To replace it, you'll need to know whether it's a Robertshaw or Maxitrol Valve. As well as the Model number of the valve and whether it's Natural Gas or Propane Gas. Unless, you're really experienced with working on gas appliances, I would not recommend this as a DIY project.
Hope this helps solve your problem.
Posted on Mar 21, 2011
Marey tankless hot water heater 16ng
turn down gas and turn down pressure switch
Aug 02, 2017 | Water Water Heaters
Tip
How to Change the Gas Valve and Thermostat on a Hot Water Heater
<p>If you are having<b> trouble with the temperatures</b> of your <b>gas hot water heater</b> fluctuating too much, or after <b>changing the thermocouple</b> of your gas <b>hot water heater</b> then you may need to change the complete <b>gas valve and thermostat assembly</b>. Also if you have changed the <b>thermocouple</b> and the pilot still will not stay lit, then the gas valve could be bad or the <b>ECO (Emergency Cutout)</b> may have activated and is open. This is a onetime device and cannot be replaced.<br /> <p><br /> <p>These instructions are for the older style <b>gas valve and thermostat combination</b>. These commonly have a large red knob that adjusts the temperature of the water. Also note that the burner tube nut for <b>natural gas</b> is right hand thread, but if you have <b>LP or propane gas</b> the burner tube nut is left hand thread.<br /> <p><br /> <p>The newer <b>gas valve thermostat combinations</b> that have come out recently are similar, but they have a well in the tank that the sensor slides into. The assembly is held fast with a set screw. With this type of <b>gas valve and thermostat unit </b>the tank does not need to be drained, but most of the rest of the change out is similar.<br /><br />To change a <b>gas hot water heater thermostat</b> you will need to first buy a new gas valve for your <b>hot water heater</b>. The <b>gas valve</b> and the <b>thermostat</b> are integrated into one unit.<br /><br />To <b>replace the thermostat on a gas hot water heater</b> you must follow these procedures....<br /><br />1. Turn off the incoming water and<b> drain the hot water heater</b>.<br /><br />2. Remove the <b>pilot tube</b>, the <b>burner gas tube</b> and the thermocouple from the gas valve. Turn off the <b>gas line</b> and remove from the gas valve.<br /><br />3. Get a <b>pump pliers</b> or a<b> wrench</b> in behind the gas valve and turn the whole assembly CCW to remove it from the tank.<br /><br />4. After applying pipe dope or tape to the new gas valve threads, turn the new gas valve into the tank by turning in a CW direction. Be careful not to damage the small wires to the <b>ECO</b>. They are the little red wires on the back. If you break them the assembly is irreparably damaged.<br /><br />5. Reinstall the gas line, thermocouple, burner tube, and the pilot tube to the gas valve.<br /><br />6. Fill tank with water. Make sure to open a <b>hot water faucet</b> and <b>purge all air from the tank.<br /><br /></b>7. <b>Check for leaks</b> where the gas line hooks up with soapy water.<br /><br />8. Relight pilot light and check operation.<br /><br />9. Set the new temperature setting to a medium setting and then adjust the temperature to your liking from there and adequate time for heating completely<br /> <p>
on Feb 25, 2011 | Water Heaters
Heater comes on with water
please see the next step:
he pilot light may be out or may not stay lit. There may not be enough hot water, or the water may be too hot. The water heater may leak or be noisy, or the hot water may be dirty.
A problem with your water heater may be due to overwork, not mechanics. If your water heater holds less than 15 gallons per family member (tank volume is stamped on a metal plate affixed to most water heaters), consider a larger unit or staggering your use of hot water.
Drain a hot water tank:
  1. Turn the gas-control knob to off and close the gas-shutoff valve.
  2. Close the cold-water supply valve and open a hot-water faucet in the house to speed draining.
  3. Attach a garden hose to the drain valve and run it outside to a drain. If the heater is in the basement you may need to run the hose to or through a sump pump.
  4. Open the drain valve and allow the tank to drain.
  5. Once done, close the drain valve, open the cold-water supply valve, and open any nearby hot-water faucet. When a steady stream of water flows from that faucet, the tank is full; close the hot-water faucet.
  6. Once the tank is full, turn on the gas and relight the pilot.
Jul 31, 2012 | Heating & Cooling
Our rheem pronto tankless rutg-74xp red light will come home indicating hot water and stay on about 2 minutes and then turns off we have turned off and back on and let water run for 5 minutes and will come...
