Question about Goodman Heating & Cooling
5 ton goodman ac unit
Replaced compressor in 5 ton ac unit. ck for leaks with nitrogen. ran a deep vacum . added freon r 22 to 50 psi pressure before starting. unit ran for about 1/2 hour then stop . Kick out in overload. never fully equalized totally.
thought there might be restricktion in system , ck piston its ok, ck filter in unit its ok . took off high side line set left suction side and ck with nitrogen.
could it be the new replacement compressor bad.
    Scholar:
  • 104 Answers
You MUST WEIGH IN THE NEW CHARGE OF R-22. There should be a label on the side of the a/c unit that states what the factory charge was. This is only a starting point. Once you have the factory charge in the system, then turn on the unit and allow it to stabilize (5 min) . Check pressure on low side and check teperature on low side pipe. Temperature of pipe should be 8 to 15 degrees above what the boiling point of the refrigerant is for the current pressure you are reading. If the temperature is more than 15 degrees, add R-22 in 4oz increments allowing 5min in between each time you add until you are in the "zone". When you do this, your head pressure needs to be 225-250. if you need to cover the coil or block the outdoor fan to do this then do it. Hook up the vacuum pump and start over
Posted on Jun 18, 2008
  • Chris Lyon
    Chris Lyon Jun 18, 2008
    The compressor tripped on overload because there was not enough freon in the system to keep the compressor cool.
Compressor does not engage when ac is turned on.
If the system is low or has no Freon, the clutch will not engage. Hook up a pressure tester on the low pressure line valve. It should read 30 psi at 65 degrees outside temperature and 50 psi at 85 degrees outside temperature. If there is pressure, then it could be a fuse or AC relay. If there is no pressure, then add freon with some pag oil, plus a leak dye will have to be added to the system from the low pressure valve. Only add 1 16 Oz. can to not over pressurize the system. If the clutch engages, then check for a leak. I would recommend taking this job to a qualified technician, since he would have the necessary equipment to put the system at a vacuum of -30- To empty the system and check for a leak.
Apr 16, 2014 | 2003 Nissan Altima
Bad condenser unit GOODMAN
it is a 3 ton condensor you still can buy r22 freon condensors new but they have nitrogen charge and its expensive to charge I recommend to go with 3 ton goodman condensor which is new 410a puron and also change indoor coil and flush the line set so you dont endure the high cost of new copper lines these new systems come with 10 years warranty and the r22 systems come with only five years
Feb 26, 2013 | Heating & Cooling
Oil is leaking in my denso a/c compressor
you will need to replace the compressor has i was never able to get replacment seals
also equipment needed to performed this repair is more then a replacment compressor
1--- have sysetem evacuated from remaining freon
2--- replace compressor per supliers information
add recomended oil if stated by supplier
replace affected o-rings or matting gaskets
3---have system nitrogen pressure tested for leaks
4---have it vacumed and recharged
May 21, 2011 | Toyota Passenger Cars & Trucks
Hello, I have a Calvinator A410 unit that I am working on it is a heat pump, I had a leak remove freon and vacummed for around 5 hours. Having a problem charging the unit as a thermo protect on the...
There should be a name plate with the model and serial # which will tell you what the factory charge is for the unit plus 15 to 25 feet of line set. If you weight in the charge you should be pretty close...... In AC mode you should run around 125# suction and about 265 head pressure with 70 degree ambient F. If you have the right charge in the heat pump and you are still running 25# suction pressure in the Air Condition mode then you have a restriction filter drier or TXV locking up..... Did you replace the filter drier when you fixed the leak was the leak on the suction side if so then you definitely need to change the filter drier.
May 01, 2011 | Heating & Cooling
I HAVE SPLIT UNIT AND THE COILS ON THE OUTSIDE ARE FREEZING UP I'VE HAD THE FREON CHECKED IT ONLY DOES THIS WHEN IT AROUND 35 OR BELOW
Gas leak in your system. Don't run the unit further as it will pump the oil from compressor. Find leak by pressuring nitrogen up to 300 psi.And with soap solution you can find leak. Even with leak detector you can find.
After finding out the leak arrest with brazing and then recheck for pressure hold up. Vacumise and then do gas charging. Please call repairman to do professional job.
Dec 27, 2010 | Heating & Cooling
1 1/2 ton goodman outside unit made a hissing
Hello Scott,Your new ac is OVERCHARGED with freon.Shut it off,let it cool down and recover/remove freon.The compressor has an internal pressure valve that makes the (hiss).It will stop when the charge is adjusted.Call them back to do it.
Jul 31, 2010 | Goodman CKL36AR36 Air Conditioner
With compressor running, low side pressure starts out about 15 psi then goes to a little below zero. i have added r134 freon until low side reached 10 to 12 psi. pressure stays there for a while then goes...
Wow, it would seem like you have a leak there on the low side. You add and it goes goes back to equal on the low side again. The gauge could be off just a bit. Have you pulled a vacum test on the unit? Sounds like you should pull everything out, vacum and the weigh in the correct charge at this point assuming that you do not have a leak or can find and fix it.
Nov 15, 2009 | Frigidaire Gallery Series GLHS269ZDB 36"...
Model GSC130481AG, S# 0808548576 The common wire to the compressor rubbed through the wire insulation and melted a hole in the discharge line from the compressor. Upon loosing all of the refrigerant the...
You have a restriction in the system. Probably in the TXV or orifice in the A/H.
The burn out sent trash/fragments through the system. I would open the sytem and blow nitrogen through, then pull a deep vacuum.
You may need to install a low side filter/drier. When you open the system change out the high side drier again for sure.
Jun 26, 2009 | Goodman Heating & Cooling