Compressor trip out
Bryant high efficientcy heat pump mdl #698AN048-B, Srl #698ANX048000
ABAA . compressor trips out after running two minutes.
the control module led gives 6 flashes indicating trip range.
what would you suggest.
  • willie hodge Jun 26, 2008
    when the compressor trips out after running two minutes,the solid state control module led
    gives 6 flashes in sucession, according to schematic refer to cmpressor sensor out of range ( run range ) and in trip range.
    very much so iwas thinking along these same lines,
    i agree with you, thank you very much.
    Genius:
  • 1,011 Answers
Dear sir/madam,
Please chcek the following troubleshooting guides. It will help u.
Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} Air Conditioning Equipment Checklist
  1. Check to make sure that your thermostat is set in the "cool" position.
  2. Ensure that your outdoor air conditioning (condensing unit) is running:
    • Check the circuit breakers in the circuit breaker box (or electrical panel), most likely mounted to an outside wall in the back of the house. Make sure they are all in the "ON" position.
    • Check the outdoor unit "disconnect switch" to make sure it is in the "ON" position. The disconnect switch is located near the outdoor unit. (Normally a grey 8" wide x 16" high x 4" deep box mounted to the wall).
  3. Ensure that the blower motor in your furnace is running. (If the thermostat is in the "cool" position, the furnace blower should be running.)
    • If not, check to make sure the on / off switch at the furnace is in the "ON" position
  4. Be sure that you have changed your filter in the furnace recently.
    • An extremely blocked filter can cause your outdoor air conditioner unit to shut down due to lack of proper airflow.
    • Your filter should be changed every month.
  5. Check all return air grilles to make sure they are not blocked by furniture.
    • Furniture should be moved away from return air grilles at least four inches for adequate air supply.
Gas Furnace Equipment
  1. Check to make sure that your thermostat is set in the "heat" position
  2. Make sure that the temperature setting on the thermostat is set above (or higher than) the indoor temperature showing on the thermostat.
  3. Ensure that there is power to the furnace:
    • Try turning the fan to 'ON' using the fan switch on the thermostat to test for power to furnace.
  4. Check the circuit breakers at the electrical panel.
  5. Check the SSU switch (it looks like a light switch on a gray box located at the furnace) to be sure it is in the 'ON' position
  6. Has the furnace filter been replaced recently?
    • All 1-inch thick furnace filters should be replaced monthly.
    • Wider 2-inch thick, and other high-capacity pleated filters can most likely be changed every other month or just 6 times per year.
  7. If the system is running but you have not changed your filter, the filter needs to be replaced.
  8. Check all return air grilles to make sure they are not blocked by furniture.
    • Check all supply air registers to make sure they are open and blowing air. (The return air grilles are normally located on your walls and are wide and flat).
If these handy checklists do not solve your problem, contact your neighborhood Bryant dealer right away for service. Be sure to have your model number ready.
Thanks
Good luck
"Don't forget to rate the solution"
Posted on Jun 26, 2008
    Scholar:
  • 104 Answers
There are two problems that it could most likely be. One, the system could be low on freon charge. This will increase the compression ratio and reduce the amount of "cool back" to the compressor causing it to overheat and shut off to protect itself. The other possability is that the run capacitor for the compressor is extreamly weak. A special meter is required to test the capacitance of the capacitor. The capacitor is usually a grey or silver cylinder with either two or three terminals on the top of it. If you intend to replace it yourself, first make sure that all of the power is off to the system. Turn off the circuit breakers to the heat pump AND the furnace to be safe. Mark the wires going to the terminals on the capacitor. If the capacitor has three terminals they will be marked C, Fan, and Herm. If there are only two terminals, they will not be marked and it will not matter which terminal the wires are hooked up to as long as any multiple wires going to the same terminal are kept together. If it is the freon problem, you should be able to tell by checking the large pipe going to the heatpump when the compressor is running. The pipe should become fairly cold to the touch within about 1-1.5min. Judging by how fast the compressor is tripping out though, I am leaning toward the capacitor being the problem. If you are not comfortable attempting the repair yourself, I recommend contacting a qualified service company to take care of it for you. Also the capacitor MUST be matched up exactly on the uF or MFD (both are abreviations for micro-farad) the voltage rating should be 370v or higher. Any A/C shop should be able to assist you with finding the correct replacement as capacitors are a common item to all A/C's and are not a propriatary part.
