Neutral takes high amps 30. R PHASE 12A Y PHASE 3A B PHASE 38A
  • 4 more comments
  • pcramalingam Nov 08, 2010
    IN OUR OFFICE THE ELECTRICAL LOAD TAKES R PHASE 12 AMPS Y PHASE 3 AMPS B PHASE 36 AMPS and NEUTRAL 24 AMPS
    not fax machine . in our office electrical installation
    not fax machine. in our electrical installation.
    what is the solution?
    in our office there is a electrical problem. in 3 phase R PHASE CURRENT 12 AMPS Y PHASE CURRENT 3 AMPS B PHASE CURRENT 38 AMPS and neutral current 28 amps.
  • pcramalingam Nov 09, 2010
    In a 3 phase 440 volt circuit air condtion and computer load
  • 43,501 Answers
Hi, Depending on what the load is and what voltge the loads are thosde readings are very normal. Only the 120 volt loads show up on the neujtral leg. 240 volt loads will only show on the two legs used..... It also depends if this is a Wye or Delta hookujp
i would do some balancing of the loads and tghat is all.
Posted on Nov 08, 2010
  • D. Floyd Kolb
    D. Floyd Kolb Nov 09, 2010
    It is showing me that you made a comment back but I cannot see it anywhere... sorry... try to post again...
    President:
  • 2,777 Answers
I definitely want to help you out here but need to know, what is the device / unit you are referring to in the question?
I need to know a make / model number of the item in question.
Please let me know,
Thanks!
Tim
  • 1 more comment
  • Tim Grayson
    Tim Grayson Nov 08, 2010
    I wish you would have worked with me a bit on this one...
    Tim
  • Tim Grayson
    Ya well I never mentioned anything about a Fax Machine, that actually came from your original question, you have this listed under fax machines in your question... that's why that showed up. I realize it was a power problem and was trying to get clarification.
    So just to let you know, it was listed under Fax Machines somehow by yourself...
    Thanks,
    Tim
  • Tim Grayson
    I am not allowed to help any longer, you rejected my solution :(
    Tim
My viking vcrb 364 all refrigerator beeps 5 times and the lights are scrolling. Manual is unclear about cause.
Check power is proper.And also check neutral is not weak in plug point. Plug with some other point to confirm fridge in under problem. Check with amps meter holding phase or neutral wire for checking compressor is on or taking over current. Due to over current (high amps) light scrolling and beeps sound will be there.. If high current in compressor, call repairman to replace it.
Check what manual you're having is equal with this pdf format.
http://www.vikingrange.com/MEDIA_CustomProductCatalog/m3020004_F20603.pdf
Thanks.
Jan 23, 2011 | Viking Professional VCRB364 Refrigerator
I need to know the horsepower rating of the 8756 ice cream machine in order to match a 3 phase inverter to it
Standard is 208/230-60-3. Maximum Fuse: 45 Amps. Minimum Wire Ampacity: 3A. -220/380-50-3.
Maximum Fuse: 30 Amps. Minimum Wire Ampacity:27A.
Jan 11, 2011 | Taylor Ice Cream Makers
Taking my P660 out out a building with 3 phase power and into one with only single phase. Converter says motor will run on 2/3 power. Good or bad idea????
Good!
MOTOR:
21?2 H.P., Hobart designed, high torque ball bearing,
ventilated within mixer enclosure. Single-phase is
capacitor-start, induction-run type.
Three-phase is
polyphase squirrel cage, induction-run type.
Single Phase 208V 20.0 Amps
240V 17.0 Amps
Three Phase 208-240V 8.6 Amps
Nov 26, 2010 | Hobart P660 Stand Mixer
How can i get single phase power from my 3 phase generator
I have not wire this myself
Wiki says under heading of single-phase:
http://en.wikipedia.org/wiki/Three-phase_electric_power
Single-phase loads may be connected to a three-phase system in two ways. A load may be connected across two of the three phase conductors or a load can be connected from a live phase conductor to the system neutral. Single-phase loads should be distributed evenly between the phases of the three-phase system for efficient use of the supply transformer and supply conductors. Where the line-to-neutral voltage is a standard utilization voltage (for example in a 230 V/400 V system), individual single-phase utility customers or loads may each be connected to a different phase of the supply. Where the line-to-neutral voltage is not a common utilization voltage, for example in a 347/600 V system, single-phase loads must be supplied by individual step-down transformers.
