Question about Coleman Mach 15 Air Conditioner
Coleman mach 8333 kicks breaker
My a/c comes on and runs fine for 20-30 minutes, but when the compressor cycles it trips the breaker. I had an electrician check the current and it runs about 15-16 amps initially with the compressor on. When the compressor cycles it runs up to about 33-34 amps for about a minute then it stops trying to start the compressor for a couple of minutes then restarts the compressor at about 18 amps eventually dropping back to about 16 amps. I was wondering if this is a capacitor problem or a compressor problem.
I changed out the startup and run capacitors. A/C runs fine now
Posted on Jul 27, 2008
Coleman mach 8333 series won't run. both compressor and blower inop. checked power in 120v,checked blower switch and therm. both are working. what next?
Check the capacitor. You probably have one capacitor that controls both the compressor and fan. If that isn't it, check the contactor and make sure that it pulls in when the thermostat calls for the A/C to come on. Also check the voltage on the line side and load side of the contactor. I have seen some with voltage on the line side but it wasn't making it to the load side.
Sep 05, 2010 | Coleman Mach 15 Air Conditioner
Trips breaker and will not cool or heat
Disconnect compressor leads and tape them up. Restore power, if the breaker does not trip, than you have a grounded compressor.
If breaker trips again, hook compressor up and disconnect blower, if breaker does not trip you have a
bad blower motor.
Jun 18, 2010 | Coleman Mach 15 Air Conditioner
For the 13500 btuh cooling what is the voltage and
you need a 20 amp breaker the full load amps on that unit is 16
Apr 08, 2010 | Coleman Mach III Air Conditioner
Coleman Mach 3 ac unit tries to start compressor & kicks off
50 foot extention cord not a problem IF it is at least 10 gauge and plugged in to a 20 amp circuit
Your compressor is shutting down for a lack of AC voltage would be my best guess
Jul 27, 2009 | Coleman Mach III Air Conditioner
Coleman (RVP) 7000 AC unit compressor problem
I had a problem with my coleman mach 3 AC, we were at an RV park up at lake shasta CA and the fan would stay on but the compressor would come on for a few seconds and then trip off. It was the motor overload relay on the compressor that was tripping. the RV park was old and apparently the wiring to the panelboard at the RV park was too small, when you are drawing a lot of current there was too much voltage drop across their line, to make up for this the motor tries to draw more current and heats up the motor overload and it trips off. I solved this problem by buying an autoformer from Camping World, it senses a voltage drop and automatically boosts the voltage.
I am now having a seperate problem, the compressor is either locked up or has too much back pressure and trips off the service breaker when trying to start. The only solution I can see with my current problem is to replace the entire unit.
Oct 07, 2008 | Coleman Mach 15 Air Conditioner
Coleman rv a/c
It is definitely with the compressor. It should more like you may have a weak winding in the compressor, you can a hard start capacitor (sp5 ) that will help the compressor on restart. Note that this is a last chance solution for a compressor.
Oct 01, 2008 | Coleman Mach 15 Air Conditioner
COLEMAN TSR MACH 3 COMPRESSOR
I would check the thermostat based on what you said it could be out of calibration
Jun 11, 2008 | Coleman Mach 15 Air Conditioner
Coleman Mach 15 Air Conditioner Logo
586 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others