Question about Goodman GDS80904BNA Open Flame Heater
I have a downdraft Goodman furnace. On only some occasions the blower will start, then after a few seconds I will see the igniter light up, but then I do not get the rush of gas and lighting of the burners. It will try this a few times and then stop. Then the light on the board starts blinking once (system lockout). If I wake up in the morning and it's cold in the house I can usually turn off the switch on the furnace and then it works fine... usually. I bought this house 3 years ago and replaced the board in the furnace the first year (furnace wouldn't work at all and board was slightly burnt when pulled out). I've also had it cleaned several times. Could the board be going bad again? Should I insulate the metal exhaust pipe to keep it from getting so hot near the circuit board? Will that hurt anything?.
    Genius:
  • 1,015 Answers
It sounds like you got a tough one there.When you say the blower starts up and then the igniter comes on are you refering to induced draft motor or main blower. The proper sequence is for the thermostat to call for heat at which point the induced draft motor should come on and run for 30-45 seconds,then the igniter should heat up for a few seconds then gas valve should open and main burner should light. After limit switch reaches set point for fan on ,blower should come on till after heat has reached thermostat setting then burner should go out, and blower run until fan off setting is reached on limit switch. If your furnace is not following this sequence and then not always doing the same thing in the same order,I would recommend that you change out board again. I have had several problems similar to this with Goodman units and all but one time installing new board solved it. That time I did everything I knew to do and talked to factory service techs repeatedly and finally installed new furnace. As far as your question about insulation,. As long as it is fire proof I can't see where it would hurt anything. Sorry I'm not more help. Good luck and thanks.
Posted on Nov 12, 2010
I have a Goodman GMS9 furnace. When the furnace starts the induction fan runs for about 15 seconds, the ignitor turns on but thats as far as it goes. The burners do not light and I don't think the gas...
The igniter heats a thermocouple to turn on the gas valve. From your description, the thermocouple may have failed. The noisy stack blower probably needs to be replaced but its controller may be in need of replacement as well.
Nov 01, 2013 | Goodman GMS90703BXA Heater
Heater unit will not ignite, will note fire up
Check your furnace by the electrical panel, there should be a blinking error light. Sometimes there is a legend to how many blinking lights means what. I had an issue with mine, read the code and it turns out it was hitting the high heat limit. Turns out my blower motor wasn't turning on. Replaced it with a spare and it was fixed. Find out what type of furnace, and google the name, model, and the words, 3 blinking lights. Does your furnace turn on at all? Does it start to go through the cycle then stop? This is the proper cycle of a furnace and what should happen.
Inducer motor kicks on, it runs for a little bit, about 3-5 seconds, then you should see a bright yellow glow, this is the igniter, shortly after, you should hear a click and the gas should start to flow, almost immediately it turns to a blue flame. Then your igniter should turn off and the blower motor start up.
Mar 02, 2011 | Goodman GMS90703BXA Heater
My furnace blower kicks on and the flame lights for about 5 seconds then kicks off. I replaced the igniter recently. The service trouble light blinks continuously.
Your furnace may be kicking out on high limit. Its possible your circ. or blower fan needs to be cleaned. If you don't get enough air moving across you heat exchanger it will kick off on high limit.
Jan 14, 2011 | Goodman GMS90703BXA Heater
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 12, 2010 | Goodman Heating & Cooling
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
Change blower to down draft
I dont think you can change a gas furnace from horz/upflow to downdraft,the inducer motor would never prove the pressure switch, the drainpan would upside down,you can order a downdraft unit, i dont believe this unit is made for that
Sep 30, 2009 | Goodman GMS90703BXA Heater
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Furnace clicks many times before igniting
sounds like it could use a new spark ignitor with new pilot assy. will probably die completely soon
Nov 26, 2008 | Goodman Heating & Cooling
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater