Question about Honeywell Heating & Cooling
Fuel oil boiler circulating pump with r8182h1070 honeywell controller runs fine but periodically pump does not start to start pump i have to turn power off to the controller then back on pump starts everything is fine for aweek or so
    Master:
  • 382 Answers
Probably the boiler piper must have worn out..try replacing it which should help you,also check you dont have low-voltage which affects the pump from working..Thank you!!
Kind Regards!!..
Posted on Aug 01, 2008
  • 2,071 Answers
  • LORETO LACARON
    LORETO LACARON Aug 01, 2008
    You may find that the circulating pump is need to clean and maybe there is jambed
    some of the pumps
    have a large screw on the face that can be removed (whilst furnace is
    off and cold) allowing a little oil to escape and showing a slot /
    alen key hole for you to rotate the pump shaft and free it i am not
    sure if this facility is provided on us circulators. if not GENTLE
    tapping whilst on may free the circulator.
    also ensure that there is in fact oil in the system.
I have a Honeywell L7224U I need to know how to turn on the circulator
Assuming you have an oil fired unit. hot and neutral wires on circ should be connected to C1 and C2 respectively. Tstat should be connected to TT which will energize circ on a call for heat and boiler will run based on limits. If you boiler is set for cold start the circ will only run on a call for heat. If you have more than on tstat/zone then you probably have either a zone control box or zone valves and transformer. If that is the case I would defer to a heating professional.
Nov 16, 2017 | Honeywell Heating & Cooling
Taco 007 circulating pump stays on even though boiler shuts down
Don't know your specific unit, but in general, heating systems are two-stage devices:
1: Its too cold: the motorised HW/CH valve moved to the required position, and on achieving it, the circulaion pump starts and the boiler is enabled. (The circ pump may start immediately - its not usually important.) The hot water from the boiler circulates through the heat exchanger and/or radiators until the thermostat thinks its target is warm enough, whereupon it disables the boiler, stops the pump and closes/relaxes the valve(s).
2: The boiler is off while disabled. When enabled, it heats the circulating water to a 'high' temperature and seeks to keep it there. If it reaches that temperature, the boiler will cycle on and off as necessary to maintain the set 'high' temperature. (The circulation pump must run all the time the boiler is enabled.) This may be what you're noticing. Additionally, some boilers will run the circulation pump for a little while after being disabled to reduce the temperature if the water in the pipes and boiler.
Your question doesn't say how the pump running corresponds to thee thermostat settings, but if it were stuck on, I think you'd know!
Dec 31, 2016 | Water Heaters
I have a riello burner 40 it will fire and come to temp but wont refire, goes into lockout
My first guess would be that it sounds like a clogged oil filter, air in your fuel line, is piping overhead, or leak in a fitting or connection causing it to loose it's prime when running.
I have also seen primary controls that are faulty do this, watching the complete cycle of the run time will give you more clues as to when the control actually locks out. Does it lock out during the run cycle as the boiler reaches temp.? If so,check for oil line and suction issues as stated above.
If it locks out on start up after reaching boiler set temperature, if hitting reset right away burner doesn't start and lock out occurs with no motor engaging, check motor (Note: Some motors when HOT will not kick in when powered, but after they cool down naturally they start, motor shaft may also be bound up tight, replacement is necessary) if burner motor spins but does not fire, check for fuel flow to the nozzle, be sure oil is pumping to the nozzle, if it is, clean cad cell eye, and check transformer for spark, if all is good.. replace primary control.
Disclaimer:
Of course all this information is technical troubleshooting information and should be performed by a Licensed Technician, not knowing how to properly test for flame failure can cause injury, fire or worse! Consult a technician in your area if you are not proficient at oil burner repair!
Nov 21, 2014 | Honeywell Biasi B10-3 Boiler ,riello...
Utica Boiler model # MGB100HD with a Honeywell Aquastat Relay model # Type L8148E will not operate the circular pump. THe damper works and I can hot wire the circulator pump but it won't turn on...
how did you hot wire it. did you jump the wires on the relay board or use another power source? Does the boiler burner start? Have 120 volts incoming to the relay board? You hear relay click when turning power on/off? If so bad relay, or loose wiring terminals on the board. This control has built in transformer that can burn out, that will stop the pump relay contacts from working.
Nov 07, 2011 | Honeywell Programmable Thermostat Heater
Amtrol 41 hot water maker :not working when calling for hot water,contols are on showing temp,but tank is cold.oil fired boiler is fine,the whole system is 5 yrs old.
The problem is probably with the circulator pump or the zone valve, which ever way your water circulating from the boiler is controled.
The water needs to be moved through the boiler and the coils in the Hot water maker to heat water. If this is not happening then no water will be heated.
Check for power and then is the pump is running or the zone valve opening.
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 21, 2009 | Dishwashers
Have hot water but no radiators. Checked pilot
sounds like your circulating pump is bad or electronic zone valves
Oct 26, 2009 | Honeywell Programmable Thermostat Heater
Hot water boiler will not ignite
Check all your limit switches on this unit. One of them is either tripped or bad.
Apr 07, 2009 | Water Heaters
Rayburn boiler runs heating system, radiators tepid
What is the temp at the boiler? there is a temp/ presure guage it should read 160-180F. If that is OK then check the circulating pump. When the thermostat is turned up you should hear a little water moving through the piping as you have adjusted the system. If you hear nithing circulating you may have a defective pump.
Good Luck, Phil
Dec 10, 2008 | Water Heaters
Boiler will not shut off
boiler does not shut off when thermostat reaches temp, i already replaced aquastat but condition still exists
Nov 14, 2007 | Heating & Cooling
Heating & Cooling Logo
134 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others