Armstrong furnace model# guk100d14-2b replaced ignition,flame sensor module.Unit runs perfict for about 10 full cycles then cycles out .Then starts, again blowing only cold air.shut it off restart it and it fires just fine again.
  • 3 Answers
SOURCE: flame rollout sensor keeps tripping
The flame rollout sensor is a rather important safety feature that ideally only trips when there's an overtemperture outside of the combustion chamber. I'd encourage you to get a better quality tech in ASAP to check for a cracked heat exchanger, gas overpressure, restricted airflow (changed the filter lately?), maybe a blocked condensate drain if this is a high efficiency furnace. If the sensor was replaced and it's still tripping, you've got a potentially dangerous overheating issue that you don't want to try to bypass.
Posted on Mar 20, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Posted on Nov 23, 2009
  • 588 Answers
SOURCE: the ignition light comes on, gas flames starts,
Sounds like open limit switch or roll out switch.
Posted on Dec 30, 2009
  • 288 Answers
SOURCE: Goodman furnace burner ignites then shuts off in about 10 seconds
if you have replaced the flame sensor and it will not stay lit, the draft safety switch may be opening. It works on positive and negative pressure created by the inducer fan motor.You may have a restriction in your heat exchanger or if is a high efficiency furnace, it may not have the drain tube installed properly with a trap. The trap works just like the trap under your sink and if water isnt in the trap, the pressures can be effected enough to open the draft switch(some call it an air pressure switch)
Posted on Jan 07, 2010
  • 3249 Answers
SOURCE: ignition problem with furnace
hi igniter could be in the wrong postion or its not heating up all the way down or its got a crack in it
Posted on Jan 22, 2010
Furnace drops off on first start up cycle, immediately lights on second. Cleaned flame sensor(flame rectification) 7 days ago.
Replaced tour flame.sensor ,also you might have a control board going bad but first thing I would do is replaced the sensor and see what happens.
If issue still happening then replaced the board
Feb 23, 2018 | Heating & Cooling
Furnace won't stay lit. Intertherm Model M2RC-080A-16BN. Ignightor glows, flame starts and after a few seconds the flame shuts off. Then it starts the cycle again. It goes thru this cycle a fe
It sounds like the flame sensor is bad. If thats not the case you may need to replace the control board. You should make sure the flame sensor is directly into the flame.
Nov 20, 2014 | Intertherm Heating & Cooling
Hello, I have a Amana Air Command 80 model #GHI90A50, 22 years old. This furnace is on its third ingnition module (last one two yeras ago). The symptom I am trying to diagnose has been ongioing since this...
If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 05, 2010 | Heating & Cooling
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Gibson Furnace, Model #7106250 can not get a flame going. The furnace runs fine but is pumping out cold air without a flame. Any ideas?
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose, Dirty Air Filter), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 04, 2010 | Heating & Cooling
Just replaced idnitor and flame sensor on a bryant model 376c and its still not kicking on. blower kicks on fans kick on and then cycles off. no heat need help
Make sure all wires are connected and the gas is on. Follow the sequence of operation for this model and a few tips on what could be the issue.
Jan 27, 2010 | Heating & Cooling
Heater going through start cycle 3 times, but will not stay lit. Took temp sensor out,cleaned it, and put it back in. heater worked fibe for a while, back to same problem. Does it sound as if maybe sensor...
This unit will give you an error code on the circuit board to help with a starting point. Read on further,
Jan 26, 2010 | Goodman GMS90703BXA Heater
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling