Question about Coleman Propane Forced Air Heater w/Electronic Ignition (50,000-80,000 BTU)
My Coleman gas furnace turns on, ignites and the flame will keep going out. The entire time the blower motor will stay on humming until its hot to the touch. If I tap the gas pipe I can get the pilot to stay on and then the furnace will work. This only happens when the temps outside are warm in the day and freezing at night. Could it be some kind of vapor lock from the propane tanks? Or a bad gas valve.
  • Coleman Master
  • 2,517 Answers
IT could be the temp is too cold at night and the tank cannot make vapor ie gas, The liquied has to boil inside to make the gas you can get a heat blanket to warm your tank. Ask you gas suppier if they have one.
Posted on Mar 20, 2011
I have a coleman furnace model 4066A656
Make sure your air filter is clean. Is the thermostat satisfied? or is the room temp. still below the thermostat setting? When ever you have to turn the power off and then back on to a furnace that usually indicates that the furnaces ignition control locked out. The first thing that I would try is cleaning the flame rod.
Mar 02, 2017 | Coleman Heating & Cooling
When i turn the heat up sometimes it takes a long time for the gas furnace to start ..why?
Watch your furnace when you turn the thermostat up...make sure to record everything that it is doing. If you have an induced draft, forced air system, then the heat sequence of order should go like this... Initial call for heat from tstat, Inducer vent motor turns on-pulls in the pressure switch, circuit board sends power to igniter whether it is spark or hot surface, then gas valve opens. Flame sensor senses flame, burner stays on, and blower motor kicks in to heat the space. If you notice any variance from this, then something needs to be checked by an HVAC Service Tech.
Dec 14, 2013 | Honeywell Programmable Thermostat Heater
My heil n9mp2 isnt working just hums
is the flame igniting and then cutting off? on a gas furnace, the induction fan motor(draft motor) should start first (if the furnace is so equipped), then the flame, then the blower. if you have an induction motor (flue gas exhaust mmotor) this may be your problem (the induction motor isn't starting), if your unit doesn't have one, have you checked to see that you have gas? finally, the capacitor on the blower motor may be causing the motor not to start.
Jan 06, 2013 | Heating & Cooling
I have a coleman furnace it comes on the electric igniter glows red the gas comes on then the blower starts and the fire goes out it gives 2 different code for this 1 is ignition failure and the other is...
I would have the ignition control board replaced. That is what tells the gas valve to come on and if there is flame or ignition it will keep the gas on if the flame sensor gives the board a signal that the burner is lite. By you shuting power off and on to the furnace it resets the board and it will go through its cycle again.
Feb 10, 2011 | Coleman Heating & Cooling
Fan turns on, pilot on left side turns on red light at bottom stays solid during entire time then pilot goes out and blower stops no heat please help
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remaing solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Oct 05, 2010 | Goodman GMS90703BXA Heater
I have an intertherm gas furnace and it will turn on but it takse almost an hour from the time i turn the heat up until it kicks on. I can hear the click and it sounds like the motor is humming. I have...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 23, 2010 | Heating & Cooling
Gas furnace; flame will not stay on
Clean the flame sensor with a green scotch brite pad. Check all ground connections from the circuit board to the furnace cabinet. Check for a proper ground to the electrical box. Make sure polarity has not been reversed.
Dec 26, 2009 | Coleman Heating & Cooling
Burner flame going out on windy days on Coleman Evcon LP furnace
This sounds like a bad heat exchanger. It is possible that you do not see the crack because the crack is closed when the heat exchanger is cold (or room temp). Allow the furnace to heat up, this will allow the expansion of the crack. Turn the power off and examine the heat exchanger while it is still hot.
Mar 31, 2009 | Coleman Propane Forced Air Heater...
Coleman presidential II furnace blower on and off
Sounds like the flame sensor. But it could be the thermostat. Is the furnace standing pilot or electronic spark or hot surface ignition. I would start by checking thermostat. Turn power off to furnace take thermostat off wall and take wires marked r & w and connect them together. Turn power back on if furnace works then change out thermostat.Most eclectronic ignition Furnaces have a flam sensor, You could take flame sensor out and clean it up with steel wool or wire brush. If you need anymore help just reply back .
Jan 17, 2009 | Coleman Propane Forced Air Heater...
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
Heating & Cooling Logo
157 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
paulcarew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others