Furnace comes on for 5 min. and then shuts off.
    Sergeant:
  • 158 Answers
I'd start by replacing the filter, if there is not adequate airflow to cool the furnace, it will limit out and shut down.
Posted on Mar 20, 2011
4 Suggested Answers
SOURCE: Furnace comes on for 5 min then turns off
how can i do my aircon remote control not work?
Posted on Dec 11, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Furnace is 7 years old.
Check the air filter. Jump out thermostat to see if it stays running longer, if so replace thermostat. Make sure all return air ducts are clear of debris. If furnace has a Fan/Limit switch, make sure tabs are set at 100, 140 and 200. Sounds like something may be heating up and shutting unit off till it cools back down.
Posted on Jan 03, 2011
bobicehouse
  • 1524 Answers
SOURCE: short cylcing with the furnace,
Check the ignitor and flame sensor rod.
Posted on Feb 08, 2011
Furnace blower motor comes on runs for 5 min. then shuts off
ur having a fault issue. check your venting for blockage or the drain tube that drains the condensate
Jun 25, 2016 | Heating & Cooling
Tip
The pilot lites is on the furnace comes on the blower will not start and the...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed through the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Many newer furnaces have a diagnostic light viewed through a small window in either the top panel or bottom panel. If you remove a panel to see it, you may erase the code. If that happens, tape down the door safety switch and cycle the furnace with the panel off until the code appears again. Find the wiring diagram that is glued on one of the panels. There will be a diagnostic or error code chart that will give you a starting point where to look based upon the number of blinks the circuit board flashes.
Check out other tips at www.chandlerrepair.com.
on Dec 22, 2009 | Heating & Cooling
The heater runs for a few minutes and then it turns itself off it's on stable ground and everything
My furnace keeps shutting off, only runs for about 5-10 mins ...
? 5:19
https://www.youtube.com/watch?v=pEng9mtBtKk
Dec 15, 2013 - Uploaded by shannon122005
My furnace shuts off before reaching the set temperature on the... and then i turn switch back on , the furnace running about 4-5 hours and then ...
Furnace starts, then shuts off. - Home Improvement ' DSLReports Forums
www.dslreports.com > ... > Home Improvement
DSLReports
Dec 1, 2009 - 30 posts - ‎18 authors
[HVAC] My gas furnace cycles off every 6 minutes. ... This cycle will repeat a fewtimes, then usually after the second or third time everything ... How long is it after the big blower cuts on that the gas shuts off? ... Turn the furnace on, once the inducer blower is running you should read 0 volts (switch is closed).
Jan 03, 2016 | Heating & Cooling
Goodman furnace Model GDS80703AXBB -fan comes on then igniter light comes on, then burners turn on but shut off right away and wont stay lit. Now igniter light wont come on so burners not coming on at...
Sounds like either the flame sensor is not working.
The sequence for starting the furnace is:
1. extraction fan on
2. pressure sensor (for fan)
3. ignitor (spark or glow plug) comes on
4. gas valve opens up
5. ignition of flame
6. flame sensor (or temperature sensor)
7. plenum temp. sensor
8. main fan starts
It is most likely that the flame sensor is dirty or gone,
or (and I hope not), the module is gone and needs to
be replaced.
Sep 10, 2017 | Heating & Cooling
Furnace is 7 years old. Will not stay running for more than 5 min. Will start up again after shutting off and then run for another 5 min. Suggestions?
Jan 03, 2011 | Ruud Heating & Cooling
I have a furnace 90+ . I have no power at the t-stat..no led, blank screen, and the blower will come on. The furnace is tied into a control panel. I can jumper the the unit at the furnace to have the A/C...
either a thermal switch is open or the pressure switch is closed at start up the system checks all of these before sending power to the T-Stat
Sep 29, 2010 | Heating & Cooling
Lennox furnace 17 yeanrs old. flame comes on and the shuts down sometimes right away some times in a few minutes. We have the furnace go down to 58 at night. It takes all day to get back to 67.
Sounds like a dirty flame sensor.
Also 9 degrees is a large swing to recover. Most specialist will advise no more than a 5 degree set back, otherwise recovery time eliminates any savings you may achieve.
Dec 05, 2009 | Dayton (3E407) Heater
Furnace runs but once it gets to teamature it does not shut off but goes in and out of stages
Disconnect the thermostat wires from the circuit board. Tape door switch closed. Put a jumper on R and W on the circuit board. Let the heater run for about 5 min. Disconnect the jumper, furnace should shut down. If it continues to run you have a bad board. When you reconnect the thermostat, look for a shorted wire or a bad thermostat. I suspect a bad board if the furnace is hunting thru the stages.
Nov 03, 2009 | Goodman GMS90703BXA Heater
Wall furnace shuts off after about 10-20 mins
sounds like its not venting properly...it likely is shutting off on a "Spill switch" or "Vent safety switch"....check the vent/chimney first off.....also the pilot could be dirty..,..a lazy pilot tends to blow out easily....pilot should be blue and sharp,,,big enough to fully envelope the thermocouple
Oct 30, 2009 | Heating & Cooling
The furnace won't stop at the programmed temperature set ponts
this is called a swing tempature it is desined to improve the eficincey of the frnace because it take less energy to run an hour in a three hours then 3 bursts of 25 min in a three hour period
HOWEVER if you do not like this you can usualy set the swing temp
Jan 16, 2009 | Hunter Fan Company 5/1/1 Programmable...