Semia condens f30e, when i start it after resets it cuts out after 20 seconds whats the problem. i have changed the gas valve, still goes to lockout, is there anything else i can do, the fan is working ok so is the pressure switch.
3 Suggested Answers
pierre1811
  • 144 Answers
SOURCE: Gas valve lockout
It means that the furnace isn't igniting and for safety the control board is preventing the gas valve from opening. Turn off the power to the furnace for a few seconds then observe what the furnace does in heat mode. Some furnaces will run the blower for a minute after you power it back up. After that see if the furnace tries to come on. If you are still getting the code then one of you high temp limit or roll out switches has tripped. Now is the time for a service tech. Make sure that you check you filter and air flow too. Low air flow means the furnace may be over heating.
The other thing is the hot surface igniter. Look closely at it with the power off. Do you see a white spot on the element or a crack. If so the HSI is bad. It's an easy replacement but DO NOT touch the carbon element with your fingers and be very careful handling it as it is EXTREMELY fragile.
Posted on Mar 17, 2009
SOURCE: re: worcester bosch heatslave 20/25
Air in Oil line, Blead air out.
Posted on Aug 25, 2008
Why my heat pump only heat in emergency heat only,the condens is cutting off and on
It sounds like a maintenance issue with your heat pump, its clear that the unit is trying to run but one of the safeties is shutting it down trying to protect itself. most heat pumps are equipt with a High press lockout usually a manual reset ,a low press, cut out switch resets on rise of press automatically. Causes of LPCO Extremely dirty condenser coil or evaporator coil, Loss of fan on condenser, Low refrigerant charge. A competent Service man should be able to locate and correct this problem. A seasonal check up on the unit avoids these problems.
Feb 22, 2015 | GE Zoneline AZ38H12DAD Split System Air...
Richmond powervent model 6G40PV-40F Lockout 4-2 blink. What's wrong. What do I replace to fix?
1) Rheem-Richmond does not post service manuals:
Copy following link to identify service manual by type of gas control valve:
http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html#intellivent
2) For lockout, the air intake might be clogged or combustion parts dirty, causing overheating which will break TRD glass vial. Gas control may need to be replaced. Reset gas control by rotating knob to lowest temp for at least 6 seconds.
3) Call Rheem or local service tech.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Mar 10, 2013 | Water Heaters
I have an older sterling gas furnace hung from the garage ceiling that cuts out intermittently . It does not trip the breaker but often if I reset the breaker at the fuse panel box it will start up.
The heater is going into "lockout"... it should be flashing a code on the ignition control that will tell you why it went into the lockout condition...
My guess would be that the high limit switch is bad or going bad and it is cutting out when it shouldn't be... or the flame sensor is loosing contact and cutting the burner off...
You could try to clean off the flame rod with a soft cloth...
heatman101
Jan 18, 2011 | Sterling RF30 Natural Gas Garage Heater
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Fault code says pressure switch lockout
This more often than not, indicates that your pressure switch is gone and needs to be replaced. Watch the YouTube video for a fuller explanation and heed the warning to use OEM parts! Gas Furnace Pressure Switch Failure and Replacement Amazon com gas furnace parts
Feb 06, 2010 | Heating & Cooling
GMP050-3 heater, gas turns on and lights for 5-7 seconds and just as thr igniter goes dim the gas shuts off. after 3 cycles the erd LED flashes on/off at a 1.5 seconds on and 1.5 sec off Gary
After the gas turns on, it is the flame sensor's job to see that ignition took place and send 24v to the gas valve. If it does not do this, the gas valve shuts down as a safety precaution. After 3 tries, the furnace will go into "lockout" and will not let it attempt to start again. The lockout can be resolved by turning off the power to the furnace for a couple minutes and then turning it back on. Sounds like the real problem is a faulty flame sensor not sending 24v to the gas valve. Sometimes they can be cleaned with a piece of sandcloth. This will cure failure to recognize the flame due to carbon build up on the sensor. Otherwise, the sensor will need to be replaced. Hope this helps!
Dec 16, 2008 | Goodman Heating & Cooling
I have a problem with my heating system. It is about 10 years old and has had the ignitor, combustion blower motor, and programable thermostat replace in it's lifetime. The system worked great last year....
sounds like its not proofing flame. it has a sensor usually like a needle sticks out into the flame that tells the gas valve the flame lit and is burning so its ok to keep sending gas, if its fails to proof flame then burner shuts down, then it tries to relight 3 times then locks out on fail safe. the blower will sometimes run continually once that occurs to highlight a failed condition. every time you reset it will try again 3 times then shut down. lp gas is very dangerous, even i do not work on it as the gas acts like gasoline and lays around. not like natural gas that disperses well. if you see the flame sensor try gently cleaning it with a little emory cloth. also a loose ground can cause this. check tio be sure any green wires are snug , they actually flow volts to ground through the flame on some to proof, thats why no ground no flame. if that fails then the board is most likely problem. change wire for wire , or get generic replacemant and follow directions exactly. good luck.some ignitors act as a flamre proofer as soon as they are done igniting! rarely do they fail to perform both funtions.
Nov 20, 2008 | Heating & Cooling
Heating & Cooling Logo
162 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Tim Whalen
Marvin
Marvin