Question about Air Conditioners

2 Answers

I have a riello burner for my central heating system. When i turn the heating on the burner ignites for a few swconds and then goes out.... the burner tries to re-ignite and the same happens. I have plenty of oil and tried to clean the fuel nozzle and electrodes as I thought it may be dirty. I still need to clean the inside of the boiler free of sut. Can you tell me if I need a new photocell, pump or something else

Posted by on

2 Answers

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

Ireplaced the photocell which was blinded and the burner started and stayed lighting....
Thanks for all your help

Posted on Aug 05, 2008

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 1,420 Answers

Replace the nozzle, don't try and clean it. After the burner runs a few seconds, do you have to reset the control (red button) before it will start again? Does it sound like there is a pulsation in the flame when it starts or it is running out of oil? You may have a bad ignition control. Start with the small stuff, nozzle, strainer filter, oil tank filter and then work to the more complicated.

Posted on Aug 04, 2008

1 Suggested Answer

tborn6
  • 700 Answers

SOURCE: burner propblem

have you tried to wipe off the fire eye on the unit if it has one? If it's dirty too then it will not see the flame and not let the unit come on correctly. Good Luck and have a Happy New Year.

Posted on Jan 05, 2009

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

How do i change a nozzle on f3 riello burner


I have a manual for this burner i can email it to you if you do not already have it my email is steve_e_morris@hotmail.com i will send it to you if you need it.

Dec 17, 2014 | Heat Controller Comfort-Aire Lowboy Oil...

1 Answer

Have strong oil smell when riello 40 oil burner starts up


I looked at the drawings from this unit and it is completely sealed between the heat exchanger and supply air. So you should not smell oil at any time you have a leak some place look for that .

Nov 09, 2014 | Air Conditioners

1 Answer

I have have a YORK central air/ heat unit that is not firing up. Thermostats seem to be working but they aren't turning the heat system on. Background info: I had a lightning strike this summer that took...


If the stack blower (fan) does not start when you select heat, the fan control may be defective. If the igniter does not heat up long enough to cause the thermocouple to open the gas valve and fire the burner, the igniter is defective. If the igniter heats long enough but the burner doesn't fire up, the thermocouple is defective.

Nov 26, 2013 | Air Conditioners

1 Answer

Pilot light out....buderus furnace but a red riello ingniter on the front....I've watched my fuel guy flash a light into it this baby when out before but need to do it myself now.....could you walk me thru...


This is due to a "Lock-Out" Check your flame sensor for carbon build up. Possible heat exchanger blockage.
The reason he used a flashlight was to trick the burner into seeing a flame, not a good idea for a novice.

Mar 16, 2011 | Air Conditioners

1 Answer

I have central air ( Dimond 80 York Heating Air conditoning Unit ) My air conditoning unit has stopped working. The board has checked out ok.but there seems to be a voltage problem some where from inside...


Try the following step.....

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).




Jun 08, 2010 | Air Conditioners

1 Answer

Burners ignite but turn off after a few seconds


On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Jan 08, 2010 | Ruud Air Conditioners

1 Answer

I have a central air and heat heat uses gas so when the heat is on should the main fan be turning


Typical systems are designed with a thermostatic "fan limit switch" which protrudes into the heater (house air portion of the passages). The "fan limit switch" is mounted to, and protrudes into the duct within the burner section of the heater.

This switch triggers to fan to turn on only after the air in the duct has reached well above ambient temperature. This prevents the fan from coming on too soon and the system blowing cold air, which people don't like.

Depending on system design, installation and current operating conditions, the time delay from main burners on to fan on can be up to a couple of minutes.

This same limit switch, if the temperature goes high enough, will also turn the gas valve off; a fire safety function.

Jan 06, 2010 | Goodman CKL49AR49 Air Conditioner

3 Answers

Riello 40 F5 oil burner, on boiler, intermittently running


with a forced draught burner the fan motor would be checked via a pressure switch. if the pressure switch is not set correctly or the fan is too weak the contacts will not be made in the switch and the burner will lockout. if the damper is not open enough when the fan runs then the air supply will be too small for the switch to make. check to see if you have a capacitor on the fan windings if this is faulty then the fan will fail intermittently.

Jan 19, 2009 | Air Conditioners

1 Answer

Burner propblem


have you tried to wipe off the fire eye on the unit if it has one? If it's dirty too then it will not see the flame and not let the unit come on correctly. Good Luck and have a Happy New Year.

Jan 05, 2009 | Air Conditioners

1 Answer

Riello burner will not pump oil to nozzel to burn.


Revisit the photocell:
1. Check if you connected the socket end, into the two pins properly, as it is possible to miss a pin.
2. Try to borrow a working photocell or use yours in another burner to make a determination.

Dec 27, 2008 | Air Conditioners

Not finding what you are looking for?
Air Conditioners Logo

Related Topics:

602 people viewed this question

Ask a Question

Usually answered in minutes!

Top Air Conditioners Experts

Dan Webster
Dan Webster

Level 3 Expert

8147 Answers

Bill Long

Level 3 Expert

577 Answers

Tim Whalen

Level 3 Expert

3056 Answers

Are you an Air Conditioner Expert? Answer questions, earn points and help others