Question about Lutron 1000-Watt Incandescent Dimmer Switch by Electronics, Inc
I replaced a 600 watt dimmer switch with a 1000 watt dimmer after installing a new chandelier. The chandelier works, but a neighboring room does not. When I put the 600 watt back in, the other room works again. I'm not leaving any wires out (there are 3 + ground, and I have tried every possible configuration). The chandelier always works. Is it possible the switch is defective? The breaker box never trips. I have gone back and forth with the two switches and the problem is always the same.
  • BoomerP Jan 05, 2011
    I think you need to explain the "other room" thing a bit more. Are you talking about the lights in another room, or is there a light switch for this chandelier in that other room?
    Problem Solver:
  • 10 Answers
You miswired the switch. One of your black wires is misplaced.
Posted on Jan 16, 2011
Dimmer switch buzzing and lights won't stay lit
Check the rating of the dimmer switch. It is more than likely a 600-watt dimmer. Either way you should replace the dimmer switch with a 1000-watt rated dimmer switch.
Feb 14, 2013 | Intermatic T104 24h 208-277v Mechanical...
Lutron dimmer switch # D1500 1500 120vac Voltage to switch is OK but lights(8 100watts) do not go on.
I can't locate the Lutron D1500 dimmer switch on Lutron web site. Perhaps there is a different number for it.
Anyway, you are attempting to dim a total of 800 watts of light. A standard dimmer switch will not handle this much of a load as they are rated for 600 watts. A 1000 dimmer is the next size up and would be the minimum rating to be used. This means the dimmer would be operating at 80% of capacity and the switch may become warm - but all within acceptable limits.
A dimmer switch rated at 1200 watts or even 1500 watts may be a better choice, as the 800 watt load would present a load that would only be 66% and 53% (respectively) of rated capacity, and would likely run cooler and last a lot longer.
The down side to these higher wattage rated switches is their cost. It is not unusual for the price to double for a 600w vs a 1000w dimmer.
Sometimes, a 1000w dimmer is not sufficient to control a 600w load. This happens when 2 or more dimmer switches are installed in a single location under one wall plate. It is a fairly common arrangement for electricians to install 2, 3 or more "ganged boxes" so that there aren't 2, 3 or more individual switches clustered around a doorway. Even though a two ganged box has twice the area of a one gang box, the issue is about heat dissipation. A box will contain the heat. So the heat is given up from the front of the switch. The metal fins provide more area for cooling. When two or more dimmers are located in a multiple-ganged box, there is too much heat for the space. Two 600 watt dimmers would need to be derated to about 450 watts each (instructions for derating are included with the switch - each manufacturer has their own formulas), and if three 600 watt dimmers were in a single location, they might need to be derated to 300 watts each. So, simply moving to a 1000 watt or 1200 watt dimmer may not get you to the 600 watt level if there are several dimmers that require derating to 50%. Installing dimmers in boxes with standard "toggle" type (non-dimming) switches require no derating as toggle switches do not produce appreciable heat.
Make sure that the lighting load is a type designed for dimming. The popular CFL (compact fluorescent lamps) are not designed for dimming, unless the package specifically states otherwise. Lights that have a filiment but no transformer, ballast, starter, etc. are the only ones suitable for use with a dimmer (again - unless the package / fixture states otherwise). The dimmable types are typically "standard" incandescent, quartz, halogen and tungsten types.
Furthermore, a dimmer switch is not suitable for use as a fan speed control either. There are special switches to provide speed control of fan motors. Use of a dimmer on a motor load is a fire hazard.
I hope this helps & good luck!
Jan 08, 2013 | Lutron Electrical Supplies
I changed the light bulbs in the fixture it controls, now it does not work. What is wrong?
This switch is designed to dim incandescent lamps. It has nothing in its description about being used with CFL (compact fluorescent lamps) types. If you are attempting to dim standard CFL types, it will not work.
