Question about Whirlpool ED2FHEXN Side by Side Refrigerator
Electrical problem I am rewiring my new bathroom and using the original wiring that was in the room. The wiring setup was a 15 amp circuit breaker going to a ten gauge wire that went into the room and the lights worked. What I did was cut out the existing lights rewiring new lights with 12 ga wire and a 20 am circuit. there is still 10 ga wire going to the room though. the problem is that my switches are not cutting the flow of power to the lights and the lights are not coming on either but the senor says there is power. Do I need to change out the 10 ga wire for 12 ga?
    Sergeant:
  • 359 Answers
No the problem is not the 10 gage wire , 10 gage is good for 30 amp circuits and you can always use it provided it is fused or breaker to accommodate the smallest wire in the circuit example , if a circuit contains 14,12,and 10 gage wire the fuse or breaker must be sized to accommodate the smallest wire which is the #14 which means it would be fused @15 amps but the circuit would work fine as long as you did not exceed the 15 amp rating on the circuit , you must have something wired improperly in the circuit re-check the wire connections
Posted on Jan 01, 2009
The fuse trips when the iron is switched on
dead short internally or bad wiring in the cord
cord can be replaced by electrician but otherwise junk it and get a new one
Dec 09, 2016 | Irons
I had a house inspection and in the main panel I have a 20 amp QT breaker that is rated from 15-35. I have a 20 gauge wire and and a 15 gauge wire running to this breaker. Inspector says I need a 15
He is correct. I'll not go into the particulars but the fact is, you have two separate circuits connected to the same breaker. Separate the two circuits by installing another 15-Amp breaker. Although I understand your situation, please understand wire gauge and electrical amperage are two different animals. Breakers are rated in Amperage and electrical conductors are sized by wire gauge. That said, the 20 gauge wire you speak of is actually a 12 gauge conductor and the 15 gauge wire as you say is a 14 gauge conductor. Have a good day.
Aug 30, 2014 | Siemens Ite Twin Q1515 Circuit Breaker...
Installing arc fault interrupter with ground fault
Question is vague. Arc fault and ground fault are slightly different.
Are you installing arc fault breaker?
http://waterheatertimer.org/How-to-wire-GFCI.html#arc-fault
http://waterheatertimer.org/How-to-replace-circuit-breaker.html
Code says Maximum 12 boxes per circuit breaker.
Arc fault breaker and GFCI outlet in bathroom?
>>> do not connect this way.
Do not install 2 fault protections on same circuit.
Install the arc fault circuit breaker, and then remove bathroom GFCI, and replace with ordinary outlet, or switch-outlet.
How many outlets can be connected to a bathroom GFCI?
It depends on total boxes on circuit.
Count the boxes. Max 12 boxes per circuit breaker.
How many amps can be connected to 15 amp device?
15 x 80% = 12 amps
Electricians use 80% rule to calculate safe maximum
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/See-inside-main-breaker-box.html
Add a comment
Apr 21, 2013 | Siemens Seimens Arc Fault Breaker
Room heater caused 15 amp circuit breaker to go bad. Can we update 15 amp circuit breaker to 20 am (similar to ones next to it)
Probable not, in order for you to install a 20 amp breaker, the wiring must be a #12 gauge cable.Check the power requirement of your room heater. It should be not more than 15 amps. Check and retighten the connections to the heater.
Install a new 15 amps breaker.
Nov 21, 2011 | Electrical Supplies
We have a new 12 room motel addition we are wiring. There are two bathrooms in which the arc-fault breakers are trippping. The loads are - two three lamp incandescant wall fixtures, and two GFCI...
Hi, I know it sounds simple but sometimes its the simplist things that get you. Check your earth, as it sounds as if this may be causing the problem.
Sep 28, 2010 | Eaton ARC FAULT CIRC BREAKER
How many outlets will this carry?
While there is a practical limit for the number of outlets on a 15 or 20 amp general purpose lighting circuit in a _residence_, the National Electric Code (NEC) does not impose a # of outlets per circuit limit (residential ONLY).