So it sounds like you take 2 legs of the 3-phase.
or
Take one leg of the 3-phase and connect to neutral ... neutral could be a ground rod.
I would put a meter on that circuit before hooking up my power saw.
Nov 17, 2010 | Electrical Supplies
Can tree limbs touching/rubbing against the wires coming from the utility pole cause the 100 Amp Main circuit breaker to trip????
yes,if it has worn the insulation through on one or more of the hot phase conductors to the neutral phase wire,but also check the neutral busbar in the breaker panel for a high resistance connection as this will also trip the main breaker
Jun 06, 2010 | Gb Electrical 100 Amp GE Load Center
How to install a 208v outlet for a stove
if its a single phase panel you will only have 120/240 v.a.c. you can wire it for 240 volts and it will heat faster anyway the only way you could have 208 volts would be if you had 3 phase delta or open delta 3 phase or buy a special "dry-type" transformer for 240 volt to 208 volt step-down,otherwise it will be red-& black will be your 2 hot phases of 120 volts each/white-neutral/and green or green-yellow will be the case safety ground
Nov 14, 2009 | General Electric Profile PP945 30 in....
I HAVE 1.5TON AC IE WINDOW a\C IT CONSUMES MORE
Air conditioners compressors are high starting torque motors , although it uses 15 amps running , it takes perhaps 3 times that briefly to start a compressor. Thats why in the old days the lights dimmed while the ac started etc. Air conditioners are designed to operate at 95 outdoor/ 80 indoor. The design temps are 80 air into a 40 coil gives 60 supply temp, for a 20 temp drop with each pass.
The outdoor coils are 30 above ambient so the hot outdoor air will still be cool in relation to the hot refrigerant gas and remove heat to condense it back to a liquid. Since the pressures and temps are according to ambient there isnt any way to not have the amp draw increase with load.
That said check the breaker for age and replace if not pretty, check all connections for tightness, consider dedicated circuit.
Aug 25, 2009 | Heating & Cooling
I am Replacing a pump motor and I'm not sure of the connections
high speed phase neutral should go to High speed {phase} neutral low speed {phase} should go to neutral .....Low speed and high speed {phase} need not be connected
Jun 15, 2009 | Waterway 5 Hp 230 Volt 2 Speed Side...
Fujing fj-38a webcam driver is needed
cam fujing driver مش لاقيلها تعريف هيا كام فيها ست لمبات وليها مخرج usb وخرج تانى للصوت
Mar 28, 2009 | Cameras
What type of powercord and outlet does this dryer require? Electrician installed a 220 outlet.
ELECTRICAL REQUIREMENTS
ELECTRIC Dryer
CIRCUIT - Individual 30 amp. branch circuit fused with 30
amp. time delay fuses or circuit breakers.
Use separately fused circuits for washers and dryers, and DO
NOT operate a washer and a dryer on the same circuit.
POWER SUPPLY - 3 wire or 4-wire, 240 volt, single phase, 60
Hz, Alternating Current.
POWER SUPPLY CORD KIT - The dryer MUST employ a 3-
conductor power supply cord NEMA 10-30 type SRDT rated at
240 volt AC minimum, 30 amp., with 3 open end spade lug
connectors with upturned ends or closed loop connectors and
marked for use with clothes dryers.
WARNING – Risk of Shock. Appliance grounded to neutral
conductor through a link. Grounding through the neutral link is
prohibited for (1) New branch circuit installations (2) mobile
homes; (3) recreational vehicles; and (4) areas where local codes
do not permit grounding through the neutral, (1) disconnect the
link from the neutral, (2) use grounding terminal or lead to
ground appliance in accordance with local codes and (3) connect
neutral terminal or lead to branch circuit neutral in usual manner
(if the appliance is to be connected by means of a cord kit, use
4-conductor cord for this purpose). USE COPPER CONDUCTOR
ONLY. The dryer MUST employ a 4-conductor power supply
cord NEMA 14-30 type SRDT or ST (as required) rated at 240
volt AC minimum, 30 amp., with 4 open end spade lug
The complete installation manual is at ftp://ftp.electrolux-na.com/ProdInfo_PDF/Webster/134917700es.pdf
Jan 28, 2009 | Frigidaire FEQ1442ES Electric Dryer
53 people viewed this question
k24674