How do I wire up a Maestro Lutron MAW-603-RH dimmer in a 4-way situation?
    Novelist:
  • 107 Answers
If you bought the 3-way package, there should've been two products included: the MA-600- and the MA-R. First of all, if this is a four way circuit, that means you currently have at least three switch locations. The package you bought takes cares of two of those locations, but to get the third, you need another MA-R. If there are more locations than that, each additional location requires an MA-R.
It doesn't matter which product (the MA-600 or the MA-R) you put at each location. They all wire the same.
At the 3-way locations (ends of the lighting circuit), install the dimmers just like you would a standard 3-way switch. The only thing I caution you, make sure that the blue screw on the dimmer is connected to one of the traveller wires going to the next switch box. Also note what color wire its attached to - because when you go to that next switch box, the blue screw of that dimmer needs to tie to that same wire. At the 4-way switch box, the most important thing to remember is this.... make sure all the blue screws are connected together (which is why its important to know WHICH wire is connected to the 3-way switches).
As long as you have enough product and you tie the blue screws together, it should work.
Posted on Nov 11, 2010
Can I reuse a Lutron Maestro MAW-603 dimmer in a 2 way situation?
you should be able to by hooking up the black wire on the dimmer to the hot wire(that comes from the electrical panel) in the wall box and the red wire from dimmer to the switch leg(the wire that goes to light fixture). if the dimmer has a white wire(nuetral wire) you will need to hook that up to the white wires in the wall box....CAUTION!!! when removing the old 1 pole switch, there should only be 2 wires and possibly a green or bare copper ground wire attached to it. if either of the 2 wires(not the ground) are white, IT IS MISLABLED OR MISCOLORED. DO NOT hook the dimmers white wire to it cuz it will fry the dimmer. If this is the case, then most likley you do not have a nuetral in the wall box but look anyway for a couple of white wires tied together with a wire nut and stuffed in the back of the box. if you find those than most likely thats your neutral(check with a wiggy or meter to be sure) and thats where the dimmers white wire goes. hook up the dimmers green wire to a green or bare copper wire in the wall box and then put a wire nut on the dimmers red w/white stripe wire.
Feb 16, 2014 | Maestro Lutron MAW-603-RH 3-way 600 Watt...
I have always used a lutron maestro dimmer. I replaced the chandelier and put in 6-60 watt bulbs. My previous chandelier used 18-25 watt chandelier bulbs and the dimmer worked fine. after changing the...
You should have just two wires plus a ground hooked up to the dimmer. It should install just like the maestro. If you are getting no lights with a double tap, or tap and hold, and if the led is not on, it is one of several things. Most are basic, but will list anyway. Check that your connections are good. Make sure you have power there. Make sure the bulbs are good. If all is fine, you probably have a defective dimmer if it worked prior to this. To test, take the dimmer out, restore power, and carefully touch one insulated wire to the other one. If the light comes on, it is the dimmer at fault.
Mar 06, 2011 | Lutron ELECTRONICS MAW-600H-LA SMART...
Need the wiring diagram for MAW-603-rh-wh
http://www.lutron.com/TechnicalDocumentLibrary/0301122A.pdf
On the first page, its the wiring diagram smack-dab in the middle.
If you couldn't find it before, its because the MAW-603-RH-WH is a package containing two other products, the MA-600 and the MA-R. So the instructions I have noted above are appropriate.
Feb 15, 2011 | Lutron Electronics MAW603RHWH Maestro 3Way...
I have a Meastro dimmer MAW-600 W that is installed, but the light does not turn on and the LED keeps blinking. Any idea what the problem can be?
1) If this installation was working before, the Maestro has a small pull-out circuit breaker that lets you reset the device. This is called the FASS Front Accessible Service Switch, located at bottom of dimmer where it meets cover plate.
Open sample Lutron Maestro dimmer manual to see FASS illustration
http://www.lutron.com/TechnicalDocumentLibrary/0301106A.pdf
2) If this is new installation, then double-check your wiring and check that load matches dimmer capacity: 600 watt incandescent or halogen, which excludes CFLs apparently.
Some electronic devices have shortened lifespan on circuits that are not clean. Use circuit analyzer on outlet on same breaker to see if line has interference.
3) I don't see MAW-600 W listed among Maestro dimmers, so I don't have that specific manual.
http://www.lutron.com/Service-Support/Technical/InstallationInstructions/Pages/InstallationInstructions.aspx?syst=Dimmers+%26+Switches&prodn=Maestro%C2%AE+dimmer+%26+switch
4) Amazon certainly shows the MAW-600 W, in case you need a replacement.
http://www.amazon.com/Lutron-MAW600H-WH-Electronics-Maestro-Dimmer/dp/B000BPCWQE
5) Lutron has customer service numbers:
1.888.LUTRON1 (588.7661)
1-800-523-9466
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on dimmer or any do-it-yourself project.
