I have a Vulcan Ducted Central Heater, about 7 years old It won't fire up The Combustion Fan starts and nothing else happens I have isolated the pressure sensor to try to isolate the problem I have found that no power is getting to the gas solonoid Does this point to the circuit board?
    President:
  • 1,654 Answers
If your not getting power to the gas selenoid, then the circuit board is not sending the signal. Your getting a signal from the thermostat, cause the combustion fan is running. To rule out the thermostat, raise the temp as high as it will go and let it cycle. You probably have already powered the unit down I assume and tried to reset it, if not then do that if the gas valve still won't ignite with the thermostat wide open. Also some units have seperate fuses or breakers. Check yours and check the board for fuses or bad spots such as bad capacitors that are bulging, leaking or split. Also I assume you have good gas pressure? no interuptions of your service?
Posted on Mar 26, 2011
Brivis ducted Heater won't get above 19 degrees ,
could be broken ducting letting hot air escape or on the intake side drawing too much outside air in. could be the fan unit not pushing enough air
Jul 26, 2013 | Cars & Trucks
I have a Vulcan Ultra 21E ceiling ducted unit The LED flashing fault is no 8 which is a gas interruption. The unit fan runs, ignition starts full flame and gas flows for about 2 secs then shuts down The...
Just been thru a similar problem with my Climate Technologies Vulcan High Efficiency Ducted Gas heater which in this case is installed under the house. This heater is about 7 years old and I have previously (2 years back) refurbished the controller by replacing the main power supply electrolytic filter capacitors.
I also had a communication problem with the Touch pad Thermostat which in the end required replacing the entire touch pad as one of it's voltage regulators had gone intermittent (Touch pads are available on E-Bay). To operate the heater while the touch pad was out of commission I installed a manual switch between the heat contacts on the heater controller. Closing the switch causes the heater to permanently run if it has no thermostat. Once communication with the touch panel was restored we were able to try and find the intermittent heater fault.
Again I have been getting Fault Code 08 "Gas Interruption" however the heater was lighting OK and then going out after about a minute or so. In the end I found 2 distinct heater faults.
Fault 1 was the flame sensor where the weld between the wire and flame probe rod had broken but it was still touching. This meant it was sensing Flame OK and then later would go open with expansion as the temperature rose. I fixed this by replacing the Flame Probe with a new one sourced from Reece HVAC.
At this point I celebrated thinking it was fixed!
Fault 2 after the flame sensor issue was cleared the fault still persisted but slightly less often.
The heater was cycling 3 times to get going and then locking out, requiring a reset from the touch thermostat or heater controller board. Sometimes the heater would achieve a onging burn for a long period, and other times just locking out after 3 tries.
Careful observation of the flame, through the observation holes after it lit, showed correct flame sensing but as soon as the nominal 65C duct temperature was reached the combustion fan (modulates) throttles back too far and the flame goes out, the flame sensor switches off and gas valve is then closed. The pressure differential across the burner manafold controls the Gas flow rate so if the combustion fan goes too slow the flame goes out due to lack of gas.
On the control board there is a potentiometer marked "MIN GAS RATE" this needs to be tweaked clockwise until the burner remains lit when the nominal 60-65C duct temperature is reached. Don't turn it up too far or the heater may not throttle back enough and end up going out on overheat.
Once a stable flame is achieved when throttled, try the heater in the economy mode which uses a lower recirculating fan speed and check the flame still remains lit. My problem was most obvious in the Econ mode.
Hope this helps someone else - It took me over a year to solve this one. NeilP
Aug 21, 2011 | Heating & Cooling
Hi, Vulcan " burwood " gas space heater.I have
As long as the burner works it is unlikly that the thermostat is your problem. It is more likly the fan limit switch needs replaced.Unfortunatly I am having no luck finding a wiring diagram for this model so I can't tell you where it is at,but I think that's the problem. Thank you. Sorry I'm not more help
May 19, 2011 | Heating & Cooling
Vulcan ducted heating system 530 E (5 years old) have replaced AAA batteries on remote control but still not working. Thanks Michael
You have to recode the remote to the heater if the batteries have been removed for more than 3 minutes. On the comfort control will the remote is in a off state turn the heater off at the power.
While off press and hold the up button and the on/off until code appears then release buttons and turn the power back on to the heater.
When code disappears from the remote turn on the remote set the temp higher than current temp and combustion fan should start up then heater will fire up.
If not repeat process as they are easily corrupted by other remotes.
Download control manual from - http://www.bonaire.com.au/support/documentation/owner/default.aspx
Set / check fan speed or it may overheat.
May 17, 2011 | Heating & Cooling
We have a Vulcan Ultra high efficiency gas ducted heating
Gas ducted central heater won't switch on all of a sudden
Nov 04, 2009 | Vulcan AUW230A Heater
Brivis central heating fan will not switch off runs continuous
brivis wombat 2P 20 ducted heater, gas fires up but fan not starting
Any suggestions...???
May 12, 2009 | Heating & Cooling
Vulcan ducted heating not working
How many wires for the thermostat do you have? If you tell me I can help. The green flashing, instead of red, in my experience, means a thermostat problem.
Feb 24, 2008 | Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen