Maestro Lutron MAW-603-RH  3-way 600 Watt Preset Package  Logo
A
Anonymous Posted on Jan 16, 2011

I bought a MAW-603 with an accessory dimmer to be placed in a 4 way circuit. I followed the instruction on how to connect the accessory dimmer in the 4 way switch location but doesn't work. When I leave the regular 4 way switch the other two switches work. Is MAW-603 the same as a MA 600 multilocation?

1 Answer

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

  • Master 565 Answers
  • Posted on Jan 16, 2011
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

Joined: Jan 24, 2009
Answers
565
Questions
0
Helped
269889
Points
1490

You are saying that you have a "4-way circuit". That means that you originally had two 3-way switches and at least one 4-way switch. ALL existing mechanical switches _must_ to be replaced with electronic dimmers in order for things to work correctly. You must have only _one_ master dimmer (MA-600) located wherever you desire. All of the other switch locations must be companion dimmers (MA-R)., NOT mechanical switches.

The MAW-603-RH comes with a master dimmer and one companion dimmer, so I suspect that you need to install one more companion dimmer.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Can I reuse a Lutron Maestro MAW-603 dimmer in a 2 way situation?

you should be able to by hooking up the black wire on the dimmer to the hot wire(that comes from the electrical panel) in the wall box and the red wire from dimmer to the switch leg(the wire that goes to light fixture). if the dimmer has a white wire(nuetral wire) you will need to hook that up to the white wires in the wall box....CAUTION!!! when removing the old 1 pole switch, there should only be 2 wires and possibly a green or bare copper ground wire attached to it. if either of the 2 wires(not the ground) are white, IT IS MISLABLED OR MISCOLORED. DO NOT hook the dimmers white wire to it cuz it will fry the dimmer. If this is the case, then most likley you do not have a nuetral in the wall box but look anyway for a couple of white wires tied together with a wire nut and stuffed in the back of the box. if you find those than most likely thats your neutral(check with a wiggy or meter to be sure) and thats where the dimmers white wire goes. hook up the dimmers green wire to a green or bare copper wire in the wall box and then put a wire nut on the dimmers red w/white stripe wire.
2helpful
2answers

Need the wiring diagram for MAW-603-rh-wh

http://www.lutron.com/TechnicalDocumentLibrary/0301122A.pdf

On the first page, its the wiring diagram smack-dab in the middle.
If you couldn't find it before, its because the MAW-603-RH-WH is a package containing two other products, the MA-600 and the MA-R. So the instructions I have noted above are appropriate.
0helpful
1answer

Removed the switch plate and connected the two wires going into the dimmer box and the lights still dont come on. I as thikning by bypassing the dimmer the lights should still function. What else could be...

Hi Jay,
Ive suspect that there's a problem in the main line of the wiring. Since four halogen bulb are already replaced with a new bulb and bypassed the dimmer switch concentrate now on the wiring and the main panel board. Look for a tripped/busted breaker on the box, reset it.Replaced if busted. If nothing works, you need to check the wiring on the ceiling for open.
Hope it may help you.
Have a nice day!
Thanks for using fixya.
JDVillanueva
0helpful
1answer

Removed the switch plate and connected the two wires going into the dimmer box and the lights still dont come on. I as thikning by bypassing the dimmer the lights should still function. What else could be...

I am going to stick my neck out a little with this one although I agree with BoomerP. The clue of halogen bulbs is feeding my answer. Halogen bulbs require a high voltage transformer to operate and won't normally work with a dimmer but I never tried it. Bypassing the switch should bring them on though. If you have the proper voltage at the switch and they don't work with the switch bypassed, its probably a bad transformer in the fixture. Good Luck. Be careful.
0helpful
1answer

I have a Meastro dimmer MAW-600 W that is installed, but the light does not turn on and the LED keeps blinking. Any idea what the problem can be?

1) If this installation was working before, the Maestro has a small pull-out circuit breaker that lets you reset the device. This is called the FASS Front Accessible Service Switch, located at bottom of dimmer where it meets cover plate.
Open sample Lutron Maestro dimmer manual to see FASS illustration
http://www.lutron.com/TechnicalDocumentLibrary/0301106A.pdf

2) If this is new installation, then double-check your wiring and check that load matches dimmer capacity: 600 watt incandescent or halogen, which excludes CFLs apparently.
Some electronic devices have shortened lifespan on circuits that are not clean. Use circuit analyzer on outlet on same breaker to see if line has interference.

3) I don't see MAW-600 W listed among Maestro dimmers, so I don't have that specific manual.
http://www.lutron.com/Service-Support/Technical/InstallationInstructions/Pages/InstallationInstructions.aspx?syst=Dimmers+%26+Switches&prodn=Maestro%C2%AE+dimmer+%26+switch

4) Amazon certainly shows the MAW-600 W, in case you need a replacement.
http://www.amazon.com/Lutron-MAW600H-WH-Electronics-Maestro-Dimmer/dp/B000BPCWQE

5) Lutron has customer service numbers:
1.888.LUTRON1 (588.7661)
1-800-523-9466

Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on dimmer or any do-it-yourself project.
Fixya is always less expensive than a service call.
0helpful
2answers

I have a Lutron Maestro MAW-600 switch connected to 2 pendant lights and the 2 pendant lights bulbs blew. I replaced the bulbs but the lights still do not come on. The Lutron switch flashes green rapidly...

