I have a Fast HVAC part # TS21 thermostat.I hooked it up,my furnace has two wires, Red and White.I hooked them to W2(white) and RH(red).I programmed the thermostat and now all that happens is my fan comes on and then off every few seconds.Any help out there? My furnace is a natural gas Rheem Criterion II.Thanks
  • 10 more comments
  • Randy Orndorff Mar 12, 2011
    It's a single stage.I'm replacing the thermostat that was there it was a lux and it was hooked up to the W and RH terminals.My new thermostat is a Fast HVAC part # TS21 thermostat. across the bottom it has the following terminals: I2, I1, RC, DH, H, C Y2, RH, OBW, W2, G, Y1 (W2 FIRST STAGE FURNACE) WHITE WIRE -- (RH 24v) RED WIRE, IS HOW I HAVE IT HOOKED UP.
    No,there was only the White and Red wires. On the Lux 500 the one I took off the wire hook up is labeled G,Y,W,RH,RC there is a short black wire going from RH to RC.
    I'm not sure.It's doesn't sound like it's trying to spool up like the blower.There is an important notice in the back of the manual.
    When using this thermostat with a gas furnace a common wire C must be connected.
    When working without a common wire:
    A confirm in heat mode the cooling does not switch on or B confirm in cooling mode the heat does not switch on.
    If test A or B fail or the thermostat shuts down in either heat or cool mode then it is necessary to connect a common wire(C),alternately it may be possible to solve this issue by simply connecting the 250 ohm 10 watt resister between C and Y1 at the HVAC equipment
    Ok how do I do that? Coming out of the wall is just the two wires.
    I have the TS21 Manual here too. Is there a certain page I should look at?
    Maybe I should just go get another of the same thermostat I had and use it.I tried to to go fancy might have been a mistake.Thanks
    When I do this does the furnace just continue to heat until the wire are disconnected?(if nothing is wrong)
    Ok,I will give this a try and post what happens.Thanks
    Ok,I hooked the wires together turned the pwr on and the OK led blinked once stayed on,the power led stayed on the whole time..A fan ran for about 30 sec. then the furnace tried to light, it flamed on for 3 to 5 seconds went out, so did the gas led and the blower started running.
    For about 3-5 days before the furnace would run fine all day and then would do the above for a few hours but sometime during the night it would work fine a heat the house.
    OK,I will try that and hopefully it will work.I will let you know.Thanks again
    OK,I did that ,powered on and it is working like it is suppose to.Thank you very much for your expertize.
    The solution fixed my problem.
  • 8,841 Answers
Hi, this may be a problem with the furnace itself. Have you tried connecting the red and white wires directly (without the thermostat)? The furnace should light when you do this. If it doesn't, it will probably blink trouble codes to be diagnosed. Please let me know if you have any questions, and thanks for using FixYa.
Posted on Mar 12, 2011
  • Jeffrey Turcotte
    Jeffrey Turcotte Mar 12, 2011
    yes, when the wires are connected, it's the same as if the thermostat is turned up to 150 degrees--it will not shut off. I do not recommend leaving it like this. This was only to test the furnace.
  • Jeffrey Turcotte
    OK, I think you have a problem with the flame sensor. It's a little thin cylinder that sits in front of the burner flame. If you can get some steel wool on it, scrub it real good (with thermostat wires unhooked). If you can't clean it well on the furnace, take it off and clean it. It's held on a by a couple of screws and has a cable connected. Put it back and make sure it's sitting right in front of the flame. Hook up your thermostat as you had it originally and you should be good for at least a year or 2. If the sensor is getting oxidized too fast and acts up again, replace it with new.
    Genius:
  • 1,033 Answers
Hello, is this a 2 stage furnace? there should be just a W terminal and a RH where the wires hook up too if it's a single stage unit.
  • 4 more comments
  • Robert Mar 12, 2011
    Do you have a common wire hooked up to C terminal?
    Which fan keeps turning on and off the inducer or blower motor?
    ok that is a jumper wire u have there, if this tstat is just used for heating the jumper should be removed.
    So this is heating only and single stage, which motor is running on and off the inducer or blower motor?
    I have the manual in front of me and a common wire should be hooked up,this thermostat is a little tricky to hook up, but if you add the common wire you should be ok.
    You will have to run new tstat wire from the board on the furnace to the tstat on the wall, you will need 3 conductor tstat wire. you can use fish tape to guide it through the wall. I know it kinda sucks to do all this work but without that common wire the tstat wont work.
I installed a Honeywell RTH230B model thermostat. The heat works fine, but the AC is blowing warm air. Wires from old system are as follows: Y=yellow; G=green; R=red; O=brown; C=blue; E=white (it looked...
the colors of old system are for heat pump.if you have a heat pump you need heat pump thurmostat and colrs will make more sense.if not,then you need to go into furnace to see what colors go where.yellow is cool, goes to compressor contactor,usually another wire going from furnace to outside unit.green is fan relay rh is heat call rc is cool call
Jan 01, 2011 | Honeywell Programmable Thermostat Heater
York Furnace and Honeywell Thermostat Problems...
run the red wire to rc and run a jumper between rc and rh tape off the brown
Feb 10, 2010 | Honeywell Programmable Thermostat Heater
I just purchased a Honeywell RTH2310 and cant get it to work. I have a gas furnace that has two wire R and White. I tried connecting to Red-Rh and W for white, with and without the jumper for Rh and Rc....
red is 24volt power, white is load,I.E. relay,touch the red and wht wires together, the furnace should start, if it don't the problem is the heater, Rheat-Rcool you have a heat/ac thermostat, no ac forget Rc,try turning thermostat all the way up, dig up a multi-meter or powered light tester, touch Rh with one wire of tester,touch the other wire to different terminals until it lights,hook up your wires, you should have heat
Jan 31, 2010 | Honeywell Focus 6300B 5-2 Days...
