Question about Guardian Electrical Supplies
My 15 kW Generac Guardian -- 04390-0 (15kW LP) will not auto transfer with power loss. It will transfer only if I take the panel cover off and manually switch the lever down on the part no. 0C2237 (transfer switch home standby 100A2P250V) John - (snowed in, in north GA)
  • John Jancuski Jan 02, 2011
    mrfixit-jerr, Thanks for the info. I have the original manual, but it doesn't have the detail the one you sent has. I had to depart my mountain home last Thursday after being snowed in on top of my mountain and will return Monday and check out the trouble shooting procedures. I have had my unit since 2001 and aside a cracked block in the engine during the first month (replaced under warranty) and a starter gone bad after about five years (I had to pay for that one- about $300 for the part and mostly labor), I have been very happy with the generator. Is there any one part that you would think I could order and replace that might solve the auto transfer problem? Sorry for the delay in my reply.
    Thanks, John
CarlGehrke
  • 169 Answers
SOURCE: Generac Guardian 15kW Generator
That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.
You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.
Regards,
Carl
Posted on Jan 26, 2009
CarlGehrke
  • 169 Answers
SOURCE: Gen. set won't auto start.
This sounds a little like a bad wiring problem between the transfer switch and the generator. But before I leap to any unfounded conclusions let's make sure I understand just which Guardian generator and transfer switch you have. The generator I think you have is an air conditioner sized box that has a 2 cyl air cooled Generac GT990 engine in it. The control panel has a 15 amp fuse, and maybe a 7 amp one, some LED indicators, a 3 position rocker switch (manual,off,auto), and a momentary set exercise switch. If you look inside your transfer switch there is the transfer mechanism, a single relay, either 2 or 4 fuses, and a terminal board where 4 small control wires connect to the generator. The control wires will be labeled N1, N2, 193, and 23.
If all of that is true then I'll also assume that the generator is blinking all of the LEDs and as soon as you put the rocker switch in the manual position the generator starts and the transfer switch moves to the "generator" position. It shouldn't do that, manual means switch the switch manually too. :-)
Let's take care of the exercise setting first. Switch the main output breaker of the generator to the "off" position, this prevents the transfer switch from activating even if the generator runs. Next put the generators rocker switch into the "Auto" position and wait at least 1 minute, if the generator starts we have to fix the wiring between the N1 and N2 terminals in the transfer switch and the matching terminals in the generator before we can proceede. If luck was with us and the generator is just blinking its LEDs at you, press and hold the set exercise switch for 30 seconds, you're reseting a "watchdog" type circut so it has to be for the whole 30 seconds. When you let go of the set exercise switch the LEDs should blink another 10 times or so, then the generator should start and run its exercise for 12 minutes more or less and then it'll shut down. At that time the only LED that should be lit is the green "system ready" one and it should be steadily lit. Remember to close the output breaker again.
Next let's address the transfer switch issue. If I've understood you correctly, the transfer switch moves anytime you turn the generator on. The only reason a regular old RTS type transfer switch could do this is that it's being commanded to transfer. It works like this, the 2 coils that move the transfer mechanism get powered by the source we're trying to switch to, once the switch gets into the position it's going a pair of limit switches disconnect it from the power supply so that the coil is only "live" during a transition. Spring loaded contacts hold the switch in either position once it's more than halfway towards either one. The relay inside the box is also in line with the limit switches so that if the relay is deenergised the switch will try to get to the utility position and stay there, it can't if there is no utility power to drive the transfer coil. On the other hand if the relay is energised, the switch will try to get to the generator position and stay there, if there is no power from the generator it can't because the generator is what drives that bottom transfer coil. So I think that for whatever reason the relay in your transfer switch is staying energized when we don't want it to be.
On the terminal board inside the transfer switch you should see terminals labeled 194 and 23, these are the power to the relay coil (194), and the ground to transfer signal (23). With the generator set to off, and a fairly quiet room, disconnect the wire from terminal 23, if you can hear the relay coil click on and off when you touch the wire to terminal 23 there is something wrong with the wiring at the generator end of things. You should also see 12 volts DC between terminal 194 and ground, this comes from the generator too.
If the relay didn't click back and forth above check it by using a short piece of wire to connect terminal 23 to ground, if the relay isn't energised when terminal 23 is grounded and deenergized when terminal 23 is open you either have a bad relay or a problem in the grounding of your system. To get a bad relay fixed for free call up Guardian, register the generator (you'll need proof of purchase), and get them to tell you where your nearest warrenty service person is. If you tell him about this post he'll bring a relay with him when he comes to you.
If you're satisfied that the relay in the switch is working properly, we're on the trail of a wiring problem at the generator end of things. If the generator has just been installed you should carefully check that wire 23 hasn't been connected to terminal 0 at the generator terminal block. It's easy to get this connection wrong when doing th e install. The other thing that can go wrong is that the wire can get pinched inside the conduit and short to ground. To check this disconnect both ends of wire 23 and measure between either one and ground, you should get nearly infinite resistance.
If you've proved to yourself that all of the wiring is correct, and the generator is properly grounded, you probably have a broken control board in the generator. To get the control board replaced use the same procedure as the relay above.
If that doesn't get this resolved for you post a comment and we'll try a different approach.
Regards,
Carl
Posted on Mar 06, 2009
  • 384 Answers
SOURCE: 10kw Generac Guardian not cranking, shows rpm sense loss
Sounds like Generator mode switch should be "ON".
Posted on Sep 08, 2009
SOURCE: When utility power goes out, the transfer switch doesn't transfer
Call an electrician.
Posted on Jan 23, 2010
  • 3 Answers
SOURCE: I have a 10 KW Generac Guardian Stand By withe a
Hi, I have a 10kw Generac Generator and I went out to check on it to see that all was working and saw the display panel blank. The generator wont turn over. This was installed 3mos ago and all was fine. It has an automatic transfer switch in the main panel. I tested to see if the gen was getting power from the 2p 15amp breaker and showed power to gen. I think it might be the battery charging system were can I find this?
Posted on Feb 27, 2011
Generac power management module install
Mount the transformer on the generator. Hard wire it into a 120 vac plug. Run wires to the module and connect to the coil on the relay. Now run the load you want to disconnect while the generator is running to the load terminals of the relay in the module.
Sep 10, 2016 | Generac GUARDIAN Air-Cooled Automatic...
Generator hard to start and sputters like its missing
About 15,000 results (0.73 seconds) Search Results
    2 - Generac : Questions, Answers, How To, FAQs, Tips ...
    answers.generac.com/answers/1506-en_us/searchquestions.htm?...
    Can I run an 8kw standby generator on a 100 lb propane tank? 2 answers ... What am I getting for the extra cost of the Guardian unit? ... The engine starts hard and runs rough. 1. Air ... On auto start, unit sputters and I smell gas. ... Does the gas and electrical feed into the unit from the back as previous air cooled units?
    2 - Generac Questions and Answers
    answers.generac.com/answers/1506.../generac.../questions.htm?...
    On auto start, unit sputters and I smell gas. .... The 20kW automatic standby generator has the option to delay start up during an ... This is for a guardian 20kw. ....has been designed to make the battery installation and removal so difficult? ... The air cooled generators are designed to allow for the smallest footprint while still ...
    3 - Generac Questions and Answers
    Generac's Guardian Series 17kw automatic standby generator does not come with a.... The automatic response features of our air-cooled units initiates the unit's startup,.... This week I tried the same and it tries to start but just sputters and fails until .... A C delayed start still chocks 17kw generator would a hard start kit help?
    On auto start, unit sputters and I smell gas. On manual start ...
Feb 08, 2016 | Generac Guardian Air-Cooled Standby...
Why does it crank and almost start on 1st try?
Generac Generator Troubleshooting - YouTube
? 1:39
https://www.youtube.com/watch?v=AKN2dc59cxY
Dec 20, 2013 - Uploaded by Appliance Princess
I want to learn about Generac generator troubleshooting. ... I have a 16 kW propane fueled standby air-cooled generator. ... I have a brand new generac 20K guardian Evolution and the first time my power went out my generac ...
Generac Power Systems - ConsumerAffairs.com
www.consumeraffairs.com > Homeowners > Utilities
Rating: 1.3 - ‎26 votes
Hey, Generac, make a change and start making generators that work, don't cost .....Standby generators are not supposed to be used as a primary power source ... and three months ago, I spent $4,000 to have a Guardian generator installed at ...
Generac standby generator - Propane - wont start?? - DoItYourself ...
www.doityourself.com/.../487838-generac-standby-generator-propane-w...
Feb 4, 2013 - I have a Generac 4LM41A standby generator that I need help introubleshooting and repairing. It is about 12 years old and hasn't been used ...
141 GENERAC complaints and reviews @ P'ed Consumer
Dec 12, 2015 | Generac GUARDIAN Standby Generator 10 kW/9...
Coil smoked on start up
THIS SOUNDS LIKE OIL IS LAYING ON TOP OF THE PISTON.
Apr 08, 2013 | Generac Guardian 200 Amp Transfer Switch...
Just finished installing a 20 KW Generac generator (fueled with natural gas). The included transfer switch will not automatically transfer to the generator, but transfers back to the utility without...
Check the connections on the tranfer relay and two coils. The two coils have blue wires. I have seen them come off from assembly or shipping its common. Each coil has two blue wires #8 and E1 with crimp steak ons and limit switches make sure there all pushed on all the way. Hope this helps
Mar 09, 2011 | Generac Guardian RTSE200A3 200 Amp...
I have a 10 KW Generac Guardian Stand By withe a prwired EZ transfer swithc. Everything works except the 12 volts battery charger. What could be the problem. Only have three weeks innstalled.
Your generator is equipped with a battery trickle
charger that is active when your unit is set up for
automatic operation. The trickle charger is
designed to help extend the life of your battery by
maintaining the battery when the unit is
not running.
you will need to review which circuit bord controls this and have that board replaced or serviced some of these gen heads have this built in and it will be the rectifier in the gen it self it will be a black 1x1x3/8 inch with a mounting hole in the center and 4 lug post for the wires replace this and your issue should be solved but consult your dealer for witch unit you have as to a control board external or the built in rectifier hope this helps.
Aug 11, 2010 | Generac Guardian Series 5502 10 kW...
Generac Guardian 15 kw overspeed fault
Did you remember to set the overspeed shutdown threshold on the control board?
Apr 03, 2009 | Generac 13,000 Watt / 13,000 Watt Home...
Electrical Supplies Logo
240 people viewed this question
Top Guardian Electrical Supplies Experts
Matt Olenzek
Matt Olenzek
richie46
Are you a Guardian Electrical Supply Expert? Answer questions, earn points and help others