Question about Electric Electrical Supplies
I have a intertherm mobile home furnace. When i turn on the heat the circuit breaker in the funace heats up and blows the breaker. this only happens when i turn on the heat if i turn on the fan it is just fine. what could the problem be?
    Problem Solver:
  • 16 Answers
You said it yourself. when an electrical device is running it produces amps, with every amp is a unit of heat. breakers are heat sensitive as well. so you might want to consider a new breaker. newer breakers are made out of better materials that are able to displace heat more efficiently. or check to make sure the screws on the terminals where the wires go in are tight. if there is a loose connection that will increase the units of heat traveling through the termination. or, worse case scenario, like when all hope is lost. splice in some more wire, correctly, emphasis on correctly, and relocate the breaker. perhaps use insulation around the breaker, non flammable of course.
Posted on Feb 24, 2014
3 Suggested Answers
muttandjeff
  • 359 Answers
SOURCE: electric furnace wire heating up
you should have a 3- conductor # 6-3 copper wire running to this 60 amp breaker @ the furnace to the panel if this is not the case you should replace this with a # 6 as of now as it is a fire hazard as it is and needs to be fixed at once , # 10 -2 wire is only good for 30 amps and a 60 amp breaker will not trip under fault condition and you could have a fire , if you need further assistance on this let me know and i will try to help
Posted on Jan 10, 2009
  • 10865 Answers
SOURCE: 30 amp breaker trips intermittently
It sounds like this circuit breaker is worn out and needs to be replaced. good luck
Posted on Jan 21, 2009
Intertherm FEH-015HA. Why does it keep opening breaker?
Avery, if the breaker is properly sized, there is something in the circuit that is causing higher than normal resistance such as possibly loose connections on one end or the other. Check the 'minimum circuit ampacity' (for circuit A and possibly circuit B) on the heater tag and make sure the correct size breaker has been installed. That should be a 15 kw furnace and could either be a dual circuit or a single circuit heat strip. Fifteen kw correlates to approximately 60 amps at 240 volts.
TURN OFF THE POWER and check the connections inside the furnace terminal block for discoloration and tightness. If its a dual circuit, there will be two breakers to turn off. Check to see if it is a dual circuit and if so, see if someone has paralleled those two circuits together inside the furnace. If so, you have to make sure the appropriate single circuit wire and single breaker has been installed.
It is usually recommended to run the separate circuits to the furnace instead of paralleling them together.
Good luck and whatever you do...BE SAFE ABOUT IT .
Dec 05, 2015 | Heating & Cooling
INTERTHERM NO HEAT OR BLOWER
This could be failure of the igniter and/or thermocouple.
Jan 27, 2014 | Intertherm 56000 Btu Gas Furnace
Intertherm feh 015ha
either the heat strips, fusible links on elements or sequencers.
Sep 21, 2013 | Intertherm E3EB010H Electric Furnac
Intertherm furnace burner comes on, but blower does not. If I turn thermostat off then back on until it clicks the fan will then come on. It does not do this all of the time, just now and then.
Furnace burner and heat element are not the same. I think the fan time delay, a sensor that turns the fan on when this sensor senses heat, is shot and needs replacing, for a furnace type heat ( gas heat)
Aug 08, 2017 | Intertherm E3EB010H Electric Furnac
Intertherm electric furnace modular home
Will be to clean each contact-switch and scrape the contacts and use wd40 and spray of air and remove all rust, its possible that exist another options of failure.
Jun 17, 2012 | Heating & Cooling
The furnace is blowing warm air even if the thermostat low.
The only thing that tells the unit to come on and off is the thermostat so I would definatly say it is it. When you turn the system back on, does the a/c run normally? If it does, then it's the problem with the heating side of the tstat. Also, does the fan come on when you put it to on and then turn of when you switch it back to auto? If it does, then the system is working fine, its the t-stat. Let me know if you have any more problems.
Mar 23, 2009 | Intertherm P3RA-048K Air Conditioner
Jan 19, 2009 | Siemens 2 pole 30 amp breaker
Replaced blower motor in my Intertherm furnace, now blows cold
most blowers have a high( black wire) and low(red wire) low works much better in the heat mode
Jan 17, 2009 | Berkel 827E Gravity Feed Deli Meat Slicer
Intertherm funace limit switch controls the heater coil
Take the part into a heating and cooling repair business and have them order that part. You will also need to have the model number and brand of the furnace you have. I'm sure they will order one for you.
Jan 15, 2008 | Heating & Cooling
Intertherm E1EH-015HA FURNACE no heat
Sounds like a downflow electric furnace? If so it sounds like you have 15kw worth of electric heat, you might have a defective heating sequencer, witch is what they call a dual on one plate.
Nov 26, 2007 | Heating & Cooling
Electrical Supplies Logo
61 people viewed this question
Top Electrical Supplies Experts
ashburton
Steve
Mike Carew