I had a power outage while I was gone.Now heater does no work. I have a rheem cooling and heating unit/ Fan runs but heat does not come on. It seems pilot may be out. Is there a fuse or reset button?
    Genius:
  • 1,015 Answers
The first thing I would do is relite the pilot and make sure it looks good.You may look for a flame roll out switch usually above burners.It will be a small round red button .see if you can push it in and get it to hold. If so you may have solved your problem. Good luck and thank you.
Posted on Dec 30, 2010
Heat Pump Blowing Cold
Unless you just installed or had the thermostat installed recently, I would not point at the thermostat as the problem. With what you have described I would suggest have your units serviced as it sounds like a loss of charge, or failed defrost control board. The "Aux" comes on when the unit is using secondary heating (electric heat strips). That occurs when the demand temperature (what you set it to) in Heat mode is more than the current room temperature, usually ~2-4 degrees higher. Also happens in defrost mode. Defrost is a heat pump cycle that melts any build up of ice on the condenser unit (outside unit). That process is simply the unit running in cool mode which will heat up the outside unit to melt any ice. Defrost cycles vary with manufacture but usually you can tell if is in defrost by looking at the outside unit, during defrost the unit will be warm or hot sometimes there is steam and the compressor will be running but not the fan. Defrost only happens on heat pumps in "Heat" mode. Rheem has a 10 yr compressor and parts warranty, so call the installer or Rheem authorized service company.
Nov 11, 2013 | Honeywell RTH7600D Touchscreen 7-Day...
Replaced Thermostat and now Blower Motor will not run
Sounds like a set up issue on the tstat. You say this is a packaged unit, inside the machine you should find where the tstat wires hook up. Typically red is power yellow is compressor orange is reversing valve white is emergency heat green is blower. Put red and green together, test blower. Then red green and yellow, make sure blower works again. If blower runs both ways it's either the tstat wire or tstat itself. Make sure you are landing wires on dedicated heat pump terminals, make sure in settings you are set up for heat pump with back up electric heat and TSTAT CONTROLS THE FAN. Good Luck. Also if there is a switch on the tstat for gas or electric on the back you want electric.
May 12, 2017 | Heating & Cooling
Rheem digital gas pool heater fan code
The Fan code would indicate a problem with the combustion air blower. The is a pressure switch to indicate there is sufficent combustion air, and if not then unit shuts down. Either the fan isn't running, or there is an obsturction in the fan or exhaust piping, preventing enough air flow.
cfh would be call for heat, which would be a normal display when water temp is below setpoint
See the link below for a manual. Once you open the page look on lower right side for documents, then install manual
http://www.rheem.com/product.aspx?id=2388EEB7-3DEC-4601-AE76-EC7A07F17630
Jul 04, 2010 | Solar Rheem Gas Fired Pool & Spa Heater...
Indoor fan blowing cold air when on heating
The indoor fan will continue to run. When heat pump goes into defrost the outdoor fan stops, the reversing valve switches and the unit is basically working in the cooling mode. In order for you not to feel a blast of cold air in the winter the electric strip heat also comes on so the indoor fan must run while the strip heaters are on.
Jun 03, 2010 | Heating & Cooling
Heat PumP: Rheem Two Stage Heat, One Stage Cool Thermostat Replac
R = R with jumper to RC hot side of transformer
B = Reversing valve
Y = Compressor relay
G =Blower
C = common on transformer (X on old t'stat)
W2 = Auxillary heat
E = Emergency heat
Mar 04, 2010 | Heating & Cooling
1970's Rheem electric furnace
no the older rheems had a sequencer for the heat that turned on the blower at the same time that the heat strios are energized. so the first thing that you need to do is figure out the sequencer that is keeping the fan running and get it replaced.
Jan 30, 2009 | Honeywell CT3200 5-2 Day Electronic...
Fan runs indefinitely after heat shuts off
yes I have replaced a couple of t-stats lately (honeywell)
Jan 05, 2009 | Honeywell Programmable Thermostat Heater
T8000C Honeywell - fuses???
So the indoor fan is running and blowing air inside but it is not cold?? Is the outdoor fan running ?