Fixya is always less expensive than a service call.
Feb 02, 2011 | Maestro Lutron Dimmer 600 Watts Ma-600-wh
I bought a MAW-603 with an accessory dimmer to be placed in a 4 way circuit. I followed the instruction on how to connect the accessory dimmer in the 4 way switch location but doesn't work. When I leave...
You are saying that you have a "4-way circuit". That means that you originally had two 3-way switches and at least one 4-way switch. ALL existing mechanical switches _must_ to be replaced with electronic dimmers in order for things to work correctly. You must have only _one_ master dimmer (MA-600) located wherever you desire. All of the other switch locations must be companion dimmers (MA-R)., NOT mechanical switches.
The MAW-603-RH comes with a master dimmer and one companion dimmer, so I suspect that you need to install one more companion dimmer.
Jan 16, 2011 | Maestro Lutron MAW-603-RH 3-way 600 Watt...
I have a Lutron Maestro MAW-600 switch connected to 2 pendant lights and the 2 pendant lights bulbs blew. I replaced the bulbs but the lights still do not come on. The Lutron switch flashes green rapidly...
Lutron Maestro MAW-600 manual:
Single-Pole 600 Watt Halogen/ Incandescent Dimmer (minimum 40 Watt)
Lutron technical support 1.800.523.9466
You said pendant lights blew out.
How many total watts were those lights?
Did you remove aluminum break-away fins on side of device to match wattage?
Front indicator can be pulled out to cut power to circuit.
This is called FASS switch.
Try pulling out FASS switch and then pushing it back to see if it re-sets device.
Click breaker on-off to see if it resets device.
You replaced a single-pole switch that has two wires plug ground wire.
Each wire from switch goes to either screw on MAW-600 so it's hard to go wrong there.
Bare copper goes to green ground screw.
Otherwise, it looks like tech support is next step: 1800-523-9466
Nov 24, 2010 | Maestro Lutron MAW-600H Single-pole 600...
The lights on the dimmer flash and/or brighten and dim on their own. How do we fix this?
For 100% certainty, I would call Lutron's tech support at 1-800-523-9466. They're available 24/7 and can probably troubleshoot it more effectively than through this text-based dialogue. However...
I have three guesses...
1) Check the minimum load. The minimum load for those products is about 40-Watts. If there isn't enough lamp wattage pulling electricity through the dimmer, the dimmer may not have enough juice to keep itself powered up... and then shut down (hence any flashing you may see). If the issue only happens when the lights are at full (or close to full) brightness, then that's most likley your issue. To solve, either increase the lamp wattage, or replace with a dimmer that contains a neutral wire such as the MAELV-600M.
2) Check the load type. The dimmer's are rated for incandescent & halogen. If these are LED or CFL lamps, you are going t see issues. For dimming performance, either convert the lamps to incandescent / halogen, or investigate their new Diva dimmer for CFLs & LEDs: DVCL-153P-
3) If neither of those solve the problem, the next guess is to check the wiring. I wouldn't expect this to cause any "flashing" but in the wiring circuit, each device had a blue screw attached to it, and you need to make sure that the blue screws are wired/connected to each other and ONLY to each other - otherwise "automatic" dimming can take place.
But again, the only way to be certain is to use their tech support. I highly encourage you to use that.
Nov 07, 2010 | Maestro Lutron MAW-603-RH 3-way 600 Watt...
Lutron dimmers throught the house, lights go high brightness to low all by themselves, is this just a bad dimmer?
I have spent considerable time on the Lutron site past couple days looking at their dimmers.
Lutron has a lot of dimmer varieties. The basic breakdown is 600Watt and 1000Watt. But different dimmers control different types of lighting.
Here is the long list of Lutron dimmer manuals:
Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;}
I cannot find a specific troubleshoot manual for Lutron dimmers
So I suggest 4 things:
1) Feel the dimmer switch for heat >>> if it is getting hot (not warm), then that dimmer is dangerous, so remove dimmer immediately, add up your total bulb wattage to make sure you're below the 600 or 1000 watt capacity of you model dimmer
2) Look at the list of manuals shown at link, and make sure your dimmer matches the type of bulb you are using. Your dimmer model number and wattage should be printed on side or back of dimmer.
3) These dimmers use electronics to control the lights. Electronics go bad. The higher the wattage controlled by your dimmer, the more heat, and the shorter the dimmer life.
4) Short in the wires. Replace your dimmer with one from Home Depot and see if the condition persists. If it does, then a short is probably somewhere in that circuit. Troubleshooting a short is another long answer that needs more wiring detail ... please repost if you have a short.
Oct 17, 2010 | Maestro Lutron Dimmer 600 Watts Ma-600-wh
Can a single pole dimmer replacement 3-way control dimmer?
no a single pole dimmer is for 1 location control you need a 2 location control dimmer, return the dimmer for an exchange ensuring you tell them 2 location master dimmer