I am replacing a 387.9246 Sears zone valve with a WR 1361-103 zone valve. A Sears tech told me to connect the thermostat to terminals 4 & 5; transformer to 1 & 2; and the hot water control to 2 & 3. He could not tell me which terminals to connect the red or white wires. He said ask the maker of the thermostat ! Can you help me with this problem ?
  • 2 more comments
  • donfrank99 Jan 03, 2011
    No, Your note was not helpful. The instructions you recommended were included in the package from Sears.
    My Question is what do I do with the existing red and white wires. Presently, there are wires (each containing a red and white component) hanging from the thermostat, furnace control and transformer.
    (1) From the thermostat, do I hook the red wire to terminal # 4 and the white to # 5 ?
    (2) From the transformer, do I hook the red to terminal #1 and the white to # 2 ?
    and (3) From the furnace control, do I connect the red wire to # 2 and the white to # 3 ?
    Or, does the color of the wire make a difference ?
    I'm afraid that I will short out the $200 zone valve if I connect the red wire to where the white wire should go.
    I hope this clarifies my questions.
    Don
    I forgot to add that the specs and instructions for Sears zone valve 387.9246 clearly noted what terminal the red wire should be hooked to and what terminal the white wire should be connected to. Check out the old specs, please.
    Don
  • donfrank99 Jan 05, 2011
    To: Heatman101....
    I am waiting for your reply.
    What do I do with the red and white wires ???
    Don Franklin
    I found your reply. I will make the connectons Wednesday am and report the results.
    Thanks for hanging with me.
    Don
  • 43,501 Answers
Not exactly sure what you are asking as the red and white wires would be t-stat wires which you said he wanted you to hook to 4&5....
Check this out...
http://www.emersonclimate.com/en-US/products/valves/Documents/0037-5421.pdf
It gives many wiring diagrams for many different situations....
One of these should fit your application...
heatman101
Posted on Dec 31, 2010
  • D. Floyd Kolb
    D. Floyd Kolb Jan 03, 2011
    Yes, that clarifies things....I was not following you at all....
    Here goes....the simple verision....terminals 1, 3 & 4 get the whites.....
    terminals 2 & 5 get the reds....
    So... the transformer is #2 red #1 white...
    The t-stat is #4 white and #5 red...
    The furnace control is #2 red and #3 white...
    What I often do is go to than auto parts store and buy an inline automotive type fuse holder...I use Autozone...
    I then install the fuse holder in the hot side of the transformer... the hot side will be marked with a "R" and the common side with a "C" The "R " side is the wire that will go to the #2 terminal....wire the fuse in that line to protect the transformer and the valve...install a 5 amp maximum fuse... a 3 amp is better... in that fuse holder....this way if you mess something up you will just blow the fuse and not the transformer or the valve...the valve motor should only pull .4 amp and the t-stat will pull even less...set the heat anticipator on the t-stat to .4 -.5 also...if it has one...
    Hope this gets you going... sorry about the confusion... it's tough to get a grip on exactly what is going on through the written communication sometimes...:-)
    heatman101
02 wr250 stator rotor came apart and shot a peice threw the case.shut down with kill switch. Replaced stator rotor Try to pull start, nothing but headlight shines bright any tests to suggest
Hi, Larry and the usual suspects are:
1. Fuel tank empty.
2. Fuel supply valve/petcock turned off.
3. Fouled spark plugs.
4. Engine flooded as a result of overuse of the enricher.
5. Vacuum hose to the fuel supply valve/petcock disconnected, broken, cracked, or pinched.
6. Fuel valve/petcock or filter clogged.
7. Discharged battery, check battery terminals for damage or corrosion, check the battery cables at "BOTH" ends for loose, corroded, or broken connectors, "INSIDE" and outside the cable harness, perform connector wiggle test and check cables with an ohmmeter if necessary.
8. Loose or corroded wire connection at the coil, battery or plug between ignition sensor and module.
9. Spark plug cables in bad condition and shorting, cable connections loose, or connected to the wrong cylinders.
10. Ignition timing incorrect due to a faulty ignition coil, ignition module or sensors (MAP, CMP, CKP, O2 and/or BAS).
11. Security alarm needs a reset.
For more information about your issue, please visit the websites below. Good luck and have a nice day.
