Question about Carrier 36KCARMS Air Conditioner
Model 38gf102330 ac fan outside runs all the time
  • 70 Answers
This sounds like a welded contactor if not the fan should run when the compressor does call for cooling it should go off when tstat is off if not check the contactor behind panel turn off power to unit before removing cover on outside unit will need to use ohm meter or someone who knows how to use one
Posted on Jan 05, 2009
2002 4 ton Bryant air conditioner shuts off, fan still runs but not cooling is problem in the controls in the attic or in the AC unit or both?
With a non heat pump it is a simple 24 volt AC control circuit. In the attic there is a relay that is actuated via the fan control wire directly from the thermostat. On the thermostat there is an auto/man switch that controls the fan. Manual the fan runs all the time. Auto fan turns on and off with the outside compressor.
If the system is not calling for cool and the fan continues to run the fan relay is sticking. common problem. Sometimes after running for several days the relay will stop sticking if not, replace relay.
If the system is calling for cool and the compressor stops I would still expect the fan to run until thermostat tells the A/C to off. Some compressor units include a safety switch or high-pressure cut-out switch A blocked internal valve bad control board or external fan in outside unit defective no air flow in outside unit.
High pressure cut out not good,
Suggest turning temp max cool and observe. If acceptable cool and the compressor runs without interruption all is good, except for the blower in the attic. Safely check relay in attic blower circuit.
Hope this helps.
Jun 28, 2017 | Bryant Heating & Cooling
Why is my Intertherm P681S unit getting hot and the fan is is stopping?
Is the outside running? Is the outside fan running? Probably what is happening the fan outside quits running and the compressor gets hot and goes into thermal overload. need to check to make sure the outside fan is running.
Aug 30, 2014 | Heating & Cooling
I have two outside ac one for floor and other for upstairs and i button on heater auto and ac outside fan is running is that normal or not? and live on this new house for two years and cant find someone...
No the fan out side is for a condensing unit and compressor. The compressor should not run with the heat. I am almost positive that if this is not a heat pump that the compressor unit should not be running.
Dec 20, 2010 | Goodman GMS90703BXA Heater
Carrier 38CKC042300. oUTSIDE UNIT FAN WAS TURNING REAL SLOW. ac UNIT IS OFF BUT FAN TO OUTSIDE UNIT IS STILL TURNING. sHOULD NOT BE TURNING AT ALL WITH AC UNIT OFF
The outside fan may run if the unit is in defrost mode this is normal for most heat pumps it is there way of trying to keep the outside unit from staying iced over so the next time the unit runs it will have air flow through the coil and the ice will not be there to prevent air flow.
Jan 12, 2010 | Carrier 38CKC042 Air Conditioner
Kenmore AC compressor on and off while outside unit fan running
If the out door fan keeps running and the compressor cycles off that would be the overload in the compressor.
What keeps the windings cool is the refrigerant back to the compressor.
For the overload to cycle it would have to be either not enough cooling back to the compressor or high amp draw, which could be the metering device (txv or orifice) or low on charge, or other things would be a bad capacitor, sometimes a bad start relay not staying open, when compressor gets up to speed or anything causing the compressor to draw high amps.
To check the refrigerant, he needs to check the superheat at the compressor it should be appoximately 12° to15°, and next time the compressor goes off if you shut the power off and feel the top of the compressor and if it's hot 130° or higher it's probably refrigerant.
Aug 14, 2009 | Heating & Cooling
71122 ac model starts but the fan does not blow any air .shuts off within seconds.
which fan shuts down? Outside condensor fan? Or blower inside? If its the outside condensor fan motor you probably have a bad run capacitor or a bad condensor fan motor
Jul 26, 2009 | Heating & Cooling
1990 model RUUD AC unit. Fan runs, no cooling
Is the outside unit running? Fan and compressor?
Jun 29, 2009 | Heating & Cooling
UNIT RUNS AN EXCESSIVE AMOUNT OF TIME AND AIR IS COOL NOT COLD COMING OUT OF VENTS CARRIER 58DLA / 58DLX CENTRAL AC FAN AND COMPRESSOR ARE OPERATING BLOWER IS WORKING UNIT IS TURNED ON TO AC TEMP SET AT 76...
DOES THE HOUSE FEEL DRIER IF IT IS 80 OUTSIDE WITH ALOT OF HUMIDITY THE UNIT WILL RUN FOR A LONG TIME TO REMOVE THE MOISTURE(HUMIDITY) OUT OF THE HOUSE BEFORE TEMP DROPS DRAMATICALLY IS THERE WATER COMING OUT OF THE DRAIN PIPE OUTSIDE
May 03, 2009 | Carrier Heating & Cooling
Central ac blowing hot air outside fan not moving but making a noise
This is nothing but an either or -or ! First, make the thermostat calls for cool, there are suppose to be 2- noise outside, the fan motor and the compressor (and if a old system,a humming noise which is the contactor coil which picks up the main 240-volts).. hurry up and take a stick or something and turn the fan blades, if it picks up speed and run, then its the capicator. If not then the fan motor is bad.! (BOTTOM LINE)!
Jun 09, 2008 | Heating & Cooling
Carrier 36KCARMS Air Conditioner Logo
46 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others