Contactor does not activate on 1 ton 208 V 1PH residential Heat Pump condenser. It cools and heats when manually pushed in. A green flash comes from the contactor when pushed in a and released
    Novelist:
  • 135 Answers
Green flash is the sparking, which is common which elderly contactors. It should likely be replaced. Test for the problem by checking for continuity (ohms) on the solenoid coil of the contactor. (The two small wires on the side.) Test also if you get 24v AC on those two wires when the A/C is turned on. If you have no 24v, it's a thermostat or wire problem. If no continuity, replace the contactor. (Always pull the wires off the contacts when checking the contacts for continuity.)
Posted on Nov 11, 2010
Why will my heater not come on ?
Check the break box in the house flip off than back on . Also check the disconnect box at the condenser make sure plug is in correctly .could also havea bad contactor bugs like to short them out .if heat pump still wont come on you may need a service tech.
Nov 26, 2017 | Heating & Cooling
Will not come on but emergence heat works
Check contactor that operates compressor and condenser fan. Does it try to come on when you first turn it on, or just sits there? If it tries to come on, it could be the capacitor.
Jan 25, 2014 | Goodman Manufacturing Goodman GPH1348H41...
A/c on 3 ton 13 seer ruud heat pump not cooling
you have condenser issue. check at outside unit for 240 volts to contactor and 24 volts to contactor coil.
May 11, 2013 | Ruud 3 Ton Split System Heat Pump
How do I connect my Jandy AE-TI heat pump to my intermatic T104P3
1) Copy following link for wiring illustration ... assuming timer is supposed to control pool pump:
http://waterheatertimer.org/images/T104-to-contactor.jpg
2) T104P is 240Volt (208-277V) SPDT timer in P plastic outdoor enclosure.
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T104
3) Jandy AE-TI is 208/230V pool heater.
http://www.bestbuypoolsupply.com/media/aemanual.pdf
4) Page 13 of Jandy manual shows single-phase residential wiring diagram.
5) First of all, power to main contactor is not interruped by timer, since this powers 24Volt transformer that controls the chip board and general operation.
6) The timer is connected to 'Auto-heat contactor.'
The confusion is what Load connects to this contactor? The water pump? Load is shown on diagram as 'pump time clock.'
I assume the load is the PUMP??
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Dec 04, 2012 | Hardware & Accessories
How to wire contactor on Sears ac condenser style 36LC-000087CR
The contactor for the compressor and outdoor fan is activated by your thermostat when you call for cool. The small coil is an electromagnet that gets 24VAC when you call for cool at the t stat. The red wire in your T stat connects to the blue (or sometimes yellow wire) in the t stat completing the 24VAC circuit and closing the contactor. The line voltage is supplied to the poutdoor fan and compressor upon the contactor closing.
You can manually pushthe contactor close and the outdoor fan and compressor should start. Do this with your hand on the insulated portion of a screwdriver and take the tip of the screwdriver and push the contactor closed. The compressor and outdoor fan should start. That tells you that you have a thermostat to contactor coil issue if the t stat does not close the contactor when you call for cool.
Aug 03, 2011 | Heating & Cooling
I need a wiring diagram for a starndard residential split a/c system. Just the outdoor section is fine.
Hi, if this is just a split standard heating and cooling unit, and not a split heat pump, all you need to do is pull stat wire from the indoor unit control board to control the condenser with 5 conductors, but you will only use 2 wires for the control of the condenser. Normally, the red and white tie to the 2 control wires of the contactor. Back at the control board, red to red and white to the Y or yellow terminal. You will also need to set your disconnect box for your high voltage near the condenser, where you will be coming from your breaker to supply high voltage to run the motors and compressor. Very easy to do. If it is a heat-pump, you will need to pull at least 8 conductor thermostat wire to wire this up. I would also need to know what terminals and kind of thermostat you have, and if you are using heat strips for second stage of heat. When you say standard unit, you will only need 2 control wires from the indoor to the outdoor unit, along with the high voltage. Please keep me posted and let me know if you need more help on this. A wiring schematic wouldn't be needed if its just a standard condenser.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Nov 18, 2010 | Heating & Cooling
Ruud heat pump
Did you just install this heat pump? If so it sounds like you replace a regular a/c with a heat pump, which will require more wires for the reversing valve. First check to make sure you have 24v going to the condenser. Make sure you have a heat pump t-stat. You should have a orange t-stat wire for your reversing valve. At the t-stat you will have terminals R, Y, G, O, X or C or B, W1, and W2. R is half of your 24v circuit and is a red wire, Y is for cooling mode, G is the Fan green wire, O is for the reversing valve, orange wire, X or C or B is the other half of control circuit blue wire, W1 and W2 is the heat strips in the furnace tan and black wires. These are standard color code but remember electricity does not know colors and an installer may have used different colors. If all of this is correct possibly bad contactor.
Oct 30, 2008 | Ruud UAMB Air Conditioner
A/c help
Do you have 24volts at the contactor when the T-stat. is set to cool or heat if unit is a heat pump? The outside unit must have 24v at the contactor to engage
Oct 19, 2007 | Hitachi RAS-09UH Air Conditioner
Heating & Cooling Logo
61 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Donni Steen
Marvin
Marvin