Brand new wr250f won start WR YZ 250F
2001 WR250F Starting Problem Please Help WR YZ 250F
https://www.tradebit.com/filesharing.php/search/0/2002+yamaha+wr+250f
http://www.carlsalter.com/download.asp?p=1772
http://www.pdf-manual.com/vehicle/off-road-motorcycle/yamaha/manual-wr250f-2002-18159.html
Dec 28, 2015 | Motorcycles
How do I connect a 24v damper motor with 6 colored wires red white yellow green blue black to NO COM NC terminals.
Choose two colors of the thermostat wire, and connect them to the NO and COM and connect them to the zone control board leads for the zone intended. Almost all zone valves spring return open when deenergized. So ensure the zone valve is open with the system is off. At the base of zone valve there is a set screw that needs to engage the damper valve shaft in the open position with the motor in the spring release position. Most zone valve are 90 degree moment from full open to full shut. If you have a Carrier zone valve, they go full open to full shut in 45 degrees of motion. Your open stop need to be set so the valve stops in the full stop position.
To help understand the operation of a zone system, say you have 2 zone system and zone 1 thermostat initiates a heat or cool demand. Zone 2 valves energizes and shuts and zone 1 stays open and allow air to heat/ cool zone 1. If zone 2 thermostat simultaniously initiates the same heat/cool demand, the zone 2 valve opens and both zone heat/cool. When either thermostat is satisfied the opposite zone valve closes and when both thermostat are satisfied both zone valves open.
Hope this helps you understand zone operation. The same works for higher multizone systems.
Jul 27, 2014 | Honeywell Motorized Small Rectangular Hvac...
Connecting 2 wire thermostats to white-rogers type 1311 3 wire zone valves
Thank you for your interest with Emerson White Rodgers. My Name is Joselito Laxamana from technical department. Make sure to connect a thermostat that will power open and powered closed the zone valve. I pretty sure that the two wire thermostat that your going to connect will not be compatible. To better assist you with this further contact us directly at 18002842925.
Oct 15, 2012 | Heating & Cooling
I just purchased a house with brand new furnace wired to a RTH2300 Honeywell thermostat. It only has two wires running to it. I can't seem to get it to work in "manual mode"-where I set it on...
?? Connect Wires 5.
Labels don't match?
If a wire does not match any terminal on the thermostat,
see next page.
Quick Installation Guide
6
Alternate Wiring
If a labeled wire does not match any terminal
designation, see diagram below.
Do not use C, C1 or X wire. Do not use B wire if you already
have O wire. Wrap bare end of wire with electrical tape.
This thermostat cannot be used if your old thermostat had
any two of the following wires: R, RC, RH, 4 and V.
Place a jumper (piece of wire) between Y and W if you have
a heat pump without auxiliary/back-up heat.
?? Connect Wires (cont'd)
Programmable Thermostat RTH2300
7
Set jumper JP1, on the back of the thermostat, if you
have connected a wire to the G terminal.
Incorrect jumper setting: An incorrect setting is
noticeable in a gas or oil heating system. When heating
starts, you will initially feel cold air coming out of the vents
as the fan is running before the furnace has enough time
to heat up the air.
?? Set Heating Fan Control 6.
HG Leave the jumper in this factory-set
position if you have a gas or oil furnace.
HE Place the jumper to this position if you
have an electric furnace.
JP1
8
Set jumper JP2, on the back of the thermostat, if you
have a heat pump.
Incorrect jumper setting: The heat pump operation
will be reversed, i.e., it will cool in Heat mode and will
heat in Cool mode.
?? Set Heat Pump Reversing Valve 7.
O Leave the jumper in this factory-set
position if you have connected O wire to
the O/B terminal.
B Place the jumper to this position if you
have connected B wire to the O/B terminal.
JP2
9
1) Install 2 AAA
batteries on the
back of the
thermostat.
2) Align the two
brackets on the
top of the
thermostat with
the corresponding
slots on the top of
the wallplate.
3) Push the
thermostat
against the
wallplate.
4) Tighten the screw
at the bottom of
the thermostat.
5) Turn power back
on at the heating/
cooling system.
Nov 27, 2010 | Honeywell Programmable Thermostat Heater
Dryer will only blow cold air
always use caution around electrical appliances
electric dryer-runs but will not heat
1.loose wiring--check terminals & wiring
2.defective thermostat--replace
3.defective centrifugal switch in motor--replace switch--check linkage in motor
4.defective timer--replace
5.open heater element--replace
gas dryer
1.faulty ignition or reset valve or thermocouple
2.thermostat
Jul 31, 2010 | Samsung Dryers
Replacing WHITE-RODGERS manual thermostat with 3 wires ( red, white, blue and installing Honeywell electronic thermostat RTH110B, how do I connect it? The heating is not central, baseboard heating.