I have a coleman Evcon model AH16-0 . I am
Typical Thermostat Wiring for 4 or 5 wire Heat/Cool Thermostat (not heat pumps)
4 Wire Termostat
R = Red One Side of 24 volt Transformer
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
with one transformer for both units
Rc One Side of 24 volt Transformer
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
With 2 transformers one for indoor unit
And one for outdoor unit
Rc = Red One Side of (outside) 24 volt (outside transformer)
G = Green Blower (outside transformer)
Y = Yellow Cool (outside transformer)
Rh = Blue One side of (inside) 24 volt (inside transformer)
W = White Heat (inside transformer)
COOLING ONLY Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
R or Rh One Side of 24 volt Transformer
W = White Heat
Jan 06, 2010 | Heating & Cooling
I have a coleman evcon gas furnace I want to change the termostat to a programmable thermostat I don't know where the wires hookup we have four wires red,white,yellow,green. I have a honeywell RTH230b...
The thermostat has terminals which are marked for color, R = red, W = white, Y =yellow, G =green. There should be a jumper between Rh and Rc, Hook the red to Rh.
Jan 01, 2010 | Coleman Propane Forced Air Heater...
I had an old two wire system, red and white. gas
Check for a bad thermostat and wire by jumping the red and white wire together at the thermostat. If the unit fires, you have a bad thermostat. If it does not, jump the R and W terminals at the furnace (or where ever the thermostat wires are connected to). If the unit fires you have a bad wire. If it still does not fire, you have an issue with the heating system not the thermostat or its wires.
Dec 06, 2009 | Honeywell Focus 6300B 5-2 Days...
Installing programable thermostat it has 5 wire points, i have 7 wires off the unit which ones do i use
For heat pumps........
R = Red wire (hot24v)
G = Green wire (blower motor)
Y = Yellow wire (AC condensor)
C = blue wire (common)
O = Orange wire (reversing valve)
W1 or W2 = White wire (emergency heat)
For gas furnace
W1 = white (gas furnace)
R = red
G = green
Y = yellow
C = blue
Sep 22, 2009 | Heating & Cooling
Thermostat wiring
Normal 0 MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";} Thermostat wire color codes explained.
Please note. Not all installers use the proper color codes when they install or replace equipment. It may be necessary go go to the furnace or outdoor unit to verify what wires are for what purpose. Also be sure there are no splices in the wire that could change the wire colors between components.
  • R (red) or Rh (Red heat) 24 volts from equipment.
  • Rc (Red cooling) 24 volts from transformer in cooling equipment.
Note: If only furnace has a transformer and cooling equipment does not jumper Rc and Rh.
  • W (White) sends 24 volts to furnace control to start the heating cycle.
  • W2 (no standardized wire color, usually whatever wire color is available) controls second stage heat.
Note: W2 is most often used for heat pumps to control what is called emegency heat or Auxillary heat, and most often will use the white wire.
  • Y (yellow) often (blue) is used, controls cooling unit (outdoor condensing unit) also is used for heat pump heat.
  • Y2 (no standardized wire color, usually whatever wire color is available) controls second stage cooling.
  • G (Green) controls the fan "on" operation of the furnace/air handler. Also often is used to start the blower for many electric furnaces.
  • C (common) most often brown but can also be black or other color available to installer.
  • O (orange) Energizes heat pump reversing valve for cooling (Trane and most other brands).
  • B (Blue) Energizes heat pump reversing valve for heating (Rheem, Ruud and Weatherking).
Jun 02, 2009 | Carrier Heating & Cooling
My problem is....On my new Honeywell RTH230B thermostat the color code is Rh, Rc, W,Y and G. My wire colors are red, orange, blue, white and black. I can obviously match up 4 of them but where the heck...
First you are using abnormal wire colors for a furnace. Second.... if you have an air conditioner hooked up to this furnace, you will need to install a jumper wire between rh & rc. I am assuming this is a natural gas furnace. Usually the red wire to R terminals. Usaully the white wire to the W terminal. Take the door off of the furnace. Find the thermostat wire connection in the furnace. What ever color wire is on the R terminal in the furnace should hook to the R terminal on the t/stat. Whatever color is on the W in the furnace goes on the W on the t/stat. Whatever color is on the G terminal in the furnace goes to G on the t/stat. And the Y in the furnace to the Y on the stat. and the G in the furnace to the G on the stat. Most applications use only the R, W, G, & Y ( always put the jumper wire between Rh & Rc)
Good Luck
Hvac Teacher
Mar 26, 2009 | Honeywell Programmable Thermostat Heater
Need help with wiring on Hunter 44110
There is no real color code for wiring but the standard is red wire to r, yellow wire to y,white wire to w, green wire to g, blue wire to c. since there's no c on your t- stat its probably battery operated, but in your case im betting white wire to w, and blue wire to g.
Mar 08, 2009 | Hunter Fan Company 5/1/1 Programmable...
Heating & Cooling Logo
187 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Tim Whalen