthe airway to the food section. Lots of cold air is made, but most of it stays in the freezer section, and the food section actually getswarmer.
Condenser
Self-defrosting refrigerators all have a set of coils and a cooling fan, usually under the refrigerator, that need to be cleaned regularly. If these coils get coated with dust, dirt or lint, the refrigerator may not cool properly. The coils may appear to be a thin, black, wide radiator-like device behind the lower kick-panel. To clean them, disconnect the refrigerator from the power source, use a refrigerator condenser brush and your vacuum cleaner to clean the coils of any lint, pet hair, etc. You may not be able to get to all of the condenser from the front, it may be necessary to clean the remainder of the condenser from the rear of the refrigerator.
May also need to check the defrost timer, u can get by and test manually by placing a small screw driver into the tiny slot or hole underneath the timer and turn slowly clockwise till u hear 1 click. this will engage ur defrost cycle in about 15 minutes u should be able to come back and feel the heat in freezer as it melts the ice providing ur terminator is not bad?
Another way to test it is with a multi meter. Remove timer it from fridge and you will see 4 prongs numbered 2,1,4,3 in that order. Place ur meter prong on prong 1 & 3 (if your fridge has a capacitor wired in series with the windings, then u check for micro fares rather than OHMS) If u cannot confirm this test, still try the next.
Take ur meter prong and connect to prong 1 & 4, it should read resistance or ohms ( closed) now remove prongs and place on prong 1 & 2, this should now read infinity or open (no ohms) now take a small screwdriver place it in the tiny hole or slot under the timer. Turn it clockwise slowly till u hear 1 click. Now ur 1& 2 should read closed ( showing ohms or resistance) now place meter prongs on 1 & 4 and you it should now show open ( or no resistance - no ohms) this is how u know ur timer is good, Remember when testing for ohms ADJUST meter to use a high ohms rating in the thousands as the resistance is very high in OHMS. And adjusting to low ohms rating may give a false reading or not show the proper resistance..
THE COMPRESSOR:
If you hear a clicking sound coming from the back of your refrigerator/freezer, then the problem is most likely the compressor, relay and or capacitor is overheating or not getting proper power and will not start.The compressor is the component on your refrigerator that allows your refrigerator to cool. If this component is not working properly your refrigerator will stop cooling. Most of the time the compressor is not the component that has failed.
To check ur compressor with multi meter:
Disconnect and remove the relay and capacitor from compressor, some located next to compressor in a casing.
You wills see 3 prongs coming out of compressor. 1 goes to ur srtart winding, 1 goes to ur run winding and the center goes to ur ground.
Place ur meter connector or prong on the start prong and the other on the ground (center prong) take note of the reading in OHMS for example 5 ohms.
Next place meter prong on run prong and the center ground prong agin. Take note of the reading in OHMS. Example 4 ohms
Next place meter prong on the start prong and the other on the run prong, now take note of the reading example 9 ohms. Now match the total of this ohms test with the total of ur two separate test. 9 ohms, if they match ur ok give or take 5 percent plus or minus. One more test to make to test of there is a short in compressor attach meter prong to ground prong and rub the other end of meter prong to metal ( scrape the metal clean of paint and test on metal surface not painted surface. If it shows continuity or ohms , u have a short in ur compressor. It should show infinity
TO REPLACE RELAY AND CAPACITOR WITH A HARDSTART KIT YOU CAN USE
A 3 in 1 start kit for compressors sizes 1/4 through 1/3 HP. And a 5 in 1 for higher H.P. (BE SURE TO MATCH WITH UR COMPRESSOR MODEL NUMBER AND TYPE) The kit includes relay, capacitor, and overload device, pre-wired. The kit will replace all 3 electrical components on capillary refrigeration systems. For newer systems with a run capacitor use proper kit. For smaller horsepower compressors useTJ90RCO810.
The wire set up is as follows the red wire goes to the right side of compressor prong, the white wire to the left side prong, the black wire to the center prong, and the 2 other black wires go to the power and the ground connection
Lastly you should also check ur THERMISTORS in the freezer and fridge section for continuity OHMS and for amount of OHMS current being put out. In most models around 13000 ( give or take 150 ohms) ohms is required.
