Question about Coleman Heating & Cooling
I have a customer with a new gas furnace that will not stay lit, it will go through the proper sequence but the flam goes out after 10 -15 seconds, then it will retry, fire up & go out! The preasure switch is closed and I changed the flame sensor, what else could it be?
  • Coleman Master
  • 8,220 Answers
Looks like you may need to use a manometer and do a pressure check on the gas valve. Might be air in the lines. Vibration from the blower can cause the tubing between proving switch and inducer can cause a brief interruption of the suction pressure.
Posted on Nov 10, 2010
  • Dan Webster
    Dan Webster Nov 11, 2010
    Now IF your insert is an ODS system (I have no way of knowing exactly where to look for that model number by the way) If the insert uses the popular Oxygen Depletion System safety then your pilot is dusty inside. The oxygen is lowered inside the dusty pilot safety and so it does it's job and shuts down like it's supposed to. What I do is flush out the pilot with a little rust buster. Then wait till that drys. This keeps from messing with the pilot flap and damaging the pilot. This page shows where to clean and includes a video of how it works
    ODS SYSTEM
  • Dan Webster
    Sorry I posted this to the wrong solution
I have a ruud silhouette gas furnace and I have change everything out and it still won't stay on.
From the description I see try the following.
Take your induction fan blower off and check the condition of the blower wheel. If your induction fan is not pulling flue gas out properly, the flue gas will cause a rollout flame shutdown. Older units induction fan blower wheel rust out and will fall apart and eventually self destruct.
Hope this helped.
Nov 04, 2014 | Heating & Cooling
Funace willnot stay lit
Sounds like you may have a dirty flame sensor. Try cleaning it with steel wool or Emory cloth.
Mar 16, 2014 | Amana GMH950453BX Gas Furnace
How do I troubleshoot a Carrier Gas Furnace 58GS125-JA that Pillot stayed On but Burner will not fire
Good afternoon Victor. It is a good sign that your pilot light is staying on. That means that the gas valve is recognizing the open flam and is keeping the pilot valve open. Now onto your issue. Can you tell me if the unit is a standing pilot or intermittent pilot(doe the pilot stay on all the time or is it lit with a spark upon a call for heat)?
Dec 04, 2013 | Office Equipment & Supplies
Gmp075-3 furnace wont stay lit
Sounds like an airflow issue. Is the return air clean? System is not tripping the limit switch with the door off because it's getting all the air it can handle, with door on its not getting enough air???
Aug 15, 2017 | Goodman Heating & Cooling
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Ruud UBHC Air Conditioner
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
My goodman furnace keeps lighting for about 10 seconds than goes out lots of clicking sounds
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad igniter what I see most of the time is the following sequence of operation:
Solution: You probably need to purchase and install a new igniter. I would suggest that you inspect your igniter closely for cracks. Make sure you do not touch the igniter with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, roll-out switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
NATE, NCCER, PHCC,HVAC Certified Instructor
Oct 25, 2010 | Heating & Cooling
Dometic refrigerator will not stay lit
sand your thermal cupler off or replace it not centing the flam
Apr 11, 2010 | Thetford Norcold RV Cooler/Freezer
Heating & Cooling Logo
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others