Lutron Maestro MAW-600 manual:
Single-Pole 600 Watt Halogen/ Incandescent Dimmer (minimum 40 Watt)
http://www.lutron.com/TechnicalDocumentLibrary/0301106A.pdf

Lutron technical support 1.800.523.9466


geno_3245_107.jpg

You said pendant lights blew out.
How many total watts were those lights?
Did you remove aluminum break-away fins on side of device to match wattage?

Front indicator can be pulled out to cut power to circuit.
This is called FASS switch.
Try pulling out FASS switch and then pushing it back to see if it re-sets device.
Click breaker on-off to see if it resets device.
You replaced a single-pole switch that has two wires plug ground wire.
Each wire from switch goes to either screw on MAW-600 so it's hard to go wrong there.
Bare copper goes to green ground screw.
Otherwise, it looks like tech support is next step: 1800-523-9466
geno_3245_108.jpg
0helpful
1answer

How do I wire up a Maestro Lutron MAW-603-RH dimmer in a 4-way situation?

If you bought the 3-way package, there should've been two products included: the MA-600- and the MA-R. First of all, if this is a four way circuit, that means you currently have at least three switch locations. The package you bought takes cares of two of those locations, but to get the third, you need another MA-R. If there are more locations than that, each additional location requires an MA-R.

It doesn't matter which product (the MA-600 or the MA-R) you put at each location. They all wire the same.

At the 3-way locations (ends of the lighting circuit), install the dimmers just like you would a standard 3-way switch. The only thing I caution you, make sure that the blue screw on the dimmer is connected to one of the traveller wires going to the next switch box. Also note what color wire its attached to - because when you go to that next switch box, the blue screw of that dimmer needs to tie to that same wire. At the 4-way switch box, the most important thing to remember is this.... make sure all the blue screws are connected together (which is why its important to know WHICH wire is connected to the 3-way switches).

As long as you have enough product and you tie the blue screws together, it should work.
0helpful
1answer

The lights on the dimmer flash and/or brighten and dim on their own. How do we fix this?

For 100% certainty, I would call Lutron's tech support at 1-800-523-9466. They're available 24/7 and can probably troubleshoot it more effectively than through this text-based dialogue. However...

I have three guesses...

1) Check the minimum load. The minimum load for those products is about 40-Watts. If there isn't enough lamp wattage pulling electricity through the dimmer, the dimmer may not have enough juice to keep itself powered up... and then shut down (hence any flashing you may see). If the issue only happens when the lights are at full (or close to full) brightness, then that's most likley your issue. To solve, either increase the lamp wattage, or replace with a dimmer that contains a neutral wire such as the MAELV-600M.

2) Check the load type. The dimmer's are rated for incandescent & halogen. If these are LED or CFL lamps, you are going t see issues. For dimming performance, either convert the lamps to incandescent / halogen, or investigate their new Diva dimmer for CFLs & LEDs: DVCL-153P-

3) If neither of those solve the problem, the next guess is to check the wiring. I wouldn't expect this to cause any "flashing" but in the wiring circuit, each device had a blue screw attached to it, and you need to make sure that the blue screws are wired/connected to each other and ONLY to each other - otherwise "automatic" dimming can take place.

But again, the only way to be certain is to use their tech support. I highly encourage you to use that.
2helpful
2answers

Our lutron three way dimmers leak when off. There appears to be about 8 volts still going to the fixtures. That causes the transformers on the fixtures to sing when off. Probably not good for...

If each fixture has an individual transformer, the chace is that they are electronic (about the size of a matchbox car) If so, you have the wrong dimmer installed. You will need to install a MAELV (Electronic Low Voltage) Dimmer. The regular dimmers are set up for Magnetic Low Voltage and incandescent which work differently. http://www.lutron.com/TechnicalDocumentLibrary/362219.pdf

Here is a link to the difference in how they work. Also, if they are a Low Wattage light like an LED, the dimmer may not have enough resistance to bleed off the excess voltage. The MAW-600 has a minimum load of either 25 or 40 watts. If you are operating LED's you may also need a Low Wattage Interface to act as a simulated load that wires in series with your lights. (lut-lbx)

If it gets too anoying until you get the proper dimmer, you can switch the Air Gap switch at the bottom to the off position. This completely disconnects the power to the load side of the dimmer.

Good Luck
Not finding what you are looking for?

305 views

Ask a Question

Usually answered in minutes!

Top Maestro Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66931 Answers

Are you a Maestro Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...