Read more:
http://removeandreplace.com/2013/10/31/fix-refrigerator-freezer-wont-cool-freeze/#ixzz3WDEo5NDJ
REMEMBER GOD IS THE REASON FOR GOOD ADVICE"
Refrigerator Is Not Cooling What To Check And How To Fix
Nov 30, 2016 | Refrigerators
Hi the condenser fan not running on ge refrigerator model PFE29PSDASS serial # HZ500118 can you please explain how to test diagnosE it the picture is for J2 plug .thanks
Condenser
THE COMPRESSOR:
Read more:
Oct 08, 2016 | GE Refrigerators
MAYTAG MODEL MTB1521ARW FRIDGE CKT IS RUNNING BUT COMPRESSOR STARTS AND AFTER 2 SEC ITS STOP .EVAPORATOR AND CONDENSER FAN IS RUNNING GOOD. WHATS THE REASON?
Condenser
THE COMPRESSOR:
Read more:
Jun 04, 2016 | Maytag Refrigerators
How do the wires get reconnected to the starter relay on tfx26apdaww
see pics To check ur compressor with multi meter:
Disconnect and remove the relay and capacitor from compressor, sometimes located next to compressor in a casing.
You wills see 3 prongs coming out of compressor. 1 goes to ur start winding, 1 goes to ur run winding and the center goes to ur ground or COM
Next place meter prong on the start prong and the other on the run prong, now take note of the reading example 9 ohms. Now match the total of this ohms test with the total of ur two separate test. 9 ohms, if they match ur ok give or take 5 percent plus or minus. One more test to make to test of there is a short in compressor attach meter prong to ground prong and rub the other end of meter prong to metal ( scrape the metal clean of paint and test on metal surface not painted surface. If it shows continuity or ohms, u have a short in ur compressor. It should show infinity
God is so good: so this is why I give free advice so please thank him not me.
Jan 13, 2016 | GE Refrigerators
I have a goodman manufacturing 3 ton heat pump, model #CPLE36-1. initial call was no a/c. found breaker tripped. reset and hit disconnect and tripped again.. ohmed compressor and fan motor and both ohmed...
What you need to do is disconnect the compressor at the electrical access on the side of the unit. Check each wire to the grounding screw using ohm meter if you get continuity your compressor is shorted do the same thing for you condenser fan. I bet your compressor is shorted. Make sure power is off and remember where the wires go. Trace the wires that go to compressor back to the contactor and capacitor and disconnect them there. If this help please rate me and do a testimonial.
May 25, 2011 | Heating & Cooling
2003 lincoln navigator. The air ride compressor will not come on. Checked all fusses and relays and they r good. The compressor will run when u straight wire it. Why won't it come on automatically?
I know you stated you checked all fuses and relay and they're ok but The 2003 Lincoln Navigator had two differently (wired) air ride systems. A early production and a late one, and I think I may have a good Idea of what your problem may be and will walk you through how to properly test the system. The early production navigators used a solid state compressor relay and the later production units used a standard style relay. The early ones with the solid state type has been known to have some problems and working for a Ford, Lincoln Dealer for 21 years I have replaced a good number of these solid state relay for a air ride compressor inoperative concern. There seems to be some confusion on the location of the solid state relay. I would advise you to look behind your front bumper on the passengers side of your vehicle (and below your headlight) and see if you have a 4 wire relay that's aluminum and finnd ribs on the front of it and I believe a black base where the wiring connector plugs in. (this will be mounted to the radiator support) if so, you Have got the early production style. I will walk you through how to test this relay and also help you to isolate the cause of your problem. I highly recommend using a volt ohm meter for these tests. I do not recommend using A TEST LIGHT due to the fact that you will be testing a circuit that is wired to the air ride control module, and there is a possibility of you damaging the module with a test light !!! I have been there, done that, NOT GOOD.
Ok with that said: your wire colors should be as follows:
one that's( gray and red)
another that's (light green and red)
another that's (dark blue and yellow)
and one that (light blue and pink).
Disconnect the connector at the relay and you'll be testing the wires in the connector (THAT HOOK UP TO THE RELAY). The air ride compressor and the air ride solid state relay share the same ground which is the light green and red wire.
Turn your volt ohm meter to dc volts scale and attach the black wire (NEGATIVE) lead of the volt ohm meter to the light green and red wire.
Hook the red lead of the volt ohm meter to the light blue and pink wire.
Here your volt meter should read battery voltage (of your car's battery) if not check the (F2-111) 50 amp designated fuse in the fuse box under the the dash on the passengers side (KICK PANEL).
If this fuse is ok, make sure you were making good contact with your test leads into the compressor relay connector.
If you're comfortable with the fact that you have a good connection at the relay connector and your fuse tested ok, then you have a ground problem at ground point G101 which is located right near the mounting location of the air ride relay.