CFL's are available in both dim-able and standard types. As you may have guessed, only those marked as "dim-able" will work with a dimmer switch. Dim-able CFLs cost slightly more than standard CFLs but may be controlled by any switch. Dimmer switches may only control incandescent and other type lamps that specifically state they are compatible with dimmer switches.
If you are attempting to dim incandescent lamps, make sure that you are not trying to dim lamps with a total wattage greater than the dimmer can handle. Most dimmer switches are rated for 600 watts, if you have two dimmer switches under one wall plate, the wattage rating drops to about 500 watts. This de-rating is because of the heat the switches create. There are dimmer switches that can dim more than 600 watts, but the price skyrockets for a 1000 watt dimmer, and keeps climbing.
If your wattage is within the limits of the dimmer, check the bulbs. If they are ok, the dimmer may have failed and require replacement.
If you found my reply helpful, please rate it "4 thumbs up". Good luck & thanks!
Aug 16, 2011 | GE 18027 Dimmer Toggle OnOff with Slide...
I have always used a lutron maestro dimmer. I replaced the chandelier and put in 6-60 watt bulbs. My previous chandelier used 18-25 watt chandelier bulbs and the dimmer worked fine. after changing the...
You should have just two wires plus a ground hooked up to the dimmer. It should install just like the maestro. If you are getting no lights with a double tap, or tap and hold, and if the led is not on, it is one of several things. Most are basic, but will list anyway. Check that your connections are good. Make sure you have power there. Make sure the bulbs are good. If all is fine, you probably have a defective dimmer if it worked prior to this. To test, take the dimmer out, restore power, and carefully touch one insulated wire to the other one. If the light comes on, it is the dimmer at fault.
Mar 06, 2011 | Lutron ELECTRONICS MAW-600H-LA SMART...
The dimmer switch will turn on and off but wont dim the lights on a chandelier. model 6681-w. tried 2 different ones with the same results.
The Leviton 6681 is a push-button rotary-type incandescent dimmer with 600Watt capacity
If you have incandescent bulbs, the dimmer should work.
If the dimmer has different color wires, try reversing the wires.
If the dimmer replaced a 3-way switch, then this is not the right dimmer.
If you have compact florescent bulbs, you need a dimmer that also dims florescent.
http://www.google.com/products/catalog
Link shows the Leviton 6673 incandescent and florescent dimmer
But you also need dimmable compact florescent bulbs.
http://www.amazon.com/DIMMABLE-COMPACT-FLUORESCENT-LIGHT-SPIRAL/dp/B0014B84ZM
Oct 31, 2010 | Leviton #L11-06681-00I Ivory 600 Watt Push...
I am not quite the talking type but i don't wanna burn down the house
Need to know what is your issue. If you are asking how to hook it up it is a simple task. First you need to confirm if it is a single pole or 3-way switch. Does more than one switch control the light? If not is a single pole switch. I would first turn off the power to the switch you are replacing. Check this by turning on the light and turn off breakers one at a time until the light goes out. Take out old switch and connect new one. tkae one wire off old switch and connect it to one wire on dimmer. Doesn't matter which one. Take the second wire off the switch and connect it to the remaining wire of the dimmer. If you have a ground wire (bare copper wire) connected to the old switch and you have a bare or green wire on the dimmer, connect those together as well. Mount dimmer in box, re-energize circuit and you should be good to go. I am curious why you are using a 1000 watt switch (unless you are controlling more than 600 watts of lights)(9 65 watt bulbs = 585 watts). Let me know how you make out. Hope that helps.
Oct 27, 2010 | Lutron 1000-Watt Incandescent Dimmer...
I bought a Lutron Dimmer Switch and there is a light on in the background when I turn the switch off. It is suppose to be that way. It seems to be hotter when the switch is off instead of hotter when the...
First off, if your dimmer is getting hot, then there is something wrong. This is dangerous. Do not leave that dimmer in the wall. Remove it.
