We just moved into a house with a Superior UVFC-500 gas fireplace. Our pilot will light and burn but the fireplace burners do not ignite. The blower works. There is a key on the wall that says on/off. The key spins freely in both directions - it does not have a positive stop. There is also a switch on the wall. I took the cover plate off and it looks like it has telephone gauge wire attached to the poles. I tried to test for current with a multimeter but I don't get a reading. I may not be testing it right. When we had the home inspection done, it was noted that the fireplace worked and a picture looks like the burners were burning. Can you give me any idea of what can be wrong? Thank you.
  • 74 Answers
SOURCE: Gas burner doesn't work
Most appliances that utilize gas burners need electrical power in order to operate. If the burner doesn't work at all: 1) Be sure the circuit breaker serving the appliance is "On" or that its fuse has not blown. Check both the main electrical panel and any secondary sub-panels that supply power to the furnace or appliance. If necessary, reset the circuit breaker or replace the fuse. If the circuit blows again, there is probably a short in the electrical system. Call an electrician or furnace repair technician or see HERE for electrical repairs. 2) Be sure the appliance's switch is turned on and that the appliance is plugged in (when applicable). 3) Be sure the appliance's power switch is turned on. This may be on the appliance or, in the case of a gas furnace, next to or inside the furnace cabinet. If it isn't on, turn it on and wait a few minutes. 4) Be sure the thermostat or heat dial is set properly. 5) If the appliance has a pilot light, be sure it's working. 6) If none of this works, call your gas utility or an appliance service technician. Still having trouble with your gas burner?
Posted on Jan 18, 2006
Master_Tech
  • 770 Answers
SOURCE: oven & broiler not working
you ignitor is going out you will need to replace it the ignitor needs to draw a min of 3.2 amps in order to open the gas valve coil if short of this it will not open at thimes it may just have enough to open
Posted on Jul 09, 2008
rickzilla
  • 706 Answers
SOURCE: ge spectra gas stove top not lighting
If your top burners are not lighting or will not work, it is possible that the burners have become dirty or wet. Please follow the troubleshooting directions below before calling service:
  1. Turn you burner to the Lite position:
    If you hear clicking or sparking, go to Step 2.
    If you do not, check your circuit breakers. If the circuit breaker is ok, we recommend that you schedule service by calling 1-800-432-2737 or schedule service online.
  2. Clean the burner and electrode:
    First remove the burner grate, cap, and head. Use a needle or paper clip to poke through the holes on the burner head. Re-assemble and try the burner.
    Remove the burner grate, cap, and head. Even if it looks clean, wipe the tip of the electrode with a clean, dry paper towel and PRESS IT DOWN. Re-assemble and try the burner, again.
    Check to see if the burner works, If not, then go to Step 3.
  3. Re-assemble - Make sure that each burner top matches its burner bottom. The burner top will lay flat if put on correctly.
    Check to see if the burner works, If not, then go to Step 4.
  4. The spark igniter is operating properly, but the burner is still not lighting. At this point, we would recommend that you schedule service by calling 1-800-432-2737 or schedule service online.
Posted on Sep 01, 2008
SOURCE: 1966 Ford Mustang Gas Guage not working
I had a similar problem. In my 1966 Mustang gas tank, the fuel pick-up was on a "float." My float developed a hole, filled with gasoline, and sank to the bottom of the tank, therefore, the gauge always read empty, but the car ran well. All the other gauges of course worked correctly. The repair was a relatively simple soldering job (after removing the float from the tank), but if that is indeed the problem, ensure all the gasoline is drained from the float before beginning the soldering job.
Posted on Dec 05, 2008
SOURCE: Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Posted on Jan 06, 2009
Hearthmaster fireplace shuts itself off
So the main burner does fully ignite, but after a minute everything shuts off including the pilot? May just need the pilot cleaned
Sep 12, 2017 | Heating & Cooling
Gas fireplace
replace pilot assembly and pilot generator
Sep 05, 2013 | Pool & Spa
Napoleon Fireplace propane Pilot won't light main burner even though gas flows in?
  • I'm going to assume your fireplace has a pilot light.
  • Follow the little holes in the burner that lead to the pilot light.
  • Make sure the pilot flame is pointing directly at the closest burner hole. (adjust if necessary).
  • Often, you will need to sprinkle a layer of "glowing embers" in this area. The embers will help the gas travel to the pilot light and ignite.
  • Always start your propane appliance on "High" never "Low". Cold propane likes to drop to the bottom of the firebox and accumulate until it reaches the pilot (this is called delayed ignition). Keeping it on "high" will help the fuel travel over to the pilot without buildup.
Jan 21, 2013 | Napoleon 36" Zero Clearance Top/Rear Vent...