If you had battery voltage when you tested between the (light green and red) and the light blue and pink wires, you have confirmed the power source and ground to the relay.
I should clarify myself at this point. The wires at the relay are as such: The ground is the light green and red wire, the light blue and pink is the fused power source to the relay, the dark blue and yellow wire is the relay trigger source from the air ride module to the air ride relay, and the grey and red is the relay output (battery +) to turn on the compressor. OK.
So now we're down to checking the trigger source to the relay and the relay output. At this point I want you to re-hook up the volt ohm meter with the meter still set at volts d/c scale and reconnect the (red lead) of the volt ohm meter to the (light blue and pink wire) and connect the (black) lead of the volt ohm meter to the dark blue and yellow wire (again at the relay connector).
Now this next step is best done with the help of an assistant!!
While watching your volt ohm meter, have your assistant turn on the key and open and close the drivers door two -to- three times. After cycling the door, you for a short time should see at least 5 volts minimum, if not battery voltage at your meter.
(this is a little bit unclear to me due to the fact the air ride module shows that the dark blue and yellow wire, as a ground from the air ride module to the relay. but does not clarify exactly what value that ground signal should be). I am referencing Fords own wiring diagram.
A solid state relay usally is allowed a trigger source of a lower voltage then a standard relay. If you find you have no voltage reading at your volt ohm on this test, you'll first want to check fuses F2-20 which is a 30 amp fuse and F2-27 which is a 5 amp fuse in the same fuse box as the F2-111 fuse you checked earlier.
The last test you need to make at the relay is checking the relay output to the compressor. This will be done by again using the volt ohm meter. This time you'll want to hook the black lead of the volt ohm meter to the light green and red wire at the reay connector and hook the red lead of the volt ohm meter to the grey and red wire at the relay connector. Again for this test, you'll need to have a assistant turn on the key, then recycle the drivers door again.
If the relay is working properly you should have battery voltage, aproximately 12 volts showing on your meter. If not and all other test procedures results were correct, you have a bad relay.
If you have 12 volts on this test we have confirmed the relay is good and the trigger signal from the air ride module is operating as designed.
If the pump runs like you said (when it is straight wired ) the remaining possiblity is a broke wire between the air ride relay to the air ride pump (this being the grey and red wire) which you can test by switching the volt ohm meter to the ohms scale and touching one lead of the meter to the grey and red wire at the relay connector and the other to the grey and red wire at the compressor (with the compressor and the relay both disconnected). Your reading here should be 0.5 ohms or less. If you have under 1.0 ohms you're ok but specs are 0. 5 or less.
If you have an auto ranging type ohm meter, be sure your reading in ohms and not kilo ohms or mega ohms.
If you find while performing the test from the air ride module to the air ride relay (dark blue and yellow wire) referenced as the trigger signal, incorrect and all fuses all checked o.k. then it is possible the air ride control module is defective. But, before condemning the module, there are a multitude of input signal;s to the module that would have to be checked.
WARNING: Make sure your tests are accurate. Good to check and re-check each test. Be confident of your results.
Inaccurate tests and inaccurate test results= unnecessary parts replacement. Results are large dollars spent when unneeded.
Hope this helps you out.thanks for using fixya
Jan 03, 2011 | 2003 Lincoln Navigator
My Air conditioner stopped putting out cool air. The fan unit outside stopped turning. What would the problem be?
The unit is overheating and tripping the internal overload of the compressor. Clean outdoor coils.....check outdoor fan to see if it turns or is siezed......possible bad Start/Run Capacitor which is a very common failure on condensing units......possible bad fan motor need replaced! Unit compressor can be cooled with a water hose to get it to reset the internal biometalic high limit switch that is located in the hermetically sealed compressor!
Aug 10, 2010 | Goodman CLQ36AR49 Air Conditioner
Getting a hum from the condenser
thats it? you may be hearing the contactor relay which is fed power from inside (24v). could be a bad fuse which was caused by a bad or going bad compressor. possibly one of the terminals on the compressor (probably start) has burned off and grounded on the compressor which blew the fuses. Get an electric meter and test the fuses and if they are good, inspect the compressor and see what the wires look like. If they are good disconnect them and write down where they go. test the ohms between each terminal and list them on this site ill tell ya if you have a good or bad compressor. also test ohms from the ground to each terminal and if you get 0 on any terminal to ground your compressor is dead for sure...
Oct 10, 2009 | Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen