My furnace is telling me that i have an open pressure switch via the trouble code on the circut board. its a weatherking furnace jmercadante01@hotmail.com
  • 43,501 Answers
If the pressure switch is open, that means that the inducer is not moving enough air to close it, the pressure switch is bad, or the heat exchanger may be cracked.
Check for air flow...go outside and see if air is coming out the vent pipe....make sure there is no water built up inside the vent pipe.
Make sure the air intake pipe is ope and not clogged if you have a two pipe system...
Check the small hoses by the furnace for cracks or water in the hoses...
Check for condensate buildup inside the heat exchanger...
A cracked heat exchanger can also cause a lack of pressure and or pressure differential....
If everything else checks out then you may have a bad pressure switch... they DO go bad...
Here is a tip that will help you try to figure out why yourfurnace is not working.
BasicFurnace or Heating System Troubleshooting
heatman101
Posted on Mar 24, 2011
Testimonial: "It was a bad circut board. "
Ever limit switch i changed in my Weatherking furnace, it breaks the switch, what could cause this?
You need the model number of the furnace to determine what the flashing light is telling you. Many times the part that looks to be at fault is not the true fault in the furnace. A slow running blower could cause the limit switch to trip. The circuit board tells you that the limit tripped, but the real cause is the motor or clogged filter.
Jan 02, 2016 | FACTORY AC PARTS Limit Switch Double Pole...
Tip
Trouble shooting your gas Furnace
If you are having trouble with you gas furnace they are really not that complicated to figure out. Most of the newer gas furnaces within the last 10+ years have a flash code on the circuit board inside the furnace. The trouble codes are in flashes. For example: 1 flash means ignition problem, 2 flashes mean vent pressure switch, 3 flashes means control board problem and so on. The first thing to do would be to check for a sight glass or window in the blower door to see if there is a flash code. Then you can pull off the blower door to check to see what the code represents. The code chart is usually located on the inside of the blower door.
If there is no flash type board in the furnace it still pretty simple to trouble shoot. First thing is verify that you have power to your furnace. You can do this by checking voltage with a simple meter. Check for voltage at the door switch since this is usally where the power starts. If there is power there then check for voltage at the thermostate between the R terminal and C for common. If there is power there then you need to go back to the furnace and try to figure out where the power is stopping. With the power to the furnace off start to check the safety switches. With an ohm meter or a test light you can start checking for continuity across your safety switchs. Check the roll out switch that is located near the burners if thats okay, Check the high limit that is usually located up higher on the front of the furnace that has two wires going to it, if that is okay then check your pressure switches and these you will have to check with the inducer or vent motor running. Hope that this information is helpful and if you don't feel comfortable using an electrical tester be sure to call in a professional HVAC Tech. to look at it.
on Dec 20, 2009 | Heating & Cooling
How do i bypass the pressure switch for troubleshooting
most of the time you can't bypass the pressure switch because the circut board won't let you. You can however check the voltage or ohms of the switch and this will tell you if it works. On a call for heat the inducer fan starts, then the pressure switch should close contacts and send voltage through. Find common on the terminal block and put one lead on that and one lead on either side of switch and voltage should be found on both sides or remove the wires and ohm it.
Sep 21, 2014 | Heating & Cooling
Gas valve wont engage -weatherking furnace troubleshooting
Depends on the system,if it has 2 wire switch it can be bypassed,but only 1 time for each heating cycle if the system is using i pc board to operate the furnace,sometimes you can take the hose off and lightly suck and blow on it if the switch is stuck,but should have a pro check it,could be a blocked flue pipe or other dangerous problem,and could be a bad switch,did heating and cooling for 30 years
Mar 08, 2013 | Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
Dec 12, 2009 | Heating & Cooling
Weatherking WRKA heat not working control board
U need to supply more info.There will be a sticker on the furnace likely in the lower Fan Compartment which will have a legend that explains each error code...ie: 3 blinks = Pressure switch etc....and u will need to provide more info on how the furnace is operating (whats it doing ) when it stops working or just prior to that
Oct 16, 2009 | Heating & Cooling
York Diamond 80 Issue. AC and Blower work fine. Heat will not come on. Circut breakers are fine, all power is on. Any advise.
Open the furnace door. Turn the thermostat on, and hold the power switch on. Look for the service code on the control board. That should tell you whats wrong with it. www.FastACservice.com
Oct 12, 2009 | Heating & Cooling
Weatherking furnace flashing 5 times.......
Sounds like it it isn't the igniter but probably the pressure switch. You can only tell by the clicking noises as they system goes through it's safty checks prior to the call to the igniter.
Mar 05, 2009 | Weather King 12AJA4801AH Air Conditioner
Shutting off on pressure sw. 2 yr old goodman counter flow 80+
the problem is your gettign a code and the legend is telling you its the pressure switch? From your description.
Well it is going to be rather difficult for you to check the switch without a .10" gauged water manometer gauge. It would be easier and cheaper for you to purchase another switch but if its only 2 years old the factory warranty is usually 5 years on parts. All you'd owe for is labor and freight if you have to have it sent to you. Take your model and seril no and go to who you purchased iot from and tell them what code your getting.
Some of these pressure switches and the boards that control them look for the switch to acuate both ways on and off knowing that the switch is actually working and not stuck. So you could start out by jumping the correct NC normally closed circut turn on the furnace and remove this jumper and then close the NO normally closed circut with a jumper. This isnt a fix but may help you see if the switch is actually at fault. If you get it to lite off let it cycle back off and note if it works all way through the cycle. If it does Your problem is most likely the switch because you just did all it does only by hand. DO not leave it this way because you can cause a more seveer problem and it is can develope dangerious consequences. This is just 1 way to check the switch. Another way is to check it electrically. If your femilur with open and closed circuts check across the closed and open circut whith it off then with it running and (if it has 3 terminals wires in, if it just has 2 wired in then it is not going to look for one of the operations Ive discribed). And then check and see if the voltages reverse while beginnign to lite off. If it does reverse Im betting you have a different problem and the swich is what the board has been told is giving the trouble.
Hope this is clear. If not get back to me. If it helps please grade me accordingly. THANK you and GOOD LUCK
Mar 04, 2009 | Goodman GMS90703BXA Heater
Weatherking Short Cycling
You make a good point about overheating on heat exchanger temp.
Since you don't have to reset anything for it to recycle, then I assume you have one of the newer forced draft furnaces.
There should be leds on the control board inside the furnace compartment that will blink a code to you, telling what the shutdown reason was. Blinks and code should be on a label inside the blower door panel, or inside the control box cover.
Let me know what they are, and I can give you more direction. I am assuming this furnace worked at some point, and no changes have been made (including closing of duct vents).