However, some electrician's design general purpose lighting circuits in a residence using a point system. An outlet is 2 points and a light is 1 point. So, for a twenty amp circuit, (10 outlets x 2 points) = 20. Or, (5 outlets x 2 points) + (10 lights x 1 point) = 10 + 10 = 20. Or (8 outlets x 2 points) + (4 lights x 1 point) = 16 + 4 = 20. However you want to mix it up.
Now, if this is for a Commercial building, the the NEC allows no more than 180 VA (Volt Amps) per outlet. 180 VA / 120 Volts = 1.5 Amps.
20 amps / 1.5 Amps = 13.3 outlets. Drop the .3 and one determines that 13 outlets are allowed on a Commercial 20 amp circuit.
Also, if the 20 amp circuit is considered a continuous circuit (ON for more than 3 hours a day), then it can only be loaded to 80%. 80% of 20 amps = 16 amps.
Aug 07, 2010 | General Electric 20 Amp, 1 Pole Thick Type...
I have a whirlpool WED5300SQ0 dryer that is on a 30 amp circuit , it trips the breaker after about 15 min ,,,it has 10 gage wiring but it is an older house , the breakers look ancient..should i replace the...
If you don't have an AMP clamp to measure the amount of AC current draw. Then I would replace the breaker with a new 30amp. If the electrical panel is a sylvania or Zinco then that is most likely the problem! Those panels use the same breaker type and are terrible at having breakers going bad and tripping premature. If it is one of those type of breakers better dig deep in your wallet as those breakers run $1.25 to $1.50 per amp !
Nov 30, 2009 | Whirlpool WED5300S Electric Dryer
Arc fault breaker trips sporadically
Are there any heaters anywhere in the circuit for this breaker? (ie: bathroom fan w/light and heater) If yes, I would suspect and inspect them first. Also,any type breaker will trip more easily if the electrical connection screws on the breaker are not tight enough...check to make sure that's not the case.
Jul 31, 2009 | Eaton 20A ARC FAULT BREAKER
I was changing a light fixture in my bathroom,
hello, all you have to do is to get a new breaker with the same amperage or amp's example 15 amp's of the breaker that's blown and pop out the old one and put in your new one , in the future when working with electricity always manual trip the breaker before working for your safety and the safety of the equipment .good luck
Mar 22, 2009 | Your One Source Homeline Circuit Breaker
Blown breaker
It sound like all of those go through your bathroom GFCI. I would recommend moving your outdoor circuit breaker indoors if possible or enclosing it to make it water-proof. You may also do some rewiring from your main breaker box ( if you are handy) to eliminate the outdoor box completely considering you have 100 amp / 200 amp breaker box inside your house. If you still have an old FUSE BOX with 60 amp service, I would recommend replacing it with a 100 amp or 200 amp breaker box depending on the size of your house. I would separate the laundry room by itself with 12/2 gauge wire with ground on a 20 amp breaker. You can then take your bathroom (using 12/2 gauge wire with ground keeping your gfci ) and run it to another breaker in the house with a 20 amp breaker or add a new one if there is room in your main box. Now all you have left is the porch light. You can run that separate from everything to your main breaker box using 14/2 gauge with ground to a breaker in your main box by adding a new 15 amp breaker or adding it to another 15 amp breaker that does not have a very high load such as a bedroom. In general Kitchens, Bathrooms, Laundry rooms should be on there own separate 20 amp breakers. Most every other room can be 14/2 with ground on a 15 amp breaker... hope this helps....Joe
Dec 17, 2008 | Prime 10 Amp Circuit Breaker
Whirlpool ED2FHEXN Side by Side Refrigerator Logo
99 people viewed this question
Top Whirlpool Refrigerators Experts
John Tripp
John Tripp
Charles T Nevin
Charles T Nevin
Dan Webster
Dan Webster
Are you a Whirlpool Refrigerator Expert? Answer questions, earn points and help others