Question about Coleman Heating & Cooling
I have a coleman/evcon heat pump. When the thermostat kicks on the contacts kick in and hum but the compressor nor the fan run. Is this probably my capacitor has gone bad?
  • 828 Answers
I would check the hig voltage power supply to the unit. Check the main breaker and make sure it is on. Check the disconnect and make sure there is power at that point to the condensing unit. The contactor will kick in from the low voltage in the control circuit.
Posted on Jul 11, 2008
Coleman Evcon furnace blower runs w/ no call for heat. Temp is 5+ degrees above thermostat setting. (Programmable tstat)
When you say door are you referring to the front door or the furnace door? If the unit kicks on AND off by itself I would say it's in the tstat or the tstat wire. If it were internal I would think the blower relay or heat contactor/relay were getting stuck AND THE FAN WOULD NOT TURN OFF until you flipped the breaker. Good luck
Mar 21, 2017 | Coleman Heating & Cooling
Coleman Evcon furnace. Can i make it circulate air?
Your thermostat should have a "continuous blower" setting. Use that instead of fooling around with the A/C setting
Jul 17, 2013 | Coleman 7990-319p Evcon Gas Furnace...
When the furnace shuts down, blower kicks on and off
Probably residual heat kicking the fan limit control on and off. Readjust the settings on the fan limit control.
Nov 15, 2012 | Coleman Evcon Furnace Control Circuit...
I have a coleman evcon system model BRHQ0301BC. The fan on the outside unit will not always kick on. When the fan does not kick on the AC does work. Need a manual for unit and help repairing the proiblem.
I don't have a manual but you need to check the fan capacitor and the fan motor windings with a multimeter. If the capacitor looks swollen then it is probably bad. Replace it with one of the same rating.
Jun 07, 2010 | Coleman Heating & Cooling
My Coleman Evcon heating and air unit will not blow air
bad blower motor. recommend a new blower motor and capacitor.
May 28, 2010 | Coleman Heating & Cooling
No heat at night
You have a poor low voltage connection from the thermostat or a bad contactor.The contactor is the main relay control inside the condensing unit. The incoming voltage wires connect to it.
Contactors are inexpensive. I would change that first.
Check all your low voltage wires in the condensing unit for loose connections.
Dec 11, 2009 | Coleman Heating & Cooling
My goodman gas furnace is not kicking on. the light on the unit is saying that it should be working but it is not. there is no pilot light, the fan is working the heat is not
If you are not getting any codes from the board, then the furnace is not getting a call for heat from the thermostat. A wire may have come off, the thermostat not properly wired, or a break in the stat wire. On a call for heat, you should have 24vac between W and C on the circuit board. This will let you know if you are getting a call for heat all the way back to the furnace.
Oct 01, 2009 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
276 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others