    Gas charge has been checked and reported ok. The behavior is erratic. Sometimes the machine will run for 45 mins, then the outdoor unit will stop, re-start after around 5 mins, run for maybe 10 mins, stop again and then continue this stop-start cycle. At other times, the outdoor unit stops very soon after the machine is started. I did notice that the outdoor to indoor cable is of 3 cores and, so, there is no ground conductor between outdoor and indoor units. The machine is a Mitsubishi Starmex Single Split Non-inverter unit.
    The filters, coils, etc.are clean and there is no dirt around. The machine is relatively new - about 9 months since installation.
    President:
  • 2,047 Answers
This s seldom normal with Air conditioning units to stop and restart at periodic intervals usually it is as a result of the temperature of the unit which fluctuates. The thermostat is always responsible for this function as it regulates at what temperature the unit cuts of power to ensure the life of the unit lasts quite a while.
Bt if the time at which the cut off takes place is shorter than usual then this is a sign that the thermostat is becoming weak and would need replacement as the level of heat resistance it can take has reduced. This diagnosis is a general one with air conditioners so get an expert to identify the location of the thermostat so you can order a replacement part for it.
Hope this solution has been helpful?
Posted on Mar 24, 2011
  • Mitsubishi Master
  • 43,501 Answers
The most common cause for the unit to cycle like that would be a low charge situation.
If you are low on freon the unit will cutout on low pressure and then when off the pressure will go back up and the cycle starts all over agian.....
Get a certified professional to check the unit out and fix the leak so that once recharged the unit will hold the freon.
The most common place for them to leak is the piping connection behind the indoor unit...although it could be the connection at the outdoor unit also...
These are flare connections and they can and do loosen up over time from the vibration...
heatman101
  • D. Floyd Kolb
    D. Floyd Kolb Mar 24, 2011
    No the calce should not be the problem, but the next thing that I would check would be to take off the thermistor that is on the indoor coil... this tells it to stop, then the coil warms and it restarts...this is to keep the indoor coil from freezing to a block of ice...
    Either the indoor coil is running too cold or the thermistor is bad...
    Make sure the air filter for the indoor unit is clean and that the coils are not plugged with dirt...there needs to be good air flow through the indoor coil...
    by removing the thermistor and pulling it away from the coil a bit you can tell if this is what is causing your problem...
    heatman101
  • D. Floyd Kolb
    I would be suspecting the thermistor on the indoor coil...
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
National geographic weather trouble shooting
The order of replacing batteries is important. The outdoor unit batteries first, then the indoor. You wait 10 minutes until the outdoor unit starts sending data.
Jun 16, 2014 | Televison & Video
Why is Mr Slim MS-SGF24VC outdoor unit working when indoor unit off
Possibly a bad control board in the outdoor unit. Pull the disconnect outside to stop machine, wait 10 seconds and out back in. White mist was likely frost built up on indoor coil due to condenser running without the fan.
Jun 11, 2017 | Heating & Cooling
Hi I have a goodman MSG-18HWN1 heating and cooling mini-split unit. The unit keeps going on and off on a cycle of about 5 minutes. 5 minute, unit not started, unit starts for about 5 minutes, stops for...
Due to abnormal temp of out door.Check outdoor fan motor and compressor and also sensor.
Fan motor not working- rectify/replace fan capacitor.
Sensor defective-Replace it
Compressor high amps-Replace running capacitor.
Sensor misplaced or defective-Place correctly or replace it.
Jan 05, 2011 | Heating & Cooling
Indoor unit does not function -outdoor unit works
These units have circuit boards inside that have lights on them. These lights come on and tell you what the problem is. I have had 4 units do the same thing that yours is doing. The result has been that the compressor has gone bad. You have to get access to the control board to see the lights. There will either be one inside the inside unit or one inside the outside unit depending on exact manufacturer date.
Good luck and hope this helps.
Aug 22, 2009 | Heating & Cooling
Mitshubishi split muh-18nvand inside msh-18nv
-Start the unit.
-Press EMERGENCY OPERATION switch.3-minute time delay works.Test run operation operates for 30 minutes.
-Check voltage to terminal block of outdoor unit.Is there 12V DC between 2-1?
-If voltage is presenet check the wiring, compressor contactor outdoor fan motor and compressor.
-If no voltage check voltage to terminal block of indoor unit.Is there 12V DC between 2-1?
-If if voltage is present re-connect the continuity of indoor and outdoor unit connection.
-If no voltage replace the indoor electronic control P.C.
board.
-But also check the coil thermistor sensor and room air thermistor if this two is out of range it can cause the tripping of out door unit. It has the resistance of 8 to 10 k ohms at 25 deg c temp.
Jan 04, 2008 | Heating & Cooling
Art cool keeps stopping
Try to unplug the unit or “off” after 10sec. “on” the circuit breaker and then start the unit.
But if the defect persist then you need a qualified technician. The below error may be the cause of unit failure.
- Out of range thermistor is also can also be the cause of tripping outdoor unit with matching blinking light same as low refrigerant.
- Dirty indoor and outdoor can also be the cause
Remote control units have diagnostic program in the
control, after 3 to 5 minutes of operating if the diagnostic
tools detect abnormal operation, then its shutdown the unit
to protect from damage. Thermistor sensor is one of the
parts that detect the operation of the unit. Out of range
or defective thermistor can shut the operation of the unit.
- If your indoor and outdoor is clean start the unit in cool mode and monitor the outdoor pipes. If your suction pipe is icing or dry then your unit is under charge, but if your suction is cold and sweating then the system is ok and sure that the thermistor sensor is defective.
- Out of range thermistor sensor in both return air and freeze up sensor can cause the tripping “off “ the unit. The resistance of both thermistor is 8 to 10k ohms, so can test by using ohm meter
Dec 26, 2007 | Heating & Cooling
Mitsubishi MSZ09UN Air Conditioner Logo
242 people viewed this question
Top Mitsubishi Heating & Cooling Experts
vince
D. E. Hev
Stuart Slabber
Level 1 Expert
Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others