Question about Carrier Heating & Cooling
I Have A carrier Model #38YCB048300 heat pump/a/c unit which is only used for a/c, The Pump is not coming on with the inside main fan.I have basic knowledge with a/c I have been in auto repair for 30 years, any hep would be appreciated Thanks Barry
  • 182 Answers
SOURCE: Ruud Heat Pump
this may indicate you have low voltage but no high voltage.check fuses and breakers.
Posted on Aug 09, 2008
vanni7
  • 163 Answers
SOURCE: 3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Posted on Jan 04, 2009
  • 1214 Answers
SOURCE: rheem heat pump. blower will not turn off
The fans are set to delay for 60-90 seconds to remove all heat from the heat exchanger/heater elements.
If the fan runs any longer than 3-4 minutes after the Emergency Heat shuts off, you may have a bad sequencing relay in the air handler.
Posted on Jan 27, 2009
mastatech
  • 478 Answers
SOURCE: Heat pump cycling on and off.
It sounds as if you you have a low charge of refrigerant, r22. When the unit comes on outside, the outdoor coils become the lowside, there is a low pressure switch that is tripping out contactor protecting the compressor.
Posted on Mar 11, 2009
farfield
  • 462 Answers
SOURCE: CARRIER AIR CONDITIONER/HEAT PUMP PROBLEM WOULD
what I have always been told is if your 24 volt side burns out check the high volt side if the hi volt side burns out check the low volt side.
A quick way if the primary side is burningout due to a problem with the low volt side:
1 MArk all the thermostat wires at the indoor unit
2 Disconnect them at the indoor unit.
3 Check main line voltage before proceeding (A 208 volt is not considered 220V and 240v Is not considered 208V> In these circumstances the voltage may have changed with the power company replacing a transformer and now you need to change the main power input lines at your control transformer for the correct operating voltage). If okj then proceed:
4 If you have an amp meter attach it to one of the lines going to the transformer.
5 Apply main power and listen for hum, note if smell starts again and if so problem has to be in board or main incoming voltage too high or too low. Amp draw should be less than 3 amps.
6 If your to this point and still havent found any trouble in the above as of yet, Connect the wire marked "C" together. Then just touch the thermostat wires one at a time to the places where they go on the indoor unit and watch the amp meter. If you donmt see the meter jump the circut is probably ok but leave them disconnected until you touch all of them to the correct place or wire. Here is a possible problem I ahve seen a thermostat wireing problem if the wires are stripped too far and a "whisker" of the wire sticks out and allowes one of the other wires to cross short out. In this case just cut off the excess wire or bend it over out of the way asnd continue with the test. You can always cut it off later after the tests. If you see the meter jump up and stay up and /or blowes the fuse the wire that you used and it blew is where to consentrate.
7 No wiring problem found means that you could have a relay or contactor not pulling in properly.
and this will cause the amp draw to go way over the transformers power out put or VA rating.
8 Inspect the thermostat wiring for the "whisker" I mentioned above.
9 If you have done this to the end of the thermostat wires and your main incomming voltage is correctly wired in on the transformer andf your relays and contactors are pulling in evenly and not delaying excessively your problem should be fixed.
If this helps you please rate me as high as you can and thank you for using fixya.
Posted on Apr 25, 2009
Fan doesn't work in heat mode it works on all other functions. Heat does come out but fan doesn't kick in. Outside unit is operating
AC inside fan doesn't come on AUTO - DoItYourself.com Community Forums
www.doityourself.com > ... > Air Conditioning and Cooling Systems
Jul 21, 2004 - The inside FAN doesn't run when in AUTO mode. If I leave ... Is the thermostat not working correctly or something in the AC unit causing it to do this? Thanx ... The unit is electric central air-conditioning(heat and cool). It made ... Carrier A/C condenser fan not working
Jul 27, 2012
Heater Fan Doesn't Work on AUTO
Jan 23, 2006
Blower doesn't work in ON position after repair
Mar 25, 2005
Central AC/Heat, Blower Doesn't work on Auto
Nov 30, 2004
More results from www.doityourself.com
Nov 01, 2015 | Heating & Cooling
Condenser fan on heat pump does not turn off
If it is just the condenser fan that means you have a fan relay that has welded shut. Turn power off to your unit and trace the wires from your condenser fan back into the control panel at the unit. You'll have 3 wires going to it. 2 go to the run capacitor and one goes to the fan relay. The one that goes to the fan relay is the part that needs to be replaced. If you have no fan relay and it goes to the main contractor, half of your main contractor is welded shut and will need to be replaced.
