I have a EB5000X Honda Generator and get a voltage of 127 volts on one leg and only 24 volts on the other on the 4 prong 220 plug. what is the problem. I get full 220 at the breaker
  • jerikofarm Mar 25, 2011
    I do not have 220 volts between any of the prongs. Is it normal to have continuity between ground and three of the poles on the 220 4 prong plug?
  • 3,740 Answers
Hi and welcome to FixYa, I am Kelly.
The ground is the upper left terminal of the 4 prong plug. Power is on the upper right terminal.
I am looking at your wiring diagram on page 50 of this manual:
http://www.poweredgenerators.com/honda/manuals/31Z22601.pdf
First make sure the 120 / 240 selector switch is on 240V
Once your sure that switch is in the correct position read upper left to Upper right
Next read upper left to bottom left
Last read bottom left to to top right
Let me know what your readings were.
Just from here it appears the 120/240 switch is either in the wrong position or there is a problem with that switch.
Ask as many questions as you like in your responses. I can and will help you.
Thanks for choosing FixYa,
Kelly
Posted on Mar 25, 2011
  • Kelly
    Kelly Mar 29, 2011
    Your comment:
    Generator running the output power switch / CB must be ON and the 120 / 240 switch must be on 240 to read any voltage at the 4 prong outlet
    ___Ground ____ 120 VAC
    ___ 120 VAC ____Neutral
    You will read continuity between all connections except neutral
    The neutral (bottom right) will read to the other 120 VAC outlets "Large" terminal regardless of CB Position.
    Check the stator windings. Open all CB's thenocate the terminal block (4 post) and read RED to WHITE (Main Winding 1) and then read BLUE to GREEN (Main winding 2) I think you just might have 1 open winding... BOTH windings should have equal resistance. If BOTH windings read the same continuity value then it is pointing right at the 120 / 240 switch as the problem area. Could be the switch or the wires on that switch.
    The fact that you read 127 VAC on one side and 24 VAC on the other side is telling you that your most likely missing 1 leg of power and one stator winding may be partially open. This would show up as a major resistance difference in your winding 1 & 2 checks. )R to W /1 and G to Bu /2)
    Kelly
  • Kelly
    Kelly Mar 29, 2011
    Forgot to mention this. If the winding checks fail don't assume the stator is toast. They use some in line connectors and often those in line connectors overheat from being loose and fail. I just get some heat shrink cut out the connectors slide on the heat shrink (away from area to be soldered), solder the wires together.. position the heat shrink over the splice and then shrink the heat shrink over the solder connection.
    Kelly
  • 5,603 Answers
Make sure you are reading the correct pins of the 4 prong plug. Capacitive coupling would give the low reading if you were reading from a hot one to the CASE type ground pin. You should find two readings of 120 between ONE of the 4 prongs and each of the hots and 240 between the hots. Between any hot and the safety (CASE) ground you will see a voltage that depends on the impedance of your meter and the electrical capacitance of the windings to the case. something up to 1/2 of the 120 volts would be expected so the 24 vollts would be perfectely possible.
It is important to identify which prong is the neutral and the two hots. The fourth prong then is a safety ground and UNLIKE your service entry of a residence, it is NOT tied to neutral at the generator.
  • Fred Yearian Mar 26, 2011
    Normally one of the contacts should have continuity to the frame. The other three should have continuity between themselves. HOWEVER this is ONLY if the voltage selector is in the 120/240 position. You will probably find 120 between two prongs and only capacitive coupling IF the switch is in the 120 position. In other words, what you are seeing is perfectly normal IF the voltage selector is in the 120 position. The two 120 volt windings are connected in parallel for 120 only operation and series for the 120/240 operation.
2 Suggested Answers
  • 497 Answers
SOURCE: Honda Generator 3500 - Using the air conditioner
A couple of questions come to mind. 1. Has this always happen or is this just recent? If its always happen you might be running the a/c on a breaker not strong enough. On the a/c unit on the back there should be a metal plate with the Volts, Amps required to run the unit. Make sure the breaker is rated higher then whats required. If that all checks out you could very well have a malfunctioning breaker. Its a cheap fix to try to replace. If that doesnt work then one can only assume the a/c unit or your generator is malfuntioning.
Posted on Aug 10, 2009
Generator no longer puts out 220?
If your generator is not putting out 220 volts then possibly one of your legs when I mean your power legs right you understand what I mean by that it's it's still not was going to be a dual phase power it's alternating current so one of the legs are going haywire and that's what's causing you to lose 2:20
Jan 31, 2018 | Electrical Supplies
Honda ex5500 generator over voltage output
adjust the rpm back to 115-120 volts
or increase voltage to 220-245 volts
Nov 25, 2017 | Honda Electrical Supplies
Back up generator 240 volt output is off balance?
So there is a problem. Where are you measuring voltage?
Say there is L1 - N - L2. Line1 to Neutral is 120 volts, Line2 to Neutral is also 120 volts, Line1 to Line2 is 240 volts. N or Neutral ( the grounded conductor ) is center tap between line 1 and 2.
With this system, the N wire carries the unbalanced load in amperes .
Now we are talking of L1 and L2 and amperes. When L1 and L2 are conducting 10 amperes each, N carries 0 amperes, Line1 and L2 are balanced. When L1 carries 10 amperes and L2 carries 5 amperes, Line1 N carries 5 amperes, the difference of L1 and L2. This is normal.
When there is a problem with a loose connection on N, there is a resistance and will not carry the unbalanced load normally, the voltages will Chang's under load, the problem will worsen with time, a fire hazard, connected loads may burn up from excessive voltage or not work at all.
Bottom line: Make sure the N line ( white wire ) is tight at every connection and inspect for overheating damage. You may have to open the generator connections panel to check there too.
Aug 06, 2017 | Electrical Supplies
The generator produce onely 73 volts ac on the 120 volts plug and 146 volts ac on the 220 volts plug . what could be causing this problem
Check all wiring and fuses associated with you voltage regulator if they check ok, find a way to adjust your voltage regulator replace it. Make sure the unit is running at 3600 rpm as well and making 60 hz.
Jul 10, 2011 | Coleman Powermate Premium Plus 6250W...
My GE PGS975 DEP1 (GAS RANGE) DIGITAL CONTROLS ARE NOT WORKING. I purchased this brand new gas range in the USA and had it shipped to Brazil. After i installed it and plugged it on every think worked...
Power supply in Brazil is not universal over the entire country. Your range was built for 120 volt, 60 Hertz power supply. If you are in some areas, you may not have the proper voltage available. 127 V found in states of Bahia, Paran? (including Curitiba), Rio de Janeiro, S?o Paulo and Minas Gerais (though 220 V may be found in some hotels). Other areas are 220 V only, with the exception of Fortaleza (240 V).
Brazil does use 60 Hetz, but if you are in an area which only supplies 220 or 240 volts, you would need some type of adapter to convert that to 120 volts for your gas range. If you connected to the higher voltage, you may have irreversably damaged the electronic control, requiring control replacement, before connecting to the proper (120 volt) supply. I would expect 127 volts to operate your range, but if the voltage varied up from that, it could damage the control. Even in the US, voltage variations of 108 to 125 are rather common.
May 22, 2011 | General Electric Profile PGS908 Range
I have a coleman powermate 6250 generator with a 4prong 220v female plug on the power panel. My travel trailer has a 3 prong male plug. How can I convert my generator or is there an adapter that I can...
You do not want to convert anything to a 220 v connection !!!! Your RV is 12 volt DC and 120 volt AC.
Use a 30amp female to 15 amp male adapter to plug in to regular household receptacle on generator. Available at hardware store and RV stores.
Apr 27, 2011 | Coleman Powermate Premium Plus 6250W...
7 hp brigs engine on my generator runs two fast producing 127 volts. how do I slow it down?
Hi and welcome to FixYa. I am Kelly. Since you did not mention the make or model number of your generator I will respond in generic terms. If your generator is at 127 volts with NO load it is adjust at the very top end of the manufacturers limits. There is a 10% tolerance so 120 VAC + 12 is 127 VAC. Under an electrical load above 500 watts the generator should drop the output voltage slightly so your generator would still be within factory limits. Personally on any generator as a repair person; I set the output voltage at 126 VAC no load so that when the user puts the generator to work the output voltage is good. If your generator is running at 127 VAC under load then you can adjust the governor screw on the governor plate CCW about 1/2 turn to drop the voltage. Without a generator model number or engine number I can not tell you exactly where the governor plate is on your engine / generator. The screw will have a lock nut that you must loosen 1/4 turn then turn the adjustment screw CCW to drop the voltage. Just make sure to re-tighten the lock nut when the adjustments are complete. Mind you by decreasing the output voltage you also drop the output freqency at the same time you decrease the output voltage. It is better to have 125 -127 VAC under a no load condition as the more electrical load you add the more voltage drop you will notice. It is best to adjust the generator to 122.5 -123 VAC under a medium load. (50% of output capacity) A bread toaster is 1400 - 1600 watts and is a good load for a 3000 watt generator. Also a good hand held hair dryer will use around 1600 watts. If you use this type of load and the voltage output is 122.5 to 123 VAC I would not adjust anything. I have been working on generators since 1970 so this is nothing new for me. I hope that you understand everything I posted. If not, feel free to ask as many questions as you wish in any future response.
Kelly
Jan 08, 2011 | Craftsman Electrical Supplies
Ac wiring problem
as a general rule ,only if your ac was a window unit. aka a 120 volt unit . all other acs use 240 volt. a 120 leg and a 120 2nd leg to equal 240, so there is really no common. what kills acs with a generator is the lack of watts and starting torque. an ac (3 ton) and up needs a generator of 10000 watts minimum to handle starting trque. they also need a hard start kit to boost starting voltage.for god sake someone reply and tell me what a good job i am doing!!!!!!!as in grade the response to your question.
Oct 17, 2008 | Dometic Rooftop RV Air Conditioner
Run ac off of generator.
you need to use a volt meter and test which lead from the 4 wire output of the generator a 220 v is coming out.
the round center prong of the ac is its ground and should not be connected to any live power. it could be left unused.
tnx 4 using fixya,
drcool
Sep 27, 2008 | Hampton Bay HBLG5004 Air Conditioner