I have 1990 Armstrong gas furnace Ultra III 80, Model EG6G75dc8-4 .\r\nWhen I turn thermostat up , furnace comes on, burners come on, motor that I believe turns blower turns on but i AM NOT GETTING AIR blowing IN MY DUCTWORK, any suggestions ? Thank you
  • 1 more comment
  • Robert Mar 22, 2011
    Does the blower motor turn on?
  • vulcand2 Mar 22, 2011
    I checked again and the inducer motor comes on, the motor that blows out the exhaust vent.
    The Blower motor near the bottom of my furnace does not come on, I check the Door switch, and when I toggle that door switch my burners come on and stay on, but blower fan does not come on.
    Check to see if you are getting voltage to the motor at the low speed motor tap on the control board and neutral. If you are thn check the capacitor, but discharge it first with a insulated screwdriver. Then take you meter and set it to ohms, the meters numbers shouls ramp up and down if not replace the capacitor.
    Scholar:
  • 120 Answers
Have you checked your filter yet? the other thing to check is open the fan door and jumper the door switch,if there is one, and turn the furnace on. is the fan blowing air now?
Posted on Mar 23, 2011
I have an Armstrong SX Ultra 90 propane gas furnace that the fan motor will not shut off ,the thermostat is on auto.
Hit the side of the furnace. Some times there's a sensor inside that gets locked up from a dirty filter.
Oct 19, 2013 | Emerson Lennox Ducane Armstrong Furnace...
Furnace burners won't ignite
Assuming this is a gas furnace, when the thermostat calls for heat the pilot heats an igniter to produce voltage that opens the burner gas valve. In your furnace, the igniter may have failed and the burner can't fire up
Mar 09, 2013 | Sport & Outdoor - Others
Turn main furnace switch on, combustion air fan comes on and main circulation fan comes on. About 40 seconds later the igniter lites, two burners closest to the igniter fire up and immediatly snuff out....
Hello, if all the burners are not firing up then they must be cleaned out, usually dirt gets in the crossover parts of the burner and the gas cant flow to all the burners and therefore the flame sensor will turn off the furnace for safety. Clean the burners out this should fix the problem.
Feb 25, 2011 | Heating & Cooling
I got a free armstrong ultra iii 80 lp downflow furnace and would like to install it in my garage but to make more room can i install it horizontally?
If it has an induction fan it will pull the flames through the heat exchanger however you put ... be sure to vent it properly to the outside.
Jul 10, 2010 | Heating & Cooling
Gas Armstrong Ultra V Tech 91-Is green light supposed to flash?
Installed a new filter and furnace is running great now. The old filter was not that old, but we have been doing some remodeling and I figure that is what clogged it so fast.
Jan 10, 2010 | Armstrong H 67 1PH Bf In Line Circulator...
I have an americanaire ultra sx 80 furnace that if it does start up the 1st time, the induction motor continue to run and it will not start
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 04, 2010 | Heating & Cooling
Armstrong ultra sx 80 furnace starts up and runs and then the gas shuts off for a few seconds and then lights backup and causes a small backfire my Ultra sx 80 furnace will ignite then immediately turn...
You have a dirty flame sensor. Look at the very last burner and you will see a wire going to a ceramic sensor and it looks like a thick wire. Take some steel wool or fine sandpaper and clean the surface off and it will work like a champ.
Let me know how it goes ken
Apr 15, 2009 | Heating & Cooling
Flame sensor could be dirty. It is located right beside the last burner looks like a thick piece of wire. Take steel wool and gently clean the probe 4 or 5 strokes is all it will take to take off the carbon build up off. Lets eliminate this item and see if it clears up okay. ken
Dec 21, 2008 | Heating & Cooling