Question about LG LS-L1210CL Mini Split Air Conditioner
What happens when i use a one horsepower for the indoor and a 1.5horsepower for the outdoor of my split unit..cos i'm presently in this situation after my 1.5hp indoor unit got spolit i had to use 1hp instead and since then my a.c has been malfuntioning i want to know if the mix affects the system(a.c) operation. thanks
    Sergeant:
    Champion:
  • 247 Answers
Maybe if you combined this unit the problem may be occuring is possible icing of your indoor unit but it can contol your thermostat but try to see what happen i think it will work.
Posted on Mar 19, 2011
WHAT IS REFRIGERANT SUCTION PRESSURE OF MY 1 TON SPLIT AC?
R22= 70-80psig
R410a=120-130psig
Depending on many variables such as blower speed, coils clean, indoor/outdoor temps.
Aug 05, 2015 | AMVENT 18000 Btu 1.5 Ton Ductless Mini...
What is the split pump
A split system has the parts split up between indoors and outdoors. A heat pump heats and cools your living space with the same unit. A split heat pump has the system split between indoors and outdoors and heats or cools your living space. a SPLIT PUMP sounds like something that has broken.
Feb 01, 2015 | Heating & Cooling
Error message U4
Signal transmission error. Indoor and outdoor PCB's cannot communicate. Usually a faulty controller board in the outdoor unit. If the indoor unit otherwise functions normally (can control fan speed, louvres, beeps in replay to all remote buttons) then it is probably OK so check outdoor controller PCB.
Jul 21, 2014 | Daikin Mini Split Concealed Duct Units
36VDC Indoor split in a 240VAC country
if you use the correct inverter and transformers
best if you just get new units designed to run in that country
Jun 23, 2017 | Heating & Cooling
My mini split system had an E2 code...replaced indoor pipe sensor...indoor unit works but outside unit does not...no other error codes, just motor not working outside
Check the outdoor unit to ensure power is available to it, and the contactor is closing on a call for cool 24-28 volt is present at the contactor coil to activate it.
Aug 24, 2013 | Continental Electric CE-AC7581 Ductless...
I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes
There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.
Jan 19, 2011 | Heating & Cooling
Panasonic cs-pw9gke i need wiring diagram
Split A/C-Cold:
You need four wires(two #10 and two #12) to the outdoor unit, leaving you house, and three wires(#10) coming from the breaker to tye indoor unit inside your house.
Split A/C-Cold and Hot:
You need five wires(two #10 and three #12) to the outdoor unit, leaving your house, and thee wires(#10) coming from the breaker to your indoor unit inside your house.
This ypical arrangment(all of them use three wires fro the breaker), yet there are other units which may require 6-7 wires connected to the the outdoor unit depends on the added features to the unit.
Regards,
Gulftecheng
Dec 05, 2008 | GE Quiet-Aire Ductless Split System Air...
Mitshubishi split muh-18nvand inside msh-18nv
-Start the unit.
-Press EMERGENCY OPERATION switch.3-minute time delay works.Test run operation operates for 30 minutes.
-Check voltage to terminal block of outdoor unit.Is there 12V DC between 2-1?
-If voltage is presenet check the wiring, compressor contactor outdoor fan motor and compressor.
-If no voltage check voltage to terminal block of indoor unit.Is there 12V DC between 2-1?
-If if voltage is present re-connect the continuity of indoor and outdoor unit connection.
-If no voltage replace the indoor electronic control P.C.
board.
-But also check the coil thermistor sensor and room air thermistor if this two is out of range it can cause the tripping of out door unit. It has the resistance of 8 to 10 k ohms at 25 deg c temp.
Jan 04, 2008 | Heating & Cooling
LG LS-L1210CL Mini Split Air Conditioner Logo
32 people viewed this question
Top LG Heating & Cooling Experts
Tim Whalen
Dan Webster
Dan Webster
Are you a LG Heating and Cooling Expert? Answer questions, earn points and help others