Question about Mitsubishi MSZ-A24NA Split System Air Conditioner
In heating mode, the indoor unit (MSZ24NA) blows only unheated air. Both green lights are on. Outdoor temperature is 40 degrees. Outdoor unit (MUZ24NA) appears to be functioning properly; i.e., the fan runs. Filters inside are clean, and nothing blocks the outdoor unit.
  • 33 Answers
SOURCE: Fan works, air conditioning does not. Try
Without seeing the unit,
1 - the condenser fan (which is in the outdoor unit) could be blown. This would cause the unit to go off on high head pressure.
2 - it could be low on refrigerant, which makes it do nothing but blow room temperature air around. The unit would go off on low pressure
3 - the filter is dirty, blocking the cooling
4 - the compressor could be shorted, or a corroded wire somewhere that feeds the contactor
Mr. Slim Ductless Splits are the best on the market and should only be repaired by a trained technician.
Hope this helps.
Posted on Jul 23, 2010
SOURCE: U4 System transmission between indoor and outdoor units Daikin
Have you found the problem with ya A/C yet PD with the U4 code, if so what was it.
Posted on Jul 27, 2010
hvac1960
  • 2133 Answers
SOURCE: When unit is turned on
It's communication error between indoor and out door unit.
Comms Error, check your wiring, remove external pumps. Split/Multi - check volts from terminal N to 3 = 0 - 65 Vdc, Multi V - 4 Vdc terminals 3 and 4
Posted on Jan 06, 2011
richroth
  • 9472 Answers
SOURCE: Our heat pump is blowing
Below is a quick breakdown of the BTU's. One as you can see is at 65 degrees and the other is for 17 degrees. The BTU's are more than cut in half at 17 degrees as you can see. Your heat pump will struggle at the lower temperatures.
Outdoor Heating Air Compressor Air Capacity Flow Current (deg °F) (BTUH) 65 23,529 17 11,200
Posted on Jan 24, 2011
  • 157 Answers
SOURCE: We just installed a MR.
have you checked the power to the outdoor unit
Posted on Jul 01, 2011
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
New owner of AcuRite Model 75075. Outdoor temp (just now installed) is reading 7 degrees higher than actual tempperature. How lond does it take for the indoor & outdoor unit to get in Synch?
Typically the Sensors Sync-Up within 10 to 20 Minutes. However, placement of the Outdoor Sensor is also important. The National Weather Service (NWS) and NOAA measure the Temperature in the Shade, and NOT in the Sun. So be sure that your "Exterior Sensor" is placed in the Shade, under an overhang for example. However, be careful not to place the sensor under an overhang, where there may be a soffit-vent or gable-vent, that is used to vent out warm air from the attic. Even a three (3) season, unheated porch can be warmer than the actual external temperature, due to passive/solar heat captured thru the windows (East/South/West).
Jun 08, 2017 | Measuring Tools & Sensors
Hi,My remote do not get the good temp in my house. Ex: I set to 80F in heat mode but the thermopump operate slowly and dosn't get hire than 70-72F. The remote see the unit and all. Is the sensor in th
You have a heat pump.
Once the outdoor temperature falls below 36 degrees, heat pumps will sharply lose their ability to heat.
If you are getting a 72 degree indoor temperature when the outdoor temperature is 28-30 degrees, the heat pump is performing up to spec.
On heat pumps, the air coming out of the nearest air vent to the unit should be heated approximately 40 degrees warmer than the air entering the unit.
If you have a 70 degree indoor air temperature, the heat pump should be supplying 110 degree air at the closest air vent to the indoor unit.
Gas heat is a much better heating source where outside temperatures are commonly below 36 degrees.
Even electric furnaces perform better than heat pumps under these conditions.
Nov 30, 2014 | Heating & Cooling
My Mistral MSS25 has stopped blowing hot air, it's only 6 degrees and it's friday afternoon before a long weekend! Is there anything I can do to fix it before someone can come out here next week to lo
No heat pump will put out much, if any at 6 degrees.
A heat pump is an air conditioner that reverses cycle via a reversing valve that re directs the refrigerant flow in the unit, in ac mode,
heat from indoors is rejected outdoors in the heat mode the heat from outdoors is rejected indoors.
The system does this by evaporating and condensing refrigerant.
For the refrigerant to be "boiled" or "change state" from a liquid to a vapor a temperature differential must exist, meaning the heat from the outdoor air must "boil" the liquid refrigerant.
For this to be possible the liquid refrigerant must be colder than the 6 degrees ambient or it will not boil anything.
