During air condition mode fan does not run unit freezes up and there is a red flashing light on the circuit control board. The board # is GMP 125-5. The outside compressor work normally.
  • 38 Answers
Dear tomsandi,
Either the fan motor is burnt out or it is not getting the power supply, hence the fan is not working. Since there is no air passing through the evaporator the cooling is not taken off fron the coil so it freezes. The fan motor has to checked up.
Regards,
ramesh22
Posted on Jun 25, 2008
The fan motor is on all the time with the controls shut off. I have to shut the unit off with the main breaker. The ac works but again the fan never shuts off. On the circuit board the LED flashes 8 times,...
The indoor fan or the outdoor fan? If it is the indoor fan the thermostat may be wired incorrectly or shorted. If the red wire and green wire in your thermostat maintain contact, the indoor fan will run all the time.
Aug 03, 2011 | Heating & Cooling
My Home Ac Unit Is Not Blowing Any Air
This sounds like the fan not turning during cool. You will have to check the fan relay for power during the cool cycle. The fan relay is run by the low voltage side, but still there is hi voltage present. When in heat the power goes thru the relay on one set of points then in cool goes thru the opposite side. You should have a digram present, and then on the main circuit board there is a code light. Check the light for blinking or (flash) read the bottom of the board for the code ( very small print)
May 17, 2010 | Goodman CKL24AR24 Air Conditioner
Jan 12, 2010 - My air handler fan (american Standard #TWE065E13FBO) works during a/c operation but not during heating operation. Checked continunity through the the thermo sw and throught the heating coils...
You need to check if the air handler fan running.Suppose if you donot see it then, check to see if the fan on the outside unit is running. If the fan on the outside unit is not running either, check to make sure that the breakers for the furnace/air handler and the air conditioner are on. Also if the breaker is not tripped, then the problem may be your thermostat, the furnace/air handler control board, or the wires between the furnace/air handler and the thermostat.
Let us know if you need further assistance.
Thanks for contacting Fixya.com
Jan 12, 2010 | Heating & Cooling
Fan freezes up with ice in winter
They need air, do not cover it when in use.
If ti cools fine in summer then you just have a defrost problem.
Make sure the outdoor coil is clean.
If the coils are clean, then you have a bad defrost control.
In heat mode the unit should go into a timed or temp controlled defrost. If it is frosting up to the point of stopping the fan, in heat mode only, and otherwise operates properly, then its a bad defrost control.
It is reccomended that the defrost temp sensor be replaced at the same time the defrost control board is replaced. Some temp sensors are part of the board and not a seperate component, but not most.
Aug 19, 2009 | GE Zoneline AZ25E12D3B Air Conditioner
Penguin model 610012-001a/c compressor won't start
I would check to make sure that the control is sending the "cool" signal to the control unit. LO on the room temp display usually means that the fan speed is set to low. Is LO and Auto showing on the display at the same time. Try resetting the thermostat first. Hold down the Mode and Zone buttons with the tstat off. While holding them down, turn the tstat back on and hold the buttons down until FF appears on the screen. Release the buttons and try the AC.
If this does not work, on the control board is a freeze control switch plug (blue usually). Try unplugging this unit and insert a small jumper wire. If the Compressor comes on and runs then you have a bad freeze control switch. If not, then you should replace the control board.
Hope this helps,
Jeff
Jun 23, 2009 | Dometic Rooftop RV Air Conditioner
Goodman forced air gas furnace not firing
if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
Apr 04, 2009 | Heating & Cooling
Coleman 15k will not come on
Here is the troubleshooting guide for your unit. Hope this helps.
TROUBLE SHOOTING GUIDE
TROUBLESHOOTING
Symptom Remedy
1. Remote does not turn on system
- Check and replace remote batteries if the display fades while
any button is activated or no display is present. - Point remote towards IR receiver during transmission. 2. System does not turn on, no green LED & no beep
- Check wiring. (see "installation instruction")
- Check modular cable to receiver.
- Check diagnostic LED status in the upper unit control box.
3. System does not turn on even when receiver green LED is on.
- Low or over voltage condition, check diagnostic LED status in the upper unit control box.
4. Fan runs but no cold air.
- Evaporator temperature sensor reaches low limit, defrost mode.
5. System runs continuously in the cool mode
- Remote was set for "I feel" mode and is left in a heated environment (sun etc.)
6. System runs continuously in the heat mode
- Remote was set for "I feel" mode and is left in a cool environment
1. Diagnostic LED (green)
(Note: Located on the control board in the upper unit control box.)
a) The LED is on when the 12VDC is adequate and communications are
present.
b) The LED is flashing fast and steady when in the freeze mode. Evaporator has frozen and the freeze proctection switch is engaged.
c) The LED is flashing slow and steady when the delay on break timer is
activated.
d) The LED is flashing 1 cycle on and off for one second with high or low
12VDC. Check the incoming 12VDC power for OK.
e) The LED is flashing 2 cycles on and off for one second with a
communication problem. Problem with the control board in the unit and the remote.
Hope this helps.
Jeff
Rate me Please!!!
Jul 29, 2008 | Coleman Mach 15 Air Conditioner
Why is my air conditioning unit keeps freezing up
Low ambient outside temperatures can cause this problem if you are running your system with the fan in the automatic mode. When the fan cycles with the temperature ice built up in the cooling cycle has no means of defrost. Set your fan control to on.
Apr 29, 2008 | Heating & Cooling
Air Conditioner malfunction
Hi, Sounds like you have a short in the control circuit to me. Turn off all power going to the unit. Write down or otherwise mark the wires leaving the control board going to the thermostat. Remove them from the control board. Replace the fuse. Turn power back on and see if the fan still runs. If it does, check and or replace the heat limit switch that brings the fan on during the heat cycle. It may just need adjusted. If the fuse blows, I would think that the control board is probably bad. If it doesn't blow, Remove the thermostat. Leaving all thermostat wires open check them with an Ohm meter. There should be no continuity between them. Twist all the wires together at one end and ohm them again at the other end. You should have complete continuity on all wires. If the wiring checks out, down power the unit. Double check your wire colors and rewire the control board. With all wires open at the thermostat, turn the power back on. Touch the RED wire to the YELLOW wire. The Condensing unit should come on. Touch the RED wire to the GREEN wire. The fan should come on. Touch the RED wire to the WHITE wire. The heat should come on. Down power the unit. Replace the thermostat. Test unit. If the fuse has lasted ok but blows now it is either wired wrong at the Thermostat or the thermostat is bad. I hope I have helped. NOTE: If you can not understand these instructions. Call a licensed Heating / Air conditioning company. kstfas
Sep 23, 2007 | Heating & Cooling