Question about Goodman Heating & Cooling
No ignition No Heat. When the thmostat powers the furnace on, the small ventilator comes on (red control light as well) - after 30 sec's the gas control clicks and gas is released into the burner tubes (smell), but no ignition. Does that point to an defective ignitor? Thank you, ralf Huck san francisco
  • 143 Answers
Yes. Gas ignitors either spark or glow. Find a way to look at the ignitor, even if you have to use a mirror. If it sparks or glows, figure out why the gas isn't getting into contact with the ignitor. If it doesn't spark or glow, the ignitor is probably bad, but the controller might not be sending it electricity (bad controller). This is what electrical meters are for. Checking for voltage at the ignitor will tell you if the controller is telling it to ignite.
Posted on Jul 25, 2008
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Ruud UBHC Air Conditioner
Induction fan motor cycles on and off , with no call for heat
Nov 26, 2010 | Heating & Cooling
Air pressure switch is closed before the ignition sequence causing the boiler not to ignite can you advise solution
I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 25, 2010 | Heating & Cooling
Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 24, 2010 | General Heating & Cooling
My goodman furnace keeps lighting for about 10 seconds than goes out lots of clicking sounds
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad igniter what I see most of the time is the following sequence of operation:
Solution: You probably need to purchase and install a new igniter. I would suggest that you inspect your igniter closely for cracks. Make sure you do not touch the igniter with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, roll-out switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
NATE, NCCER, PHCC,HVAC Certified Instructor
Oct 25, 2010 | Heating & Cooling
Hot surface ignitor won't ignite,I replaced the igniter and it still won't.
Goodman furnace model # GMNT100-4B On vacation, neighbor checked house, house filled with gas. He shut off main and furnace. came home turned on gas to everything except furnace. All good. Furnace will...
Solid red typically means bad controller. Try unplugging the furnace, wait about 30 secs, then plug it back in. The possibility that the controller was sending voltage to the valve even when there was no flame is a bad sign. If the controller starts the furnace, watch it very closely and see what it does. If the solid light comes back on, it's time for a new board.
Mar 24, 2010 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
128 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others