Before calling service technician, open following link for Rheem troubleshooting resources.
http://waterheatertimer.org/Troubleshoot-Rheem-Tankless-water-heater.html
List of causes MIGHT include one of following:
Bad household circuit breaker that powers electronics, or loose wire inside outlet where tankless plugs in.
Tankless fuses and control board.
Water flow rate too low. Minimum .8 gallon required (depending on model)
Tankless inlet filter clogged.
Household aerators clogged at faucets.
Crossover at single-handled faucet
If installed, there can be crossover at mixing valve.
Faulty household check valve, including check valve on re-circulation system if that system is installed.
Restriction in household water line, such as clog at elbow.
Unequal pressure in household hot and cold lines, caused by restriction in hot line. When single-handled faucet turns on, the cold water pressure is higher so hot does not flow and tankless will not turn on.
Loose wire connection inside tankless.
Unit temperature set too high.
Unit temperature set too low.
Water temperature is very hot coming out of tap, so more cold is added, but that reduces amount of hot water flow, so tankless turns off because flow rate is too low.
On some tankless, if water is preheated by solar or other indirect source, the burner will not activate.
High mineral content in water > delime tankless yearly
Misaligned temperature sensor
Low gas pressure. Wrong type of gas. Undersized gas line.
Too many faucets on at same time.
Faulty tankless water valve. Water valve stuck.
Fluctuating household water pressure, for example MUD and PUD district water pressure problems or water well pressure.
Faulty household pressure reducing/regulating valve if installed.
Faulty household pressure tank, if installed -or- pressure tank needs to be installed.
Apr 24, 2011 | Rheem RTG-74PVN-2 Natural Gas Pronto Whole...
I have a reliance 501 propane gas water heater how do i change a thermostate
To change a gas hot water heater thermostat you will need to first buy a new gas valve for your hot water heater. The gas vaive and the thermostat are integrated into one unit.
To replace the thermostat on a gas hot water heater you must follow these procedures....
1. Turn off the incoming water and drain the water heater.
2. remove the pilot tube, the burner gas tube and the thermocouple from the gas valve. Turn off the gas line and remove from the gas valve.
3. get a pump pliers or a wrench in behind the gas valve and turn the whole assembly CCW to remove it from the tank.
4. After appliying pipe dope or tape to the new gas valve threads, turn the new gas valve into the tank by turning in a CW direction. Be careful not to damage the small wires to the ECO. They are the little red wires on the back. If you break them the assembly is irreparably damaged.
5. reinstall the gas line, thermocouple, burner tube, and the pilot tube to the gas valve.
6. Fill tank with water. Make sure to open a hot water faucet and purge all air from the tank.
7. Check for leaks where the gas line hooks up with soapy water.
9. Set the new temperature setting to a medium setting and then adjust the temperature to your likeing from there and adequate time for heating completely.
heatman101
Feb 23, 2011 | RELIANCE ELECTRIC WATER HEATER
The water heater red light keeps flashing rapidly on my Powervent 2 model 41VRP40N. It is not producing hot water and when I read the manual it says it needs more heat. What does this mean. How do I fix...
There are many things to check. The single most important test is for 24V at the gas valve after the ignitor is supposed tp be on. 19 V or less and there is either a bad ground or the ingition control board has failed. (Wire ground problems are a high probablilty)
Here is what the book says:
PROBLEM #1 - HOT SURFACE IGNITOR DOES NOT GLOW RED
(Remember to wait for purge time, 17/34 seconds, on models so equipped).
Possible causes
A. No main power
B. Faulty transformer
C. Faulty thermostat
D. Faulty limit switch
E. Faulty blower interlock switch
F. Faulty hot surface ignitor
G. Faulty ignition control
Solution
Step #1
Perform normal system checks of main power, transformer, thermostat, limit
switch, blower interlock switch, and replace faulty component.