I have only seen one Honeywell thermostat that would work with a 3-wire heating system.
I would replace it with a White-Rodgers 1F80-0471. They are about $100, but they are a good thermostat, and they work well with the 3-wire zone valves.
Most other thermostats have the "Y" terminal that you need, but do not control the zone valve correctly.
Helping Hands Services
- Fairbanks, Alaska -
Jan 30, 2010 | Honeywell Electronic Programmable...
I'm replacing my old thermostat with a honeywell
usually you should have 4 or 5 wires....if you have AC then this wire should be Y if not was it connected at all before?...Heating requires only R&W
Oct 24, 2009 | Honeywell Electronic Programmable...
How do i install a zone valve in my hot water heater. I need the schematic from boiler controller to the valve. if I tie the first floor to one valve , the rooms (2) will be on the last section before the...
The two zones have seperate supply and returns, correct? If not zoning will not be possible without piping the system in that way. Assuming the piping is correct, for two zones, you will need two zone valves, one cut into each zone. The wiring will vary, but for a 3 wire zone valve, (Taco), power from the transfomer goes through the thermostat, into terminal 1 on the Zone Valve, Terminal 2 on the zone valve goes back to the transformer, (24v common), and also to one "T" terminal on the aquastat (boiler control), and Terminal 3 on the zone valve goes to the other "T" terminal on the aquastat.
For a Honeywell, or other motorized Zone Valve, power again goes from the transformer, through the thermostat and into one side of the motor contacts/wires (depending on brand), the other motor wire goes back to the transformer, (24v common) Then the two end switch contact/wires go back to the T T terminals on the aquastat.
If you are using motorized zone valves, and only 2 of them, the transformer in the aquastat will be strong enough to power them.
Hope this helps
Jul 04, 2009 | Kenmore 75944 Gas Dryer
A duo therm thermostat (p/n 3105058) was removed because it would not operate the air conditioner/heater in a firan fireside camper. it was knocked loose from the wall damaging it.the thermostat is for use...
a. Remove the cover of the thermostat.
b. Connect the RED wire from the air conditioner
to the “RC” terminal on the thermostat.
c. Connect the “YELLOW” wire from the air conditioner
to the “Y” terminal on the thermostat.
d. Connect the “BLUE” wire from the air conditioner
to the “H” terminal on the thermostat.
e. Connect the “ORANGE” wire from the air conditioner
to the “G” terminal on the thermostat.
f. Push the thermostat wires into hole in wall and
fill excess hole with insulation.
g. Mount thermostat base to the wall with screws
provided.
h. Check all thermostat wires on base to ensure
they are completely clear of the bimetal coil of
the thermostat. Adjust if necessary.
i. Replace thermostat cover.
If nothing operates on the air conditioner, remove the
return air grille assembly and verify the red, orange, yellow
and blue wires are properly connected (red-to-red,
orange-to-orange, etc.).
Next, disconnect the red wires and check for 12 volt
DC between the red wire from roof section and the orange
or blue wire from roof section. If no voltage received,
refer to Section F2. If voltage is received, the
problem lies with the thermostat or thermostat wires.
Next, disconnect all 4 wires (red, orange, yellow and
blue) from the thermostat. With the thermostat set on
COOL mode, FAN mode set on AUTO and HIGH, and
temperature selector set lower than the room temperature. Check for continuity between terminal RC (red wire)
and terminal G (orange wire); and RC (red wire) and
terminal H (blue wire). If continuity is achieved on each,
proceed with the next step.
Set fan switch to LOW. Continuity should NOT be present
between terminal RC and Terminal H, but present between
the other terminals (Y & G) and terminal RC.
If all of the previous checks are good, the thermostat is
good, do not replace it. If any one of the previous checks
are not correct, replace the thermostat.
Jun 15, 2009 | Dometic Rooftop RV Air Conditioner
Kenmore Dryer will not heat
Does the limit switch have a reset button on it or is it an auto reset? Have you tried depressing the reset button on it if it is a manual reset? Have you checked your voltages to the gas valve, ignitor to make sure they are being called to come on? Trace your electrical connections from your electronics to these items. If they are not being told to come on, then you know it is the electronics. Also, have you checked the continuity of the door switch, and the ignite? These are all suggestions that must be ruled out before replacing parts.
Apr 18, 2009 | Kenmore 63942 Dryer