Sep 18, 2014 | Carrier 52PQ-515---3 Premier Series Heat...
Carrier OEM to Honeywell Programmable Tstat - NEED HELP
you likely have a "two stage" system, but not a two stage heat pump. the first stage is probably the heat pump itself, and the second stage is the auxilliary resistance heat that suppliments the heat pump at lower temps. if i knew the terminals that are available on the new stat, i could advise you on the proper wiring.
Jan 27, 2013 | Carrier Heating & Cooling
Carrier heat pump (basic model) runs at 0 or below
A basic model heat pump with an air handler with electric strip heat generally will continue to run with a call for heat regardless of the outdoor air temperature unless there was an outdoor thermostat (an accessory) installed. There is still heat in the outdoor even at temperatures of zero and below. Generally, there is a balance point of approx 30-35degF that allows the heat pump to heat your house to 68degF without the need for the electric heaters. Below that, the heat pump can still extract heat from outside and "pump" it into your house; however, it will need help from the electric heaters. In temperatures below the balance point, the heat pump will run non-stop. As the temperature in the house falls approx 1 - 2 degF below the setpoint, the electric heaters will energize. So it is not uncommon for the system to run non-stop with the temperature falling a few degrees below setpoint. The colder the outside temperature, the more often the strip heaters will cycle on/off. If your system is well-maintained and operating at proper performance, it is still cheaper to run your heat pump than it is to run on straight electric heat. If you live in a climate where below zero temperatures are normal during the winter months, you might want to research heat pump options that offer higher COP's and increased performance in colder temperature than the basic contractor's model. Start with initiating communication with a local contractor. You will need to consider initial cost and the pay-back period based on your local energy costs and your specific demands you want your system to meet.
Hope this helps!
Feb 14, 2010 | Carrier 38CKC036 Air Conditioner
Carrier 38CKC042300. oUTSIDE UNIT FAN WAS TURNING REAL SLOW. ac UNIT IS OFF BUT FAN TO OUTSIDE UNIT IS STILL TURNING. sHOULD NOT BE TURNING AT ALL WITH AC UNIT OFF
The outside fan may run if the unit is in defrost mode this is normal for most heat pumps it is there way of trying to keep the outside unit from staying iced over so the next time the unit runs it will have air flow through the coil and the ice will not be there to prevent air flow.
Jan 12, 2010 | Carrier 38CKC042 Air Conditioner
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
My Carrier model 38YKC060 heat pump unit fan does not come on and icicles are forming around the bottom. What do I need to do?
You must be having some very cold weather. Heat pumps shut the fan off when the temp. of the coils on the outside hit a certain temperature. That is to increase the pressure inside the unit to get more heat out of it. Your unit also goes into a defrost when ever it gets that cold also. But the compressor turns off also.
Now if your fan never comes on need to check the motor with a ohm meter. And check the capacitor it is a dual one meaning fan and compressor. One side can be out so need to check that also. Turn power off to the outside unit just pull the safety disconnect on the side of the house. Take the capacitor out ohm out the C side and the fan side. You will notice the Herm side meaning compressor. My guess is motor is bad. But I'm not there so concentrate your efforts there. Let me know how it goes okay. Ken
Dec 21, 2008 | Heating & Cooling
No heat
Your compressor sounds like isn't working? And the problem is if we are lucky you just lost the capacitor. turn off the breaker to the ac/heat pump unit. Open the electrical panel on condenser locate the capacitor if it is swelled up like puffed up can then for sure it is bad. It has two sides to the capacitor one for the fan and one for the compressor. If you have a meter check it in ohms. If you don't have a meter take the capacitor to a heating and air conditioning parts house and get a new one just like the one you have very important to get right size. let me know how it turns out. ken
Dec 20, 2008 | Carrier 38BRC048 Air Conditioner
Hi- Can not tell if my unites are straight cool / heat or a heat pump.
if you look inside the condenser unit outside,see if you see the big reversing valve,if not it is a straight cool,heat, the heat strip ins in the air handler so you would have to take the side panel off and look for the heat stripe,my the way heat pumps also have a aux.heat stripe just in case it does not get cold enough outside,hope this helps you-mike
Oct 25, 2008 | Carrier 38CKC042 Air Conditioner
Heating & Cooling Logo
95 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others