Step #2
With power on and thermostat set at its highest position, check voltage
between "TH" and "TR" on HS780 ignition control. If 24 volts is not present
check output at transformer. If no, replace transformer. If transformer
checks out OK look at other controls in the 24 volt circuit I.E.: thermostat,
limit switch, blower interlock switch. Check for 120 volts between "neut"
(L2) and "120" (L1). Check for 120 volts at the ignitor across "IGN" and
"IGN" terminals on the HS780 ignition module. If 120 volts is present,
replace ignitor. If no, replace the 780 series module
PROBLEM #2 - IGNITOR GLOWS RED BUT MAIN BURNER
WOULDN'T LIGHT
Possible causes
A. Improper ignitor alignment
B. Faulty ignition control
C. Faulty gas valve
D. High inlet gas pressure
E. Polarity reversed
F. No earth ground
Solution
Step #1
Check for availability of gas at gas valve. Make sure the manual valve
upstream of the gas valve and the gas valve are in the full on position. Also
make sure gas is being supplied to the system at the proper pressure, too
high will lock-up the valve.
Step #2
Check proper polarity of "NEUT" and "120" on the ignition control by reversing
the wires, if reversed gas valve will not open. If this does not solve the
problem, replace wires as they were.
Step #3
Check for proper ignitor position.
Step #4
Check for a good earth ground by using a meter connected between L1
and furnace chassis. Should read 120 volts, if no, check and/or repair ignition
ground wire or ignition control mounting screws.
CAUTION POLARITY MUST BE OBSERVED
Step #5
Check for 24 volts at the gas valve terminals; "1" and "2" on a 7200 series,
"M" and "C" on a 7100 series, "TH" and "TR" on a 7000 series. If yes,
check wire integrity or change the gas valve. If no, change the 780 series
ignition module.
That is pretty much all of the troubleshooting required.
Thanks for choosing FixYa,
Kelly
Feb 14, 2011 | Rheem 40 Gallon FVR NATGAS Low WATER...
Rinnai Infinity 26 hot water system set to 55 degrees with remote temp adjuster. Water only luke warm for showers. Burnner working, water & gas pressure ok. Any thoughts ... Stephen
If you aren't getting any error codes, then the heater is probably doing its job. Your problem is probably somewhere in your plumbing system. The most common reason you get this sort of problem is due to cold water mixing in the hot water system. There are a number of causes for a "cross connection" :
-Faulty check valve
-Missing check valve on reciculation return line
-Faulty shower cartridge
-Thermostatic mixing valve set too low
-Faulty thermostatic mixing valve
-Faulty anti-scald valve
The easiest way to confirm a cross connection is to: 1) shutoff the cold water entering the tankless heater 2) open hot water valves around the house. If you still have water flowing at your hot water fixtures, then you have a cross connection.
Jul 09, 2010 | Rinnai Digital Remote Water Heater Control...
I have Atwood GC6aa-9e. Water isn't getting hot.
If you've checked at pressure relief valve ( careful, not to burn yourself just in case it is hot) by pulling lever and catching some water that comes out in a cup or whatever. If it feels hot out of there, check that by-pass isn't faulty. Not uncommon for valves to seize, and only partially open, or close, and end up mixing hot with cold.
Mar 12, 2010 | RTO Atwood DSI-RV Water Heater-6 Gallon
Can't get hot water heater to work - Rinnai Infinity 18
If you can get to the gas valve make sure it is in the on position and not in pilot or off. Does it sound like
a spark ignition system? Even though you say the gas valve is on, by code thered should be a gas shutoff valve located within site of the unit. Follow the
gas pipe until you find such a valve and make sure its on
Feb 07, 2010 | Rinnai Vent Free Gas Heater/
I have a propane hot water tank that in discharging the hot water out the relief valve (Champion energy saver series)
possible problems not knowing age of unit the
control valve could be sticking open allowing gas to continue to flow until high limit is reached and shuts down valve another possible problem with the newer style back flow preventer being install by water companys the rapid heating and expansion of the water over pressures the water system causing releif valve to pop open and reclose most water heater manufacters are recommending instalation of an expansion tank to allow the growth in volume of water somewhere to go is valve constantly leaking or only during heating cycle if you could supply additional information does unit only leak when heating
or is steam expelled when releif valve opens
t-stat not opening gas valve sticking partially open
bad high limit bad pressure releif valve no expansion tank to allow for thermal expansion if steam is present and unit is boiling water inside replacement of water heater for safety concerns,would be reccomended if only water and pops couple of times water temp not over 140 degrees after most hot water has been used out of tank and is reheating most of capacity probably lack of expansion tank as the releif valve is the final safety device on a water heater is of great concern
the temp control gas valve or high limit are supposed to shut unit done long before the safety limit of releif valve is reached
Dec 11, 2009 | Water Heaters
Heating & Cooling Logo
97 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others