Question about Hayward H2501 HSeries Millivolt Natural Gas Pool Heater 250000 BTU
My Hayward gas heater H250 does not seem to be heating as hot as previously. Is this my imagination or can there possibly be a heating issue? It is set at max heat but does not seem to be as hot when it enters the pool even though it is definItely warm, just not very hot.
  • skyle99 Nov 15, 2010
    This was very helpful. Thank you.
  • 10,515 Answers
There could be an issue with Hayward gas heater.
Have you tried resetting the high limit inside the heater service panel?
If you remove the service panel you should see a limit switch with a red reset button.
It will look similar to this. If the high limit is tripped it will keep it from lighting.
Now there are other safeties involved. There are 3 more limit switches, (automatic reset) with no button on them, the pressure switch that proves there is enough water flow, the on/off switch and the thermostat that regulates the water temp.
If any one of these is not making a complete circuit it will keep the main gas from opening. You need to systematically check and see what is keeping it from working properly.
The most obvious places to check are the manual reset, then make sure your filters are clean for maximum water flow and make sure no bypass valves are preventing enough water flow.
The valve operates on 750 millivolts DC. (less than 1 volt.) A bad connection at any of these switches will prevent it from working properly.
You can take a little piece of wire and jumper the TH and TH/TP terminals on the gas valve momentarily to see if it will light. If it does, you know the pilot and valve are OK. If it doesn't you need to go through one by one and test each safety switch to see what is holding it from working. A volt meter comes in hand here.
If you are not comfortable working with any of this..I would advise getting your service guy back out there.
Let me know,if needed further assistance.
Hope i helped you.
Thanks for using ' Fixya ' and have a nice day!!
Posted on Nov 14, 2010
Hayward H250 pool heater will not light
see if pressure switch full voltage both sides or hi limits
Apr 26, 2013 | Hayward Pool Products Hayward H250 250k...
Hayward H250 has LO listed on the electronic panel after it had been blowing black soot out of it
check gas pressure heater overheated probably needs hi limits or fusible link plus clean heat exchange to solve
Oct 12, 2012 | Hayward H-series Electronic Gas Pool...
Hayward h250 ed2 failure error code IF
ignition failure check gas source if ok check ignitor
Aug 03, 2012 | Hayward H-series Electronic Gas Pool...
Remove high stack from Hayward H250 series pool heater
clean stack also check gas pressure sooting caused from low gas pressure plus overheating
May 25, 2012 | Hayward H250 High Wind Stack
Pf hayward error code on gas heater H250 IDPL1
check pressure switch if voltage both sides ok if not bad switch or clogged copper tube also check filters
Nov 16, 2011 | Hayward H-series Electronic Gas Pool...
Pool heater cabinet gets so hot it burned the wires
That condition is from rollout of the burner flames. Check the underside of the heater top for a buildup of debris. Clean it if necessary. You may notice your heat echanger looks like a BBQ pit. If so it is sooted over and needs to be thoughouly cleaned before further use.
If you find this condition, you should also look at your burner tubes once the exchanger is cleaned and the heater is operating. Be sure the flames are nice and blue and 3 or 4 inches tall. If they are not, and especially if they are mostly yellow/orange, you need to do some more inspecting for what is messing up your combustion, which would have led to the soot.
Finally, if none of the previously mentioned conditions exist, consider wind pressure over the top of the heater. In windy areas and in certain installation conditions, you may needa high wind stack to provide positive drafting of exaust gas.
Jun 25, 2009 | Hayward 250kbtu Ng Pool Heater - Inground
Hayward H250 (millivolt) pilot won't stay lit
make sure the flame hits the thermo couple if so then replace it lows has them in the water heater section thermo couple gets hot makes millivolt signal then opens gas valve
May 08, 2009 | Hayward H Series Millivolt 250,000 Btu...
Hayward h250, wont heat
Sounds like it could be the flame sensor.
Apr 04, 2009 | Hayward H Series Electronic Ignition...