Our Temstar gas furnace keeps turning off. The pilot light keeps going out.. can I adjust the pilot light or is there another problem?
  • jgov09 Jan 04, 2011
    Thank you
  • 2,299 Answers
If the pilot light is going out, then it could be one of two things. Either a draft blowing the pilot light out. Or the thermal couple is bad. The thermal couple is the little rod that the pilot light heats. It is directly above the flame of the pilot light. This is what tells the gas valve to stay open and supply the pilot with gas. If it is a draft, you should see the pilot light blowing. If this is the case. Then look for where the draft is coming from and get it sealed up. But usually it is the thermal couple.
Posted on Jan 03, 2011
Williams wall heater 2509622. How do I keep the pilot on? It tends to turn off after it reaches the desired temperature.
WILLIAMS 2509622 OWNER'S MANUAL Pdf Download.
www.manualslib.com > Brands > Williams Manuals > Furnace > 2509622
2509622; 2539622; 2559622; 3509622; 3539622; 3559622; ... WHAT TO DO IF YOU SMELL GAS: ... Williams furnace co. direct-vent wall furnace owner's manual (24 pages) ... Caring for Your Furnace ............24-25 Locating Wall Furnace and Thermostat ........6-7 Learn how to keep your new Williams Furnace operating.
How to light Heater or Furnace Pilot Light Gas Pilot of ...
? 5:01
https://www.youtube.com/watch?v=FZVQmKTYTTg
Oct 25, 2013 - Uploaded by 3p0cHx
How to light a gas pilot for a heater or furnace of the Williamstype. This is a general guide and is not ...
[PDF]Monterey Installation Instruction Manual - Home Depot
Dec 08, 2015 | Williams Heating & Cooling
How do you adjust the pilot light flow on an old magic chef heating unit/ceiling mounted furnace?
How long is the pilot flame? It could be you can move the thermocouple into the flame by making adjustments of the metal holder. If the flame is small, there is an adjustment for the piolet flow in the control module where you turn gas on and off and light the pilot. It should be labeled and usually has a cover that must be unscrewed to reveal the adjusting screw. Need a bright flash light to see what you're doing.
Feb 28, 2015 | Heating & Cooling
Pilot light won't light
Will it initially light, then go out when you release the button?
If yes, then change/adjust the thermocouple or pilot size.
If no, then check that you have a gas supply, that the igniter is sparking, that the gas valve is allowing the pilot flow through.
Apr 06, 2014 | Intertherm 56000 Btu Gas Furnace
My heil furnance comes on but no hot air or air at all
see this causes and fix it. God bless you
o light the pilot on a standing-pilot (always on) ignition system, follow the lighting instructions located near the control. Otherwise, try these steps: Light the pilot:
  1. gasfurnace1.jpg Press and hold the pilot control knob to start the pilot. Set the control knob to the pilot position. Hold a long match under the pilot gas port.
  2. Press the control knob; the pilot should light. Hold the control knob down until the flame is burning brightly (about 30 seconds). Release pressure on the knob, and turn it to the on position.
  3. If the pilot goes out when you release the control knob, try relighting, holding the control knob down longer. If the pilot again goes out, check the thermocouple (below).
Adjust the pilot:
  1. Remove any cap covering the pilot adjusting screw on a combination control.
  2. Turn the adjusting screw counterclockwise to increase the flame or clockwise to decrease it. It is correctly adjusted when the flame envelops the thermocouple bulb by 1/2 inch and appears dark blue with a small yellow tip.
Test and replace a thermocouple:
  1. Hold the control knob to pilot and light the pilot as above.
  2. Unscrew the thermocouple fitting with an open-ended wrench.
  3. Set a multimeter to the DVC (lowest voltage) scale.
  4. Clip one multimeter lead to the end of the thermocouple tube nearest the pilot and the other lead to the fitting on the other end of the tube.
  5. If the multimeter shows a reading besides zero, the thermocouple is functioning. Replace the thermocouple tube.
  6. If there is no reading, you will need to clean or replace the thermocouple following steps 7 through 11.
  7. Release the control knob and shut off the main gas valve on the gas-supply pipe that leads into the burner. Shut off power to the burner at the electrical service panel .
  8. Remove the thermocouple from its mounting bracket.
  9. Wipe the combination control clean and install a new thermocouple, tightening it by hand, then give it a one-quarter turn with a wrench.
  10. Insert the thermocouple into the pilot bracket, being careful to not crimp the tubing.
  11. Turn on power to the furnace and relight the pilot (above).
Adjust an adjustable burner air shutter:
  1. Set the thermostat to its highest setting to keep the burner running. Once the furnace has heated up, remove the burner access panel and loosen the locking screw.
  2. Open the shutter by turning it to the right until the blue base of the flame appears to lift slightly from the burner port surface. Then close the shutter until the flame reseats itself on the surface.
Clean removable burner tubes and ports:
  1. Shut off gas and power to the furnace.
  2. Unscrew or loosen and remove the tubes from the supporting bracket.
  3. Carefully clean the tubes with a brush or vacuum, making sure not to damage the burner ports.
  4. Use a stiff wire to clear any debris from clogged ports.
Oct 08, 2012 | Honeywell Icp Heil Tempstar Furnace Spark...
