Dayton Propane Gas Furnace Fault Code 7 - Ignition Lockout Due to Retries. The Power vent comes on, the ignitor turns bright orange, the gas valve opens, gas comes out and very nice blue flames appear. There is a click, the gas shuts off, then the cycle starts over again. After 3 cycles the fault led blinks 7 time. The flame sensor has been cleaned and replaced. I have paid service techs to come out and they can't figure it out. They have not replaced the board and said they can't get an exact replacement, the one they received was universal and confusing to them. They said they were not sure if that was the issue so they didn't want to install it if they didn't have to. Sincerely, Cold In Minnesota!

1 Answer

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Genius:

An expert who has answered 1,000 questions.

  • Master 1,015 Answers
  • Posted on Dec 22, 2010
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Genius:

An expert who has answered 1,000 questions.

Joined: Nov 02, 2010
Answers
1015
Questions
0
Helped
319887
Points
3041

Dear cold, I can identify with your problem. It sounds to me like you have done everything that I would suggest except change the control board. I would recommend that you contact Grainger supply at www/grainger.com with your furnace model no and part number if possible. I ordered a lot of parts from them when I was running my business. We are in central Ks. so I could get parts out of Wichita in a couple of days.
They can give you nearest location to you and I was always pleased with everything I got from them but the bill. They have a wide selection of dayton furnaces and parts and knowledgeable sales staff. I hope this helps you and thanks. Happy holidays.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

My Carrier WeatherMaker 8000 furnace is blinking a red light 2 times pauses then blinks red 4 times with a pause between the 4 times

They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST

DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS

11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Low inlet gas pressure
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiatingstatus code recall. After one status code recall is completed component test will occur.

here is a link copy and paste

https://www.fixya.com/support/t6287232-carrier_8000ts


.
0helpful
1answer

Error code= two red flashes, lockout/ no flame

Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...

www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com

7 Tips and Tricks to repair your Furnace DIY - YouTube

? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
0helpful
1answer

Ignition lock out due to retries

Disconnect the power source and it will clear the lock out when plugged back in.
0helpful
1answer

Amana Air Command 90 furnace LED light blinks 3 times pause 3 times

TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.

2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.

3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.

4 BLINKS Open limit switch Verify continuity through rollout switch circuit.

5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.

6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.

8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.

9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.

10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.

12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
0helpful
1answer

This is a Dayton gas furnace model GF9S120D20UP11H and i am getting a flash code of ignition lockout due to recycles. how do i fix it? i have taken all the filters out and washed them and also checked...

Usually a lockout code means it tryed so many times and then it locks out or stops. First, when a furnace is locked out you have to kill the power to the furnace to reset the lockout. I don't know this furnace but there are manual resets around the burner called flame rollout switches that have buttons in the middle that have to be pushed back in. Also the power vent has to come on when the furnace gets the signal from the thermostat. This is proven by a flow switch with a rubber hose on it. The next step is a 30 sec. purge, then the igniter glows or sparks and then the main burner comes on.
The other switches are hi limit on the front wall of the heat exchanger. That might get you started. If you have anymore questions [email protected]
0helpful
3answers

Fault code says pressure switch lockout

This more often than not, indicates that your pressure switch is gone and needs to be replaced. Watch the YouTube video for a fuller explanation and heed the warning to use OEM parts! Gas Furnace Pressure Switch Failure and Replacement Amazon com gas furnace parts
0helpful
1answer

We have a dayton gas furnace model #3E463A. thought the control box was gone. got new one we furnace starts up the power goes on, fan starts no green pulsing light on control no ignition

When your furnace starts...the Ventor motor(exhaust fan) starts up....within a short time (seconds) the Pressure switch closes proving that the Fan is indeed running and the vent is not blocked...if this doesnt happen the furnace will not poweer the ignitor or fire at all....Check the vent pipe outside and look for obstructions or dirt on the screen inside the pipe...the condensate from the fuirnace may not be draining at all...due to plugged condensate drain lines...find this tube coming out of the furnace front...bottom of upper compartment usually , and pull it off the tap....if water starts coming out then your drain is plugged downstream of the furnace.
0helpful
1answer

Fault Code on Dayton Gas Furnace

This happens when the furnaces tries to light to many times and doesnt succeed. If you stand in front of the furnace while it is coming on, you will be able to hear the problem. If its an electronic start, there will be a clicking sound, followed by the gas valve opening to start it. If it has a pilot light, make sure it is lit, then listen for the gas to come out, it will make a hissing sound. If no gas is coming out, first double check to see if the gas is turned on to the unit, if it is, then its possibly the gas valve. Oh, if it is electronic, and you hear gas, but dont see a glow inside the furnace, or no glow or gas, it could be the ignite. Hope this helps.
Not finding what you are looking for?

190 views

Ask a Question

Usually answered in minutes!

Top Dayton Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Brad Brown

Level 3 Expert

19187 Answers

ZJ Limited
ZJ Limited

Level 3 Expert

17989 Answers

Are you a Dayton Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...