1) A typical wall switch controls up to 1400 Watts. Look at the watt rating of your dimmer. A 600 watt dimmer will control up to 600 watts. If you have 600 watts on your dimmer, expect a shortened lifespan for that device. If you have more than 600 Watts, expect overheating and possible fire.
2) Lutron makes 1000 Watt dimmers
http://www.lutron.com/Service-Support/Technical/InstallationInstructions/Pages/InstallationInstructions.aspx?syst=Dimmers+%26+Switches&prodn=Maestro%C2%AE+dimmer+%26+switch
3) Type of bulb: Review the specs shown on link above because they show wattage, and they also show which light the dimmer is made to control
4) If your lights are on a 3-way switch, then dimmer has 3 screws and connects to 3 wires. If your wiring is incorrect, it might give symptoms shown above.
If your switch had 2 wires and you put those wires on a dimmer with 3 screws, it might be wired incorrectly.
Check wiring. Re-post a question if your are confused about details.
5) There might be a short in the circuit ... or in the dimmer ... replace dimmer with another one from Home Depot and see if symptoms persist. Disconnect ground wire as a test only and see if symptoms disappear ... if so then there is a short somewhere in the circuit
Don't burn the house down.
Oct 17, 2010 | Electrical Supplies
I just installed a chandelier. This is a new connection. So I ran a 3 wire from the chanderlier to a new lutron slide dimmer. I then ran a 2 wire from this dimmer to the switch. When I turned the...
Lutron Dimmer manuals
Lutron manuals show a couple things that might be affecting you lights.
1) Wattage: If you have wrong wattage dimmer
2) Type of light bulb: Dimmers work on different types of bulbs
3) Wiring: You say you got 3 wires going to the chandelier? Why you got 3 wires? Is this a 3 way switch? Are the chandelier bulbs wired separately so you can control groups of bulbs with different switches?
Does the dimmer have 3 screws? A dark-colored screw and 2 brass screws? If so, then that sounds like a 3-way dimmer. A 3-way, is where more than one switch controls the same light.
Does the dimmer have 2 screws? Then that dimmer controls a single circuit. Your black Hot wire from breaker box connects to one screw and the black wire to Load connects to other screw.
A quick glance at Lutron wiring manual shows that Hot and Load wires connect to either screw.
The question is your 3-wires from the chandelier ... does the black Hot wire from breaker arrive in the ceiling box first? Or does it arrive in the wall box first? If your Hot arrives in ceiling box, then the Hot must come down to the switch box and connect to a screw on the dimmer >>> a second wire connects to other screw on dimmer and travels up to the ceiling box where it connects to black wire on chandelier. The white wire on chandelier connects to white Neutral.
4) Dimmer might be bad
Oct 16, 2010 | Lutron #DVW-603PGH-WH 600W White Single...
Light switch feels hot
If the switch is rated at 600 watts and you have six 100 watt lamps connected to the switch, you are at the capacity of the switch and heating would be expected. It's general practice to not place loads on a device that will exceed 80% of the device's ratings, in this case 480 watts.
Some heating in a dimmer switch is not unusual, but if it's hot, it should be replaced with a device with a higher rating or the loads should be divided. You could also lower the wattage of the lamps (to around 75 watt each) unless you would lose too much light.
If the sockets in the fixtures can be lowered closer to the surface of the fixture, you can probably reduce the wattage since more light will exit the fixture. You will also save a few bucks with less wattage. Lastly, check the fixtures themselves and see if they are rated for the wattage of the lamps you have in them.
Apr 14, 2009 | Lutron 1000-Watt Incandescent Dimmer...
Lutron 1000-Watt Incandescent Dimmer Switch by  Electronics, Inc Logo
185 people viewed this question
Top Lutron Electrical Supplies Experts
Steve
jdthefixer
ken skalski
Are you a Lutron Electrical Supply Expert? Answer questions, earn points and help others