How to light pilot on Dayton furnace and then start furnace
If this is a standing pilot system, turn the gas valve to pilot position. push in the knob & hold while lighting pilot...keeping holding knob down for a minute... this will pick & hold the gas valve. Let go of the knob & see if the pilot stays lit, if it does, then turn the knob to on position & the furnace should start if there is a call for heat from the thermostat
Sep 15, 2011 | Dayton Gas Furnace Heater
I have a 1987 Goodman, (GU150-5 REV S) model gas furnace. The problem I have is keeping the pilot light on. I replace the thermal coupling twice, work for a few days and goes out again. Please tell me what...
If you have a weak pilot flame it could cause this. There is an adjustment screw for the pilot flame under another philips head screw that takes a small flat head screwdriver to adjust. Turning the pilot flame up may help.
Dec 21, 2009 | Goodman GMS90703BXA Heater
My pilot keeps going out on the furnace. We lite
Check the pilot light size. Is it small and not surrounding the top 1/3 of the thermocouple? If it isn't then the pilot orfice is restricted or the pilot tube compression nut could be loose. The pilot gas adjustment screw may also need adjusting if this gas valve has one. These problems should only be addressed by an experienced service tech.
Nov 09, 2009 | Heating & Cooling
Lighting the pilot light
The steps involved can vary slightly depending on your furnace model and pilot valve type, so if possible try and find the instructions inside the furnace door cover or in the instruction manual. This is for a gas fired furnace, but applies to any gas-fueled appliance including water heater. Two of the most common types of pilot valve body assemblies either have a red reset button and a gas valve or no reset button and a valve knob that can be depressed. But whichever type you've got, if you have an older model furnace with a standing pilot (flame is lit all the time) then this is the basic procedure.
  • Turn you thermostat to 80 degrees or to a setting that will demand heat. Make sure the thermostat is in "Heat" mode.
  • Go to the furnace and find the pilot valve. The pilot valve body is a box shaped device into which the main gas line will run and is located near the gas burners. It will usually have a gas **** or valve knob that reads "On, "Pilot" and "Off." Locate this gas **** or knob.
  • Turn the knob or gas **** to the "Off" position and wait about 3 minutes for any residual gas to clear away.
  • Find the pilot. It's located near the gas burner tube assembly in the furnace.
  • Get your match or lighter ready. Sometimes the pilot is hard to reach. If possible, try and use a long fireplace match when you light it. If you don't have a fireplace match then a butane BBQ grill lighter works well too. If you don't have that, then you can fasten a match to the end of a stick when you light the pilot
  • If you have a pilot with a red Reset button, turn the gas valve from "Off," to "Pilot."
  • If you have a pilot with no red button, turn the knob from "Off" to "Pilot."
  • Place the lit match or ignited lighter tip at the pilot and depress and hold the button or depress the knob as appropriate. Depress the button or knob for about 30 seconds. This maintains gas flow to the pilot until the thermocouple gets hot enough to open the main gas valve.
  • Once the pilot stays lit, slowly release the button or knob and turn the gas **** or knob from the "Pilot" position to the "On" position. This will ignite the burners and keep the flow of gas supplied as required for the burners as called for by the thermostat.
  • If the burners fail to ignite then it may be because the thermocouple did not get hot enough to open the gas valve. Wait a few minutes and then repeat the above procedure. This time hold the red reset button or depress the knob for about 45-60 seconds.
  • Once the main furnace burners ignite, adjust the thermostat to the desired setting.
  • If you've followed the previous steps on lighting the pilot and it still does not light after, or will not stay lit, then you probably have a problem with the thermocouple or an adjustment needs to be made to the pilot. You'll need a furnace service technician to replace or repair these parts. You may find that the pilot lights, but it is an anemic looking flame. That's a different problem we'll look at in the next section.
  • If the pilot lights but the flame is a weak yellow flame, it will not get hot enough to heat the thermocouple to its set point allowing the gas valve to open.
    A natural gas flame should be a bright blue with the tip of the flame having just a tinge of yellow. A propane flame should have a bluish green flame with a tinge of yellow at the tip. The flame should be strong enough to hit the thermocouple tip about 1/2 inch from the tip end. If the flame is weak or shaky looking, check to see that a breeze or draft is not blowing on it. Adjusting the Flame
    There is usually a small screw on the pilot valve body that will adjust the flame. You may have to refer to the manufacturer's instructions to find the screw. Turn the screw as needed to adjust the flame throw. Yellow Flame
    A yellow flame is caused by lack of air and incomplete combustion. It can be caused by a dirty pilot tube tip. Split Flame
    This is caused by dirt in the pilot tube. Take a needle or small nail and gently clean the tube. Flickering or Wavering Flame
    A flame that flickers is usually caused by a draft.
Thanks for using FixYa - a FixYa rating is appreciated!!
Feb 18, 2009 | Water Heaters
The pilot light for the oven went out.
Relighting Your Furnace's Pilot Light
furnace1.jpg - Turn off the gas at the main valve at your utility box - Wait five to ten minutes for gas fumes to waft away - Get a long match—yes, a fireplace match, not a standard match - Set the gas valve on your furnace to "pilot" - Press the red button as you hold the match to the pilot valve - Keep pressing the red button for 30-60 seconds so the pilot can heat the thermocouple. Release the button and see if the pilot remains lit - If pilot goes out, wait five to ten minutes and repeat the process - Once the pilot stays lit, turn the main gas valve back on - If the pilot light continues to go out, call a technician, who may need to adjust or replace your thermocouple or adjust your pilot
Jul 28, 2008 | Tappan 30IN ELEC IGNa Oven
Heating & Cooling Logo
77 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen