HI, I have a Carrier Gas Furnace on my roof. It heats well, but after a heating cycle it sounds as though the inside fan motor is trying to restart. This only lasts for a second each time, but might occur five times right after the unit is done with heating. I am an electrician, and it sounds like someone is "Bumping" the motor. Any ideas? This will happen even if all the thermostat wires are disconnected. Thanks
  • James Wright Jan 04, 2011
    Thanks for the info. I just have to wait a little bit for the frost to get off the before checking!
    I will let you if if that does it or I can't find it. I have a bit of a worn wiring diagram!
    Thanks,
    JIm
    Hi, Thanks for the info. I just have to wait a little bit for the frost to get off the before checking! I will let you if if that does it or I can't find it. I have a bit of a worn wiring diagram!
    Thanks,
    Jim
  • 43,501 Answers
There are two things that can cause that...
The first would be a bad board or relay on the board... the relay is not releasing completely or the board is shorting and causing the relay to bump....
The second would be the high limit bumping and triggering the board to bump the motor...
What I would do is to pull one of the wires from the high limit switch right after it runs and shuts down to see if the problem continues... if it does then the board is bad... if it stops and stays off then the high limit is bad... replace that....
Hope you followed all of this and that it helps you...
heatman101
Posted on Jan 05, 2011
    Genius:
  • 1,015 Answers
It sounds to me like your fan off limit switch is set to low if its adjustable or almost worn out if it's not adjustable. I would like to be of more help but I need more information,such as age and size of your furnace and type of limit switch if you know. Thank you.
Posted on Jan 04, 2011
Furnace reaches temperature set then shuts down and restarts 8 times before final shutdown.
When you say the the furnace re-starts 8 times before shut down, what is cycling 8 times? just the indoor blower or is the main burner re-firing 8 times? If it's only the fan it sounds like the fan control.
Mar 07, 2018 | Coleman Heating & Cooling
Trouble shoot Dayton gas furnace model GG9S100C16MP11A fan is left on constant but in cold weather 10 or colder fan will go off and furnace will go thru a restart mode and run fine for awhile then will do...
Do not run contentiously during heat mode. the fan runs at a slower speed with heat and heat fires first then the fan cycles on during heat cycle then when heat satisfies the thermostat the heat will cycle off and fan will run for a couple more minutes and then cycle off. So set stat on fan cycle to auto.
Feb 03, 2015 | Dayton Gas Furnace Heater
Burner shut off then there is a clicking sound, burner ignites again
this is normal the clicking sound you hear is the system starting another cycle for your furnace to ignite the burners, then turn on tbe fan blower.
Sep 27, 2017 | Heating & Cooling
Furnace gas valve is not opening
YOUR FURNACE IS IN LOCKOUT MODE DUE TO A SAFETY FEATURE OF UNIT. USUALLY THE HIGH LIMIT HAS BEEN TRIPPED, OR YOU PRESSURE SWITCH FROM DRAFT INDUCER MOTOR FAULTY OR PLUGGED. IT WILL CONTINUE LOCKOUT MODE UNTIL THIS IS FIXED.
Dec 23, 2012 | Carrier Weathermaker 8000 Gas Furnace 125k...
Wiring schatic to wire a 10 kw heat strip inside of a trane gas furnace
If you are using strip heat as seperate mode you must install a fan isolation relay which would be energized by emergency ht mode of stat.
Nov 25, 2012 | Carrier 38CKC042 Air Conditioner
Williams wall furnace no longer adequately heats home
A couple thoughts. On some of the wall furnace gas valves there's a knob that you can set for low fire or high fire. If your valve has this make sure it is in the high fire setting. Is the wall furnace controlled by a wall thermostat or a knob on the heater? With the thermostat turned all the way up like to 90, does the burner and fan continue to run or is the burner short cycling. Is the fan clean and running up to speed. Some of the Williams wall furnace had a two speed fan motor so when the fan came on at first it would run on low speed. As the heat exchanger got hotter the internal fan switch would switch it to high speed. Outside of that you would need a monometer to check the manifold gas pressure.
Aug 31, 2017 | Heating & Cooling
Carrier Heating furnace
either the gas at the outside valve is off, or the gas valve at the furnace may be off, or the switch on top of the gas valve in the furace may be off. if they are all on, then you may not be getting a call for heat from the stat to the furnace control board. check to see if you are getting a 24 volt signal from the stat to the w terminal and common terminal on the furnace board. if you are then check to see if the voltage is arriving as 24 volts to the wires at the gas valve itself . if it is then the gas valve is possibly bad. if it is not then the board is possibly bad.look for loose or broken connections on the low voltage wiring. most unusual that the board does everything else but send power to the gas valve. you need to zero in on the valve i think and start by turning off power and that should restart the sequence of operation and you can observe it step by step . if you are not getting a call for heat then the stat may be bad be sure you are in heat , fan in auto and temp pushed up to max. if no 24 volts is sent to furnace board white and common low voltage board then stat is bad. remove it if you think its faulty and jumper the white and red wires together on the subbase. that duplicates what the stat normally does. if the furnace lights its the stat. having said that i realize the stat has to be sending a heat signal or the other stuff would'nt start. so..... back to the furnace board. check that 24 volts in from stat and 24 out to valve and that will put you on your problem item. good luck
Oct 30, 2008 | Carrier 38BRC048 Air Conditioner