For a refrigerant used for AC to be that cold the pressure will be in a vacuum for most refrigerants temperature pressure relationship.
Heat pumps below 40 degrees ambient outdoor temperature are
not effective, at this temperature outside drops a degree lower it further degrades the heat output .Power companies that finance Heat pumps typically will install an outdoor thermostat to prohibit the 2nd stage or electric heat strips from coming on until it is 40 or below outdoors, at a certain point well before 6 degrees a heat pump should be ran on the emergency heat mode which is the heat strips and the fan. Since 1500 Watt electric heaters are available at Wal-Mart for $20 the best alternative in this situation would be to buy a few of them.
Jun 06, 2014 | Heating & Cooling
Front grill
Check the air filter and if it is dirty, replace..
Turn equipment off and let the ice melt.
After ice melts, place a/c in cooling mode and set the thermostat to 3 degrees below room temp display.
The indoor unit fan should start blowing cold air immediately and then turn off once the room temp drops one degree below the cooling temp setting.
If the indoor unit does cycle off, check the outdoor unit and make sure it turns off at the same time.
If the outdoor unit continues to run and the indoor fan is not running, the indoor unit will ice up.
A defective compressor relay that is stuck in a closed position will cause icing of the indoor unit because it keeps the compressor running when it should turn off with the indoor fan.
Do you have an error code being displayed on the controller?
Is there an led light that is flashing on the indoor unit?
Another possibility causing the indoor unit to ice up is if the freon in the system starts to get low.
Make sure the ice has all melted for this next check.
Pretty easy to check without special tools.
If the air filter is clean and there is no dust/ dirt blocking the fins on the indoor unit, turn a/c back on to cool and check that the indoor unit fan comes on and is blowing air good.
Once everything seems to running good go to the outdoor unit.
There will be two lines with black rubber insulation covering them.
Peel back the insulation three inches on each line and observe the copper lines.
If either line starts to frost up the a/c system is most likely low on refrigerant.
Another cause of indoor unit icing could be that the aluminum fins behind the air filter are clogged with dust or other foreign material.
This would block the air that must be pulled in causing the indoor unit coil to become too cold due to lack of air flow and it will ice up.
Operating the cooling system when the outdoor temperature is below 60 degrees can cause the indoor unit to ice up also.
I'm Robert.
Florida certified a/c contractor. 30 years experience.
Hope this helps.
Mar 18, 2014 | Fujitsu Heating & Cooling
Comfort star
Make sure the indoor filters are clean. The outside unit will continue to run until the indoor reaches the temperature you have selected. Dirty filters can throw the temperature out. Its common for outdoor units to freeze up when on heating mode if the ambient air temperature is below 5 degrees Celcius.. The machine should however, defrost itself. There could be a problem with one of the pipe or air sensors on the outdoor unit.
Feb 23, 2014 | ComfortStar CHH012CD-13B Wall Mounted Mini...
My outdoor a/c wont come on diplay l.e.d lights off whats the problem?
To get proper cold air set temp 23 degree and mode"cool". To get heat set temp 30 degree and mode in "Heat" Wait for 3 minutes. If no green light shows, problem with indoor PCB.Repair or replace it.
Jan 13, 2011 | Mitsubishi MS24WN Air Conditioner
Why would cool air be blowing out of my central ac unit condensor that sits outside? The other unit I have next to it blows out warm air and responds well to thermostat changes. The unit blowing cool air...
It probably has a low refrigerant charge. The air coming out of the outside unit should be warmer than the outdoor temperature when in the cooling mode and if it's a heat pump it should be colder than the outdoor temperature in the the heating mode. Check the big line going to the unit, it should be somewhere around the 40 F range and the small line should be hot.
May 23, 2010 | Goodman CKL24AR24 Air Conditioner
Heats for 15 - 20 mins then blows cool air
If the outdoor unit is in defrost mode the compressor will be running but the outdoor fan will not. You may even see some steam rising from the coils. This mode is to prevent frost or ice build up on the outdoor coil. Essentially it goes into cooling mode w/o the outdoor fan running.
Mar 05, 2009 | Goodman GPC1342H21A Air Conditioner
Mitsubishi wall unit srk50zg condenser src50zg air con not heating new install
Double check your wiring .if the indoor fan is not blowing then you either have an electrical issue OR bad blower motor .
May 24, 2017 | Refrigerators
Mitsubishi MSZ-A24NA Split System Air Conditioner Logo
71 people viewed this question
Top Mitsubishi Heating & Cooling Experts
vince
D. E. Hev
Stuart Slabber
Level 1 Expert
Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others