  • 796 Answers
Can you please explain the problem in detail
Bryant condenser not running.
Check that there's power available (open or tripped breaker or disconnect). If there's power available, check for 24-28 volts feeding the contactor coil. The low refrigerant cut-out may have tripped the 24v (leak). The pressure cut-out may have tripped (dirty condenser coil, inoperable condenser fan motor). If there's 24 volts at the contactor coil, check the capacitor before ohming the motor. A defective run capacitor will shut the compressor down.
Aug 27, 2013 | Bryant Legacy 16 Series 4.0 ton AC...
Samsung 2.0TR split ac compressor getting heated up and tripped after running for 10 mins
High limit switch set to high, obstruction in the system, or your compressor may be wearing out.
Apr 12, 2013 | Heating & Cooling
I have a 6 year old Rudd heat pump.The AC would run for a while and the compressor would shut down until I pushed the reset button.An AC contractor came out and looked at the unit and bypassed the reset...
The reset button that he is talking about is probally the high pressure manual reset. There are reasons that this can trip.
1. Dirty condensor. 2. Condensor fan motor not up to par. 3. A liquid line dryer that is partially blocked. 4. A metering device that is not feeding right. If he verified all these and it still tripped maybe a bad switch. Anyways, with it bypassed what ever problem that is causing it to trip is still there and will get worse and the compressor will burn up and he will come and put in a brand that he likes. Hope this helps.
Jun 01, 2011 | Heating & Cooling
Hello,I have an old jacuzzi vectra II hot tub (1988) 120 volt.the gfci on the unit trips every time the pump is on low speed with the thermostat calling for heat. there is no trip when there is no demand...
hi,
ok so when the pump is on high and the heater is running it doesent trip? you didnt say if it did. undo the heater leads so the pump is isolated completely. run the pump on the control centers gfci and see if it trips. if it does then try wiring directly - with an extension cord to a plug with a gfci in your house and see if it trips the gfci in your bathroom. if no trip inside house then bypass tubs gfci and run it with heater and pump through your bathroom gfci. if no trip then try and replace the tubs gfci, it gets pretty humid in the control center and gfci's have a semiconductor which which do fail after years of rough duty like that. if it trips the gfci in your house with the heater again it has a cracked heater element. craigslist always has old hot tubs and parts. you might have to buy a whole used old hot tub but that may be cheaper than a new heater box.
later
jm
Feb 22, 2011 | Jacuzzi MAGNUM FORCE POOL PUMP - TWO SPEED...
Bryant furnace model FX4C, FY4A with heat pump and a/c will not switch from a/c to heat pump. Only have heat with emergency heat on.
WELL this could be a couple of problems the reversing valve could be stuck either from not enough pressure which would be a leal and low on freon or the unit is off on low pressure switch/high pressure switch from either being low on freon or something restricting it and caused unit to shut down, ive been a servicer for many years and if it gets below 30 degrees outside i would recommend running the e-heat anyway it does cost more money minute for minute. but you will find it will heat alot faster in those colder nights than the heat pump therefore cost is about the same.
as far as not switching over could be low on freon or a stuck reversing valve... is the outside even running in cool mode if not the you may have a tripped pressure switch...good luck
Jan 04, 2011 | Bryant Heating & Cooling
AC breaker trips after 10 minutes
Whats the amp breaker? Is this for the inside unit or the outside condenser? If the inside and gas heat you have a bad fan motor, If its an electric furnace , the same, but if its the outside unit, the fan could be going bad, locking up and the compressor still runs and pulls high ampsand tripps breaker or the compressor is just pulling too many amps due to plugged coils with dirt , grass or weeds blocking airflow.(koolbreezes74401@yahoo.com)
Jun 08, 2008 | Goodman CLQ36AR49 Air Conditioner
Computers & Internet Logo
164 people viewed this question
David Payne
David Payne