Question about LG Heating & Cooling
A c unit goes into defrost too soon then it will possibly go out of defrost and hiss loudly current draw rises over 20 amps trips breaker model is a L G L 12463hl 7 k w wall split
    Novelist:
    Champion:
  • 230 Answers
It sounds like the head pressure is to high. This is sometimes do to overcharging. The hissing noise that you hear is the liquid refrigerant dumping into the suction side. This is what a compressor does when the Head pressure is way too high. The fact that it is tripping the breaker may be to a broken suction valve in the compressor. I think it might be time for a new unit.
Posted on Jul 03, 2008
I have a GE freezer, model number FUF20DPARWH that blows a ground fault circuit breaker when it goes into the defrost cycle. The case is not "hot" when this occurs and it is plugged into a circuit th
Ralph, the only way to be sure of what is going on is to check the amp draw of the freezer when it is in defrost. If the amp draw is in range ( listed on model/serial tag ) you may have a GFI that is weak.. if unit does not defrost there will be an ice buildup on the lower half of the back wall... But with unit tripping GFI it probably is defrosting............ Ken Hawk
Jan 28, 2015 | GE Refrigerators
Trip Circuit Breaker
The circuit breakers may both be functioning properly. What might be happening is that both circuits have other current drawing appliances on them. The circuit breakers react to the sum of all of the currents drawn by all of the devices on that circuit. So, if you have a 15 amp microwave and an 8 amp refrigerator on the same circuit, you would overload a 20 amp circuit by 3 amps.
Apr 14, 2014 | LG LMV1813ST Microwave Oven
I have 2 15000 BTU A/C units run to a double pole 20 amp each breaker. The breaker keeps over heating and one side will trip. Should i separate the units on their own breaker? The units cool and run fine...
That would work, if for no other reason, to isolate which one may be drawing too much/more amperage. Keep in mind as well, after a breaker trips too many times, it usually will get weak and trip at lower amperage. If all is same, ( wiring from AC units) and units are cleaned regularily and no other internal problems such as weak, bad, capacitors etc, they should both draw same or close to same. If possible that someone has a multimeter with amp draw clamp, that would confirm where trouble is.
Aug 09, 2011 | Dometic Rooftop RV Air Conditioner
Saunacore 44QRS, is a 120 vac unit. As soon as you turn the elements on it trips the circuit breaker. I've tried plugging into different outlets, even a dedicated 20 amp circuit. The unit is only...
must be running with gfi. run for one hour without neutral wire connected. it will dry moisture content within heater elements. then reconnect neutral wire, and walla, no tripping.
Jul 13, 2011 | Saunacore Standard Residential Sauna...
Is it possible for a delfield freezer 6151 XL-S to trip a breaker every 2-3 hours if the TXV valve was faulty letting liquid get to compressor. This unit has had controller and relay start assembly...
I would look to see if it is tripping during the defrost cycle. One of the heater elements my be faulty. Never heard of a bad TXV causing a breaker tripping, but I guess it's possible. I would adjust the superheat so that it is about 6 to 8 degrees just prior to unit reaching temp and shutting off. I'd start there.
Apr 01, 2011 | Delfield Freezer 6151XLSR Stainless steel
AC runs for 5 minutes and then circuit breaker
What else do you have running on hydro while AC is running? Such as coffee maker, microwave, water heater, fridge. That 30 amp breaker is your main breaker I assume, or breaker on pole your plugged in to. Keep in mind your AC will normally draw approx. 15-17+ amps momentarily when compressor kicks in to cool, then drop back to 12-15 amps when running normal. If your AC is drawing too much current, then you would only normally trip 20 amp breaker for AC in your panel. Try switching other appliances to gas operation while running AC, such as water heater, and fridge. Make sure incoming voltage is up to specs as well . (115-120 volts)
If water heater takes 5-8 amps, and fridge takes same when they are calling for power, you'll be close or over the 20amp mark when you consider your on board converter etc. as well. That only leaves approx 10 amps for AC that requires approx 15 amps to run, and up to 20amps when compressor kicks in. If you switch all those other items over to propane, and it still happens, then a current draw test should be done on AC unit to see if perhaps a capacitor is faulty, or possible compressor faulty.
Jul 22, 2010 | Dometic Rooftop RV Air Conditioner
What is wrong when you install a GFI outlet and the green light in the corner goes on than goes right back off than when you try and plug something in the outlet it doesn't have power?
It means that the outlet has tripped. There are one of three problems which you can check. 1. The outlet was wired wrong. On many new GFCI receptacles if the wiring is incorrect the receptacle will trip and not allow you to use it. Proper wiring methods can be found by searching in your search bar "how to wire a gfci". It is possible that what was plugged in went over the amp rating of the GFCI. causing it to trip (note: not as likely as your main circuit breaker would have tripped first). The only other things, which has happened to me a lot is the outlet can be super sensitive to current change. GFCI measure high and quick rises in current. If it is too sensitive to the rise in current the receptacle will trip. In this case it will need replacement, and the store will exchange it for you free of charge.
Jun 11, 2010 | IDEAL 61-534 Digital Breaker Finder W/GFCI
Why does the electric breaker trip when my compressor wants to draw current?
The breaker is tripping because the circuit is overloaded. In the winter this is a common problem with a cold compressor at startup. If it is doing it in the summer then it may be you have too small wiring or too small a breaker for the circuit. A 20 amp breaker can handle 12 gauge wire up to 20 amp load. If you need more then you must have 10 gauge wire on a 30 amp circuit. A 240 volt compressor requires a 30 amp breaker and 10 gauge wire. What make and model compressor do you own? On the compressor it lists the load and requirements. Tell me the make an model and I can tell you the wiring requirements.
Jan 09, 2010 | Air Tools & Compressors
Circuit breaker overheating on rooftop ac after
Possible overcharge or bad breaker. You need to check the amp draw for the unit. If you draw under full load amps and trips breaker breaker is bad.Rus
Jul 13, 2009 | Dometic Rooftop RV Air Conditioner
My ac circuit breaker keep tripping
If your outside condenser has a locked rotor or short circuit, than the unit WILL trip the breaker - as it should. On the other hand if a breaker is tripped a few times it will have less of a capacity that the rating, (this is designed in it). You will need to determine if the unit is locked (and broken) or the breaker has become too sensitive.
Apr 20, 2008 | Heating & Cooling
Heating & Cooling Logo
146 people viewed this question
Top LG Heating & Cooling Experts
Tim Whalen
Dan Webster
Dan Webster
Are you a LG Heating and Cooling Expert? Answer questions, earn points and help others