5 min time delay for central system blower unit not reset whe serviced
My time delay is on the unit itself-not themostat-I know this because the termostat has never been worked on-but the unit in the attic has- I just don't know where on the unit I most likely wiil find the circuit board and how to reset the 5 min blower off delay. I know we need to be sure to ground ourselves before touching the unit-to prevent damage to the electronics-also my husband has a working knowledge of safety re' electricity (so necessary) and had worked on older ac units in the past-just not familiar with the newer units you described in # 3 part of your response. Thanks bunches for you help!!
  • 230 Answers
Make sure to turn off the furnace at the breaker or disconnect switch before attempting to touch the electronics of the furnace. Also look around the furnace for an owners manual. The manual will have the process for changing the blower off delay. I have given you a pretty generic process below. If you need more specific directions I will need your model and serial number. If your furnace is new enough I may be able to find your manual in our system. Good Luck:)
In most cases a circuit board model will have a small (1/4 inch x 1/8 inch) black, plastic jumper. I think I remember that some can be red also. Anyway This jumper is plugged on to two vertical prongs coming from the board. There are other bare prongs on either side of the jumper. If you look at the writing on the board you will see different numbers ranging from 60 to 190. These numbers represent seconds in time. You can change this jumper to match the seconds that you want for the blower off delay.
Posted on Jun 27, 2008
  • Don Berry Jun 27, 2008
    I forgot to add that the circuit board for the furnace is probably located in the blower compartment.
Central unit
Seems like defective wiring or thermostat. The thermostat wires needs be checked. Another thing if the ac unit has economizer feature.
With the thermostat removed, if possible wires still connected to thermostat base, jump R-G, indoor fan should turn on: jump R-Y, compressor and outdoor fan should start (may feature a few minutes time delay): jump R-W, heater should start and indoor fan after a time delay.
What you want to see is R-G and R-Y working and if this is no problem, the thermostat may be due for replacement
Jun 21, 2015 | Heating & Cooling
How can the blower motor module be fixed or reset?
Is this your home central air system.....? Name brand ? Be more specific about the system and what are they symptoms/problem?
May 29, 2014 | Carrier Air Conditioner Accessories Time...
Carrier central AC/Heat system repeats "Replace
Try unplugging the unit and waiting a few which many times resets the board.
Aug 03, 2011 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
- Obstructed pressure tubing. - Pressure switch stuck closed.
- Short circuit in secondary voltage (24VAC) wiring.
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Oct 05, 2010 | Heating & Cooling
My outside unit runs a little while then shuts off.
More likely the out door fan motor has bad bearings and that would cause the out door unit to run for 15 to 20 min but it could be low on freon
when the out door unit runs after 3 to 5 min the larger of the two copper lines going into the unit should be ice cold
If the thermostat you just installed has a time delay that will keep the indoor blower motor running for up to 5 min after the unit shuts off
Sep 01, 2009 | Honeywell Heating & Cooling
My Rheem central A/C blower motor cycles on & off
Depending on age of Rheem they have a time delay relay. May be causing the problem. The time delay operates the fan. Try turning fan to continuous and see if it stays on.
Jun 07, 2009 | Heating & Cooling
How to reset 5 minute blower delay for carrier 4 ton central system-instlalled 1995
There are potentially 3 time delay relays in this system.
1) Many digital Thermostats come with compressor ON delays that are not serviceable.
2) There is an accesory manual Time delay available for this unit. It is also a compressor ON delay. (located in the electrical compartment of the condenser)
3) Most newer furnaces have a blower OFF delay (set manually at the circuit board.
I have the technical manual for this unit if you need it.
Jun 25, 2008 | Carrier 38CKC042 Air Conditioner
Thermostat wires or solid state control, (time delay board) sounds like your symptom.
Nov 28, 2007 | Ruud Central System Air Conditioner
Carrier 38CKC042 Air Conditioner Logo
229 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others