Can one use unvented gas logs in a superior CF3860 fireplace?I
Little documentation on this fireplace but it appears to be a vented wood-burner(?) If vented, there should be no problem using gas logs. If burning correctly, you may consider cutting back on the flue and intake air, as moisture build-up is the biggest drawback to gas fireplaces. Too much air is just wasting gas.
Dec 03, 2010 | Heating & Cooling
How do I turn on my superior ventless fireplace
I'm not sure about that brand, but I finally figured out how to turn the one in the house I just moved into. The only visible control if you have not accessed the fireplace controls before is the switch on the wall. The wall switch is strictly an on off switch, but it only works if the pilot light is already lit, and the pilot light will not go out by turning off the wall switch. To access the controls, first pull out the vent covers, they are simply held in place with pressure buttons on each end. Behind the lower vent are the controls for the pilot light and fire intensity, mine also contained a metal plate with the instructions printed on it. Open the glass door by opening the four latches, two on top and two on bottom, and then swinging it out on its hinge. You will find the gas spout for the pilot light hidden between the logs. Turn on the main gas line by turning the straight edge of the red handle parallel with the gas line. Turn the gas control to pilot, by pushing in and turning, and then push in all the way to start gas flowing. I like to have a match already lit next to the valve when I start the gas. After the pilot light has been on for about 60 seconds let go of the button and it will return to its normal position. Then turn the control to on and turn on the wall switch, the main burners should start lighting. Close the glass and put the vent covers back in place and your ready to enjoy the fireplace :)
Nov 27, 2010 | Heating & Cooling
Charmglow ventless gas fireplace burners won't ignite
is pilot flame on the thermopile good, pilot flame should cover the thermocouple and thermopile if unit has both
Jan 07, 2010 | Blue Flame Charmglow 30K BTU Propane Vent...
My heat n glow fireplace comes on fine with all burners running but shuts off about 5 seconds later. it seems the sensor that detects a flame thinks the fire has not started and shuts down the gas. Is...
You may have a few sensors, one may be a thermopile that energizes the pilot. It is a very thin but long bulb located in the pilot flame. Then you may have something called a thermopile which is also located in the pilot flame that energizes the main gas valve. It is a larger diameter bulb and will have metal wrapped wireg going to the gas valve. If the pilot stays on but the flame goes out under the logs, change your thermopile and look for a bad connection at the gas valve or switch. If both the main burner and the pilot goes out you may have a gas valve problem or a plugged vent pipe. If the flame just disappears it is most likely a gas valve. If the flame changes colors and lifts from the burner, that is a sign of a plugged vent. Good luck.
Nov 04, 2009 | Leisure HOMEPRIDE Electric Fireplace...
Pilot flame starved out after burners ignite
The declining pilot light might be an indication it is being starved of oxygen by the main burners or some other sort of circumstance.
I have noticed how in a closed room without ventilation the pilot light soon begins to decline and then springs back again when a window or door is opened while the main burners are hardly affected.
This is the gas equivalent of sending canaries down coal mines and is an essential safety feature. If the pilot light declines very much the thermocouple bulb will not be heated and the gas supply to the main burners will be cut off. This is why the pilot light is set at an angle and the thermocouple bulb is slightly offset.
I am not sure if this helps but I hope it does.
Mar 08, 2017 | Ovens
Need Instructions to use Fireplace Gas Logs
There should be a set of metal cards attached inside the fireplace.
First you should read everything there.
I know you have to first light the pilot light.
And then there should be a wall switch.
The problem I have currently is that it won't stay lit when the artificial logs are there.
Nov 03, 2008 | Heating & Cooling
Marco gas firplace
I have a Model 792864B. Before you attempt to light the pilot light - make sure that any wall control switch or remote control for the fireplace is in the off position. Locate the gas supply line. There should be a gas supply valve to turn on the gas supply. The valve is usually painted a different color than the supply line like blue, green or yellow. Open the valve by pivoting the handle to be parallel to the gas line, usually counter-clockwise. When it is closed it is at a 90 degree angle from the supply line. Locate the pilot light assembly - this is the pilot light. There should also be a red or black ignitor button and a black or green valve control knob with the words "on" "off" and "pilot" on it. It may be located inside a black box, mine is marked heatolator, that has a lift off top. Lift off the top of the box. Push in the valve control knob and turn it until the word "pilot" is in line with the arrow (my arrow is red) or indicator line. While pressing and holding in the valve control knob - it presses in about 1/4", press the red or black ignitor button repeatedly (once per second) until the pilot ignites. Once the pilot is lit, continue to hold the valve knob in for about 30 seconds and then slowly release. The pilot should remain lit. If it remains lit, press in and turn the valve control knob to the "on" position. The on/off wall or remote control switch should now light your fireplace. If the pilot doesn't ignite, turn off gas supply valve, wait about 5 minutes and try it again.
Nov 20, 2007 | Leisure HOMEPRIDE Electric Fireplace...
Heating & Cooling Logo
418 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen