Honeywell Ignitor clicks several times before actually igniting, replaced old one, still have the same problem. Also replaced the smart valve.
  • Nelson Mallon Apr 11, 2011
    Problem was a build up of condensation (water) in the inducer motor...after cleaning out the condensation line I needed to pull off the inducer motor and dump out the water that was in it...no more problem after.
  • Honeywell Master
  • 3,284 Answers
Check air filter is clean , or jump out pressure switch see if it lights, check hoses to pressure switch are not split or blocked
Posted on Mar 22, 2011
I have a 10 year old honeywell furnace controlled by a SV9541 smart valve. We finally had to switch to heat but no heat. Tried restarting - system does nothing. Checked to make sure the gas line is open...
Sounds like the Ignitor unplug the ignitor check for continuity if no continuity replace Ignitor or you can usually see the crackon the Ignitor with white residue.
Sep 18, 2013 | Honeywell Programmable Thermostat Heater
I have installed honeywell aquastat relay per instruction manual on my dunkirk xeb-4 lp boiler furance with honeywwell ignition unit s8610u but it wont ever start the exhaust fan checked everything several...
If aquastat wirings are ok, and control module had been set up properly, the the furnace should start.
Check if bypassing the control the furnace starts, if it starts then check aquastat wirings.
If it depends on the furnace, check the valve, the safety sensor and the ignitor.
Here is the guide to set up the Aquastat control:
Guide to Setting & Wiring Heating System Boiler Aquastat Controls
Sep 13, 2008 | Honeywell Heating & Cooling
Armstrong GUK125D20-2B won't ignite
Did he check the Pressure switch was it filled whit water can you make the switch open on the pressure switch when blowing on it? Is the hose from the inducer motor opened and not blocked ? also if there is a block after the inducer motor it will not Ignite. If the Tech does not know how to check a pressure switch get a new tech.
Oct 06, 2012 | Honeywell Furnace Air Pressure Switch...
I have a frideadaire furnace 80 or 90 with a honeywell valve VR8205S2288 i just installed the furnace , it turns on light on the board is on , can see the igniter getting red hot ,i can feel a double
No on the 220 that system board is standard 120 Vac.
Please check again if there is gas. New installations sometimes have air in them and they need to be bled - removing the air by purging. Your description leads me to assume your call for propane gas from you electronic valve cycling on and off. Your ignitor is getting red hot which is the first stage.
there is however a infra-red sensor which opens the electronic gas valve when I sees the glowing infra-red ignitor. If it fails to see the glowing ignitor it will not open the gas valve. Look for a glass type window plate which should be or next to the ignitor. This plate could be blocked or need to be cleaned. If not then most likely the infra-red sensor may also need to be replaced
Jan 25, 2018 | Heating & Cooling
Hi I have a Rinnai 100f Space Heater. Found it with a blinking red light.. Whe I shut it off to restart it. It restart by hearing the combumsion fan start up then go off with error code 53. Manual says...
Could be one or several issues here.Here is how system works first the combustion motor started then pressure switch closes (that's the part with the small hose connect to ),make sure all exhause is clear. Now when that closes and all safety ok then gas valve open then furnace ignite.
If you have 24 volt to gas valve and could hear valve open (a clicking soind) and no ignition then you have a ignitor issue .if it's a glow type ignitor it should glow ,if not replaced .If it's a spark ignitor you should be to hear it sparking .Normally a spark ignitor will have a orange hose going to it .Trace orange hose back to board and disconnect from board then check for voltage from metal pin that hose was connected to ,you should have very high voltage and should hear it clicking ,If all safety is good ,pressure switch is good ,gas valve is open and no spark from ignition board then board is bad.If you can hear spark from board and getting high voltage then replaced ignitor or try cleaning it out with sand paper most time that healp
Feb 04, 2018 | Heating & Cooling
Gas furnace with Honeywell smart valve code error 6:2, replaced the following: pressure switch, smart valve, ignitor flame sensor and control board. Cleaned out the condensate line. Still getting 6:2 flash...
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
Mar 08, 2011 | Honeywell Heating & Cooling
Our Honeywell programable thermostat keeps clicking and furnace isn't turning on. Changed the batteries but still doing the same thing. Suggestions?
Clicking is the sound of the ignitor trying to ignit the gas. Check to make sure the gas valve is turned on, the gas **** is in the on posistion. If they are you will need to replace the gas valve.