My Gas heater went off. When I turn it back on, the heater makes all the necessary noises/switches, however, it does not ignite. The flue is clean. I cannot tell whether the pilot is lit or not. I am afraid to move or turn anything. What can be wrong?
  • 1,772 Answers
Hello and sorry to hear about your problem.
It sounds like your heater glow rod, is defective. This is the electronic pilot lite for the unit.
THIS IS A GAS PRODUCT, INCORRECT REPAIR CAN CAUSE A EXPLOSION, AND DEATH CAN OCCUR. IF YOU DO HAVE THE PROPER TOOLS SUCH AS MANOMETER AND LEAK DETECTORS, I SUGGEST YOU CONTACT A SERVICE COMPANY
I have tried to help you. Please help me by Vote/Rate this response. Thanks and good luck.
4 Thumbs - Very Helpful
3 Thumbs - Helpful
2 Thumbs - Somewhat Helpful
1 Thumb - Not Helpful
Posted on Jan 03, 2011
Testimonial: "Thank you for your feedback. I will be able to at least have some conversation with the repairman. Thank you so much."
Haywood h400 pool heater, flames coming out of flue
check gas if ok clean burners make sure it is a propane unit if a N in model number it is natural gas orfices incorrect and will overheat very dangerous
Sep 09, 2012 | Hayward H Series Pool & Spa Heater 400k...
Glo warm heater
the regulator IS not only the issue, but it's a major safety benefit,..the pilot flame is non adunstable..get a cheap regulator(like the ones for the outdoor bbq's)
Mar 16, 2008 | Heating & Cooling
I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong
Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Oct 18, 2011 | Goodman GMS90703BXA Heater
Rheem super quite 80, two blinks, no water in pressure switch line - not igniting, just making humming noise.
Hello, this code indicates a open pressure switch. Most common causes are weak inducer motor not creating enough pressure to close switch, blocked flue pipe, or the switch itself is defective.
Sep 26, 2011 | Heating & Cooling
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
My rinnai 1004 keep shuting off and is blinking 14
CODE DISPLAYED FAULT REMEDY 11 Ignition Failure Check that gas is turned ON. Service call if repeated. 12 Flame Failure Check that gas is turned ON. Service call if repeated. 14 Overheat Clean filter. Service call if repeated. [1] 16 Room Overheat Lower room temperature to less than 104°F (40°C). 31 32 Room Temperature Sensor Faulty Service call. 33 34 Overheat Temperature Sensor Faulty Service call. 49 Sensor Breakdown Service call. 53 Sparker Failure Service call. 61 Combustion Fan Failure Service call. 70 Faulty ON/OFF Switch Service call. 71 Faulty Solenoids Service call. 72 Faulty Flame Rod Service call. 73 Communication Error Turn heater OFF, then ON again. 99 Flue Block Check around the flue terminal for blockage. [2] [1] Remove any obstructions. The flue needs to be kept clear to expel exhaust gases. If the appliance fails to operate contact a qualified service agency. [2] If the fusible link needs replacement, it must be done by a qualified service agency. In addition, the cause of the overheat needs to be determined. The fusible link is a one use safety device that breaks to shut off the appliance.
Dec 17, 2010 | Rinnai RHFE-1004FA 38,400 BTU Energy Saver...
When gas wall heater lights a ball of flame comes
Lets get a tech in there to get it cleaned and the gas pressure checked.
Jan 18, 2010 | Off The Wall Heating & Cooling
Vulcan Ilec central heater main burners turn off after few second
Flame rollout sensors, overheat thermistor, air proving switch, bad earthing, blocked flue. Any of these things can cause your problem. If its a permanent pilot, is it clean burning?? If electronic ignition, is the flame rod clean i.e. no carbon or rust etc.. Safest bet is a qualified gasfitter take a look at it.
Jul 02, 2009 | Heating & Cooling
Intermediate whistle
sounds like you have dust or spider web in one of the burner tubes. turn power off to unit and clean the burners especiaally by the nossles
Nov 23, 2008 | Rinnai RHFE-1004FA 38,400 BTU Energy Saver...
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.