IT IS A CARRIER AC UNIT WITH ELECTRIC HEAT AND THE EVAPORATOR FAN RUNS ALL THE TIME THE ONLY WAY TO SHUT IT OFF IS TO TURN BREAKER OFF , I DISCONECTED THE GREEN FROM T-STAT AND IT KEPT RUNNING ANY IDEA'S WOULD BE HELPFUL tHANK YOU
  • 2,133 Answers
After switch off by remote, In your remote, there is an option " Blow" or "Air". Press it.
Posted on Jan 01, 2011
The fan motor is on all the time with the controls shut off. I have to shut the unit off with the main breaker. The ac works but again the fan never shuts off. On the circuit board the LED flashes 8 times,...
The indoor fan or the outdoor fan? If it is the indoor fan the thermostat may be wired incorrectly or shorted. If the red wire and green wire in your thermostat maintain contact, the indoor fan will run all the time.
Aug 03, 2011 | Heating & Cooling
AC Condenser motor will stop at 1pm but inside unit is still running but no AC. If I turn the AC unit breaker unit off and then an hour later turn it back on. The unit runs fine all day until 1pm. Had a...
Hi, the tech should have been able to figure the stat out with out a manual to see why the condenser is shutting off at 1:00 P.M. This is unusual for this to happen, unless it was winter and this is a heat-pump going into defrost, but just the fan would shut down. Does this unit have a box on it that was installed by your electric company that shuts the unit off during high peak conditions in the summer? This would cause it to shut down at the same time everyday. If not, it would have to be something in the thermostat that is set for it to shut off at that time. It still does not make since, as it would shut both the indoor and outdoor unit off, not just the condenser. Are you saying that just the condenser fan motor is shutting off, but the compressor continues to run until it shuts off on high head pressure when the fan stops, or does the complete outdoor unit shut down fan, compressor and all at that time??. It sounds to me like this outdoor unit has a time delay relay that has a fault in it may be shutting it off at this time daily? Please let me know if its just the condenser fan motor that shuts off, or if the complete unit is shutting off all together, this will help .
Sincerely,
Shastalaker7
A/C, Heating,
Sep 08, 2010 | Carrier 38CKC060 Air Conditioner
Ac unit clicks outside but nothing engages fan or compressor on unit furnace still runs for heat setting and fan still blows but ac will not engage just hear a clicking was running for three days this...
Have you check the outside breaker? If its ok then you got a problem in your electrical system inside the unit probably the contactor is not engaging this is where the 24 volts from the thermostat calls for the 240 volts to run the condenser fan and compressor. Be careful checking this out because of the high voltage.
Jul 09, 2010 | Carrier 38CKC048 Air Conditioner
Ac unit wont start
Sounds like a classic case of a burnt/pitted compressor contactor. The contacts can get pitted and sometimes burnt. This can cause them to stick and the unit will not shut off unless you shut off the circuit breaker. When you shut off the circuit breaker, the contacts would have cooled down which could have led to the problem you are now experiencing......will not come on. Open up the electrical box. Look near the bottom for a brown or black part with the wires from your circuit breaker wired directly to it. This is your contactor. In the center is the piece that moves up and down to allow the electricity to go to your compressor and fan motor when there is a call for cooling. Check to see if it looks burnt or otherwise damaged.
Apr 04, 2010 | Carrier 38CKC048 Air Conditioner
Carrier 38CKC042300. oUTSIDE UNIT FAN WAS TURNING REAL SLOW. ac UNIT IS OFF BUT FAN TO OUTSIDE UNIT IS STILL TURNING. sHOULD NOT BE TURNING AT ALL WITH AC UNIT OFF
The outside fan may run if the unit is in defrost mode this is normal for most heat pumps it is there way of trying to keep the outside unit from staying iced over so the next time the unit runs it will have air flow through the coil and the ice will not be there to prevent air flow.
Jan 12, 2010 | Carrier 38CKC042 Air Conditioner
AC fan stopped
Sounds just like a seized bearing on the fan motor. They can be repaired but it's usually less to purchase a new motor. Now all you have to do is figure out how to get the motor out. To get you started, you need to partially disassemble the top portion of the condenser cabinet. This will give you access to the fan motor assembly. Which model do you have? That information will be on the nameplate which is on the side where the electrical enters the cabinet. That reminds me, always pull disconnect and trip breaker before starting.
Jun 19, 2009 | Carrier 38CKC060 Air Conditioner
My Carrier AC fan will not turn, only blows out warm air.
Breaker has popped either at breaker box or at the safety shut off switch. Fuses are blown or the sending unit has popped.
Apr 30, 2009 | Carrier BCA101R Air Conditioner
No heat
Your compressor sounds like isn't working? And the problem is if we are lucky you just lost the capacitor. turn off the breaker to the ac/heat pump unit. Open the electrical panel on condenser locate the capacitor if it is swelled up like puffed up can then for sure it is bad. It has two sides to the capacitor one for the fan and one for the compressor. If you have a meter check it in ohms. If you don't have a meter take the capacitor to a heating and air conditioning parts house and get a new one just like the one you have very important to get right size. let me know how it turns out. ken
Dec 20, 2008 | Carrier 38BRC048 Air Conditioner
Carrier home ac system
sounds like your contactor is stuck closed.This is the part that high voltage connects to and lets power through to the compressor and condenser fan motor when you get a call for cooling.If you go to pull it out,kill the power outside AND at the furnace.
Aug 12, 2008 | Carrier Heating & Cooling
Heating & Cooling Logo
15 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen