I. The outdoor heat-exchanger fan runs at a low speed (with a humming noise), when the home temperature is below the set-point. ii. When home temp. in high, fan runs at full speed, like normal. iii. When A/C breaker is shutoff (in main switchboard), the fan stops. Need help diagnose the problem.
  • firoz_ara Jun 28, 2008
    Dear Tactup, Thanks for the response.
    I have an split A/C unit, as you rightly guessed.
    Make: Goodman Mfg. Co. L.P
    Model: CKB18-1
    If the capacitor is busted, the condenser fan would not run at rated speed any time. The fan runs at full speed on cooling cycle and cools the house. The fan does not stop when the cooling cycle ends, but continues to run at low speed, with a humming noise.
    Hope I have stated the problem a little better. Hoping for your help.
    You can suggest more technical diagnostics, as I am a hands-on electrical guy.
It could also be the contactor; basically an electrically-controlled switch that in turn controls the compressor and the condenser fan. If it's a 220 volt motor, and one side of the contactor has very high resistance, it'll be seeing 110 volts instead, basically causing it to either run at roughly half speed or just sit and stutter, or other weird random stuff. Depending on the contactor design, you might be able to get an emery board (yes, for fingernails--they work great!) between the contacts and lightly buff them. Of course make sure the breaker that feeds the unit is turned off and tagged out first! Barring that, I'd check - in order - the capacitor and the fan motor itself.
And just to rule it out, go through and make sure that each end of every wire is firmly attached to whatever it's attached to. Over time those quick-disconnect connectors can work loose, causing again all manner of random stuff to happen. If you find a loose one, you can probably use a pair of pliers and gently squeeze the connector tight again. Of course make sure the breaker is off and tagged before you stick your fingers in there...220 volts WILL send you flying. Or just kill you.
The 60Hz shuffle is no fun at all. Be safe.
Posted on Jul 28, 2008
  • 230 Answers
I am not sure what kind of air conditioner that this is. If it is a split system A/C then the outdoor exhaust fan should always spin at the same RPM. So if your fan is spinning slowly and humming, it is probably the run capacitor. I will bet that the capacitor is leaking oil or ballooned out. It most cases this is a combination capacitor that runs both the compressor and the exhaust fan. It should be replaced. This usually happens as a result of excess heat or normal wear and tear. After it is replaced it will be a good idea to have the system checked out to make sure the condenser is exhausting the heat correctly.
Posted on Jun 27, 2008
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
Why does my PTHP. shut off and switch to electric resistance heat?
im guessing its there way of defrosting the coils , as with this type (small) its tough to defrost the coils in an efficient way , hp runs normal to within one or two degrees of setpoint , hp shuts off or reverses in low speed , back up heat comes on to complete the room heat and to generate the heat needed to defrost the coils , entire unit shuts off when set point is reached , reversing valves set for heat and wait till next cycle
now mine does something slightly different : it runs for fifteen minutes and if set point is not reached it switches to back up and reverses the coils ,leaves compressor on (low speed) , this heats the coils up and defrosts the outdoor unit , and if it runs long enough twenty minutes total time , it goes back to normal and aux heat shuts off . this drives me insane thinking how much im spending on heating the outside !! but im sure its needed to prevent ice build up on outdoor coils ,and I sure don't want that cracking with ice formations
Jan 30, 2016 | Amana PTH153B50AJ Heat Pump Air...
Comfort star
Make sure the indoor filters are clean. The outside unit will continue to run until the indoor reaches the temperature you have selected. Dirty filters can throw the temperature out. Its common for outdoor units to freeze up when on heating mode if the ambient air temperature is below 5 degrees Celcius.. The machine should however, defrost itself. There could be a problem with one of the pipe or air sensors on the outdoor unit.
Feb 23, 2014 | ComfortStar CHH012CD-13B Wall Mounted Mini...
Rv heat pump problems
Open circuit or out of range Freeze Sensor. Air conditioner mode of operation will be locked out. Furnace, heat strip, heat pump and fan mode of operation can continue to operate but displays the last temperature set-point. There is a sensor that detects evaporator freezing, it may be bad or your freezing because of low freon levels
Sep 30, 2013 | Dometic Rooftop RV Air Conditioner
2002 chevy malibu heats up when running at low speeds
Jan 19, 2012 | 2002 Chevrolet Malibu
Unit set to heat but outside unit fan won't turn on. Outside temp is below freezing. The weird thing is that you unit is putting out heat and not set to emergency heat
If it is a heatpump, the outside unit should not turn on below 35degrees or so. Below that temperature, the unit cannot effeciently exchange heat. When the outside temperature is low, the system automatically switches over to auxillary heat which uses the same heating elements as emergency heat.
Jan 11, 2011 | Ruud Heating & Cooling
We have a tempstar down draft furnace. 2 years ago the heat exchangers where replace because we were told they were cracked. This year the downdraft motor was makikg a lot of noise & we were told the...
Sounds like the low limit or high limit is out these control the fan motor.They are usually set to kick on around 150 degrees and set to go off around 95 to 100 degrees. Over heating does happen with cracked heat exchangers and it can possibly take these two items out. Normally your furnace should run approximately five minutes or a little less then your fan motor comes on and then for cooling down burners should drop and the fan motor should run again roughly five minutes or so then shut down. Times may vary as to your settings.
Dec 20, 2010 | Heating & Cooling
I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...
If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks
Nov 25, 2010 | Heating & Cooling
Instead of the heating element turning on the heat pump runs out side thermostate is not set on eheat
The heatpump is your 1st. stage heat, when you have a call for heat it will bring on the outdoor unit.
When the first stage heat can't heat the house and the indoor temperature drops 2° or 3° then 2nd. stage heat will kick in and maintain the house temperature at about 2° or 3° below the temperature setting.
If you outdoor unit fails or goes into defrost then emergency heat will kick in and keep the house at 2nd stage temperature approximately 2° or 3° below thermostat setting.
If you have an outdoor thermostat or balance point setting on outdoor board, it will shut the outdoor unit off at a certain set outdoor temperature and the 2nd stage heat will be primary heat for the house.
Jan 05, 2010 | Heating & Cooling
Furnace runs but does not heat up the house to thermostat tempera
Did this problem just start? Or has it been a long term issue? Check for broken ductwork, return air pulling outside air in. Check supply air temps, should be 100-140° or more. And what is the outdoor temp? If it's 0° outside, 74° is doing good. Is the home insulated properly? And there is a small hole behind the t-stat where the control wire comes through the wall. Plug that hole, seal that hole to prevent cold air from fooling the t-stat. The furnace has 3 fan speeds and it may be in low speed. If so it should be in medium speed. I'd suggest a service tech doing this for you unless you are experienced in furnace repair.
Nov 02, 2017 | Goodman Heating & Cooling
Heating & Cooling Logo
142 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen