Question about Weather King 10AJA2501AH Air Conditioner
Goodman a/c not cooling
A friend had a goodman 2 t 13 seer unit installed last summer he states it never cooled very well. i put my guages on it, highh side was 125 and low was18, found capilary tubes frozen after about 30 seconds. replaced filter dryer and installed a service port just before the evaporator coil, high side pressure was the same so was the low side, charge was 102 oz, replaced evap. coil with an adp, with a txv. now the high side is 155 and low is 55, evap coil dosent freeze but only about 1/3 feels cold and does make condensate, temp at the difusers is 72 and indoor temp is 82. what i am thinking the compressor is damaged due to the practices of installation, (also when i cut the low side line at the evap coil, oil came out so i blew the line out with nitrogen.)
The problem was in the condensing coil, plastic pieces from the valves in the scrool compressor had lodged in about 1/3 of the coil tubes causing the freon to change state in those tubes then mixing with the liquid, at that point there was no sense cleaning out the condensing coil and replacing the compressor so i installed a new condensing unit now all is well and working fine, thanks for the feedback.
Posted on Jul 03, 2008
    Novelist:
    Champion:
  • 230 Answers
It looks like you did make some improvements when you replaced the coil and metering devise. The fact that this system never ran right "out of the box" is suspicious. My first instinct is that the system is either unmatched in size or the whole system is sized incorrectly. Do your Heat gain/Loss calcs and see if it matches close to what is in there, both for the coil and condenser. Secondly double check that the evap you installed is matched the same as the condenser. In some situations the ID coil can be over sized by a 1/2 ton. But that is the only exception and it does not apply to all cases.
If the system is sized and matched correctly, then I would consider the compressor to be the problem.
I have a LG minisplit (indoor unit LSN122HE /outdoor unit is LSU122HE) it cools great dehumidifies also and has for 3 months of summer. However its cold now and it will not heat. It runs for a min out
That's an inverter series motors... the outdoor fan motor is on an ambient controller to maintain pressures when cold outside in air conditioning mode, but not in heat...only defrost when needed. Check the settings on the outdoor board for defrost timing
Dec 02, 2013 | LG LSN122HE / LSU122HE - 11,500 BTU 13...
I installed my new unit this summer and the ac worked fine, now the heater does not work
frist check that the thermostat and the mood is in right positions then check that thermostat give signal to Htr.if Htr is right ohms
Nov 11, 2013 | Goodman Manufacturing Goodman...
I have a SSX140241A - 2 Ton 14 SEER R410A Goodman Air Conditioner Unit with a CAPF1824A6 - Goodman 1.5 to 2 Ton Cased Evaporator Coil. The coil came with a size 59 piston and the outside unit had a size 55...
No, it simply has to do with the fact that the conditions are exceeding the innate capabilities of the unit. Need more refrigerant and larger condenser and evaporator. Basically, a bigger, more powerful unit for the conditions encountered.
Sep 22, 2017 | Heating & Cooling
I had Ruud heating and cooling installed five years ago. Last summer my electric bill doubled when I began running my air conditioner. It did not do that the first few years that we were in this house. ...
Hello In a way you are stuck with what is called a S.E.E.R. rating which is a statement of efficiency from the manufacturer.Ex: a 10seer is less electricity to run than a 14 seer.The model # would have told me the seer rating.A 4 ton `1 zone is a large unit but even a 10 seer 4 ton is never cost prohibitive to operate and Never doubles the electric bill in 5 days out of thirty.Is the home unoccupied all month and you use it on weekends?Did the neighbor run a strange wire to your property?There might be stray or lost voltage in rare cases if there is poor grounding issues.Has the unit been serviced? A low freon charge will cause a unit to run excessively long and not cool.Do you run the indoor blower all the time.Has there been any other major purchases made (at all) that you plug in?I would look at everything because there is some cause for DOUBLE bill amount not just the cooling bill.Good luck
Jun 18, 2011 | Ruud Heating & Cooling
I just had a new Goodman 13 seer installed on 6/5/10 and the unit wont turn off and doesnt seem to cool down the house had new duct installed also they changed out the fan but it runs all day without...
CALL AN EXPERT......THE WIRES AT THE CONDENSER ARE NOT CONNECTED PROPERLY.THE UNIT SHOULD HAVE BEEN VACUUMED/PUMP DOWN BEFORE STARTING UP .POSSIBLE LOW ON REFRIGERANT ALSO.
Jul 13, 2010 | Goodman CLQ36AR49 Air Conditioner
A/C fan is running but no cool air
Make sure the outside unit is running. If it is then you may need to get the unit charged.
May 02, 2010 | Goodman CPLT24-1 13 Air Conditioner
Just had a new 3.5 Ton Goodman GSZ13-13 SEER, heatpump installed. Its working OK in Cooling, however whe switched over to heating mode the indor unit makes a loud grumbling sound. The installer stated that...
I install them every day and I have not had one make a loud grumbling sound. Sounds like you might have a low voltage (Thermostat) wiring problem. The only thing different inside the indoors unit from heat and cool is the fan speed, electric heat when on. The fan might be loose or out of balance and it only shows up at low speeds. Either way, the noise is not normal.
Oct 13, 2009 | Goodman CLQ36AR49 Air Conditioner
My goodman seer 13 package heatpump stopped blowing cool air. Fan still works, there is power to the unit.
Is the outside unit starting and fan blade spinning? Have you inspected you air filter recently?
Sep 15, 2008 | Goodman Heating & Cooling
Weather King 10AJA2501AH Air Conditioner Logo
226 people viewed this question
Top Weather King Heating & Cooling Experts
Tim Whalen
John Tripp
John Tripp
Dan Webster
Dan Webster
Are you a Weather King Heating and Cooling Expert